Default Device ID / Device Instance of SE7000 series BACnet controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Default Device ID / Device Instance of SE7000 series BACnet controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • sesa194431
    sesa194431
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2732 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Default Device ID / Device Instance of SE7000 series BACnet controllers

Picard Product_Support
‎2018-09-10 11:33 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:48 PM

Issue

Without knowing the Device ID / Device Instance these devices cannot add to the MSTP network in the AS or ES.

Product Line

Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices

Environment

  • Automation Server
  • Enterprise Server
  • BACnet
  • SE7000

Cause

Only the MAC ID / Com Address is shown in the display but not the Device ID / Device Instance.

Resolution

SE7200x Models

Default Device ID is set to: 72000 + MAC

  • Where MAC is the current MAC address of the device.

The device ID will also be upgraded as soon as there is a change to the device’s MAC.

For example, when a SE7200F5045B controller with a MAC address of 41 is connected to a network, its default Device Name will be SE7200F5x45B-41 and its default Device ID will be 72041.

SE73xxx Models

Default Device ID is set to: 73000 + MAC

  • Where MAC is the current MAC address of the device.

The device ID will also be upgraded as soon as there is a change to the device’s MAC.

For example, when a SE7300C5045B controller with a MAC address of 63 is connected to a network, its default Device Name will be SE7300C5x45B-63 and its default Device ID will be 73063.

Click here for the Integration Manual.

Please refer to the SE7300 series BACnet controller does not come online in StruxureWare Building Operation if SE7300 controller does not come online.

Labels (4)
Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
Tags (2)
  • Find more articles tagged with:
  • 12516
  • se73000
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore