Issue
How to disable credential access on Doors at different controllers using a single variable.
Product Line
Andover Continuum
Environment
Continuum Access Control
Cause
Require a method of securing multiple Doors at the same time.
Resolution
The best way to secure a number of Doors from a single variable is to use the Door Force Lock Schedule attribute in the Door object. This is accomplished by adding a numeric to the attribute on the Options tab of the Door object;
IMPORTANT:
The attribute name Door Force Lock is misleading, it DOES NOT lock the door in any way, all it does is disable credential access at the door.
For Area/Door Lockdown refer to the linked KB article
And also on the Entry Reader or Exit Reader tabs, ticking the checkbox under either Normal and/or Comm Fail for Door Forced Lock Schedule.
Setting this Door Force Lock Schedule field to a local or remote InfinityNumeric point will provide the following conditions:
- When the Numeric is on, access is permitted to all personnel by card swipe and/or keypad entry. (Allow use of the door.)
- When the Numeric is off, card reader and keypad access are denied to all personnel. (No Access)
You could have this numeric located in a central controller and all the rest of the controllers reference this numeric from the Door objects. No other points or plain English is required.
If you want to ensure that the updates are received, you can force the IE entry for this numeric to update on a regular interval, see Use just one schedule to control doors or access to areas across different controllers that discusses how to accomplish this.