Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Use just one schedule to control doors or access to areas across different controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Use just one schedule to control doors or access to areas across different controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2078 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Use just one schedule to control doors or access to areas across different controllers

Picard Product_Support
‎2018-09-06 01:14 PM

Issue

My customer does not want to have to make changes to schedules in different controllers when changing door unlock times or personnel access times to areas. How can this be solved?

Product Line

Andover Continuum

Environment

  • CyberStation
  • ACX5720, ACX5740
  • NetController
  • Refresh

Cause

How to consolidate door unlock schedules in different controllers.

Resolution

Multiple solutions:

1. The easiest and recommended method is to create the schedule in one controller and simply enter the numeric being set by that schedule in all the applicable door objects, whether in that controller or other controllers.  When you look at the point in the door editor, if it's in another controller it will include the path to the point. This "remote" point becomes part of the import/export (aka IE) table in the controller in which the door is programmed. Even if communication to the remote controller is lost, the import/export table in the door controller will hold the value obtained from the last successful IE table update. 

The IE system is very efficient - when the point in the "host" controller changes, that controller knows to update the other controllers to which it exports the point. There is only one downside to this - for a digital point, like a schedule numeric, which  does not change often, if the controller looking for the change misses it, the value there will not be updated. To eliminate this problem always include in the controller with the schedule numeric(s) a program that "refreshes" the value of the schedule numeric(s). A simple fallthru program triggered by minute works great. The syntax is:

++++++++++++

Set ScheduleNumeric1Name refresh to true

Set ScheduleNumeric2Name refresh to true 

etc

 ++++++++++++

2. Another solution is more complicated but will also work. Set up a schedule and schedule numeric point in one controller. We'll call this the schedule host controller. Then set up a schedule numeric point and program in all the other applicable door controllers that synchronizes (mirrors) the local numeric point to the host controller point. Make sure you use a Line E in the program and alarm if the program becomes, or keeps trying to become disabled. 

Also, for the "next guy" who is trying to understand the system, you may want to enter, in the description field of the local flags, what is setting the flags, ie, the program name. 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 6277
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore