With Script Programs in Continuum we were able to check the variable time against an integer value. Like "if time>500 then...".
In StruxureWare Building Operation time is of the type datetime, no longer an integer.
  • Script Program
In StruxureWare Building Operation a datetime internally is now a 64 bit number, so dates can go beyond the year 2038 which was the top limit for Continuum.  Numbers in script for StruxureWare, like in Continuum are just floats ( 32 bits ) so when trying to map a 64 bit number ( the date ) into a float it is not going to work.  You will get very erroneous readings, therefore the ban.
Here are some examples of the correct StruxureWare program:
Remember that for the dates, you can only compare dates to dates, not dates to numbers…
In general,
you CAN do the following:
    compare dates to dates                ==>   if Date1 > Date2  then
    add numbers to dates                   ==>    LaterDate = LastDate + 24*3600
    subtract numbers from dates         ==>    EarlierDate = LastDate - 24*3600
you CANNOT do the following
compare dates to numbers                ==>   if Date1 > 500  then