Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,850
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 332
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 263
    • 264
    • 265
    • …
    • 508
  • Next »

What is the difference between an Internal Analog Input (AI) and Pulse Input (PI) when it comes to fractional digits?

Issue What is the difference between an Internal Analog Input (AI) and Pulse Input (PI) when it comes to fractional digits? Environment I/NET 7700 Cause It is not always clear the difference between Internal AIs and PIs when it comes to fractional digits. A clarification note will be added to the next release of the I/NET 7700 Operator Manual, but until then, please adhere to the following when you want to display fractional digits for either Internal point types. Resolution Internal Analog Inputs (AIs) Internal AIs are limited to a maximum value of 2 16 (65535). Internal AIs fractional digits are a direct result of the M value in the conversion coefficient table. If you want to display a value in hundredths (x.xx) the M must be .01 and the B=0 and the highest number to be displayed is 655.35. If you want a number to display a value in tenths (x.x) the M must be .1 and the B=0 and the highest number possible is 6553.5. Internal Pulse Inputs (PIs) Internal accumulators can accumulate not only pulses but analog values as well, but when it comes to fractional digits Internal PIs are completely different from Internal AIs. PIs are a floating point type number. This means there is no limit to the magnitude or the number of fractional digits, except that only 6 significant digits may be displayed at any one time. Therefore, the fractional digits are not ruled by the number of decimal places of the M value in the conversion coefficient table. In fact, for a Internal PI to work properly, you must utilize a conversion coefficient pair of M=1 and B=0. An Internal PI with a calculation of P0+P1, where P0 and P1 are External AIs with values of 34.1234 and 72.5678, would be able to display the 4 decimal places with no trouble. In fact, if you used a conversion coefficient of M=.0001 and B=0 for the Internal PI, and the AIs never changed their value, the Internal PI calculation would start rounding off the value every calculation. This rounding effect would in fact be shown by the value of the Internal PI getting smaller and smaller with every scan of the Internal PI. Remember, for a Internal PI to work properly, you must utilize a conversion coefficient pair of M=1 and B=0.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1207 Views

How I/NET 2.3X has the ability to designate a particular host to do an automatic restore

Issue How I/NET 2.3X has the ability to designate a particular host to do an automatic restore Environment I/NET site Cause How I/NET 2.3X has the ability to designate a particular host to do an automatic restore Resolution Go to the host’s Network Configuration/Link Summary. Highlight the desired row. In that row you will find a column labeled “R/H”. This stands for Restore-Host. Modify this row. In the Restore Host prompt, place the same host number you entered in the host’s active Configuration Profile. (Don't forget to make sure that host has current save files!)
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1052 Views

Resources for setting up of the 7750 Building Manager

Issue Are there resources for configuring a 7750 Building Manager? Product Line TAC INET Environment I/NET site Cause The Building Manager (BM) is based on a zoned programming approach. Zones are groups of points in a system which control related equipment. A good example of a zone would be a group of points that control the lighting, heating and air conditioning for a tenant that occupies 1 floor in a multi-story building. The major function of the building manager is to give the tenant control over this equipment (through a user friendly telephone interface) and to be able to accumulate statistics to be used for billing normal and after-hours energy usage. Resolution Good sources: TCON098 TCON209 (7-28 through 7-38) TCON237 (7-28 through 7-39) Tech Tip 038
View full article
Picard Product_Support
‎2018-09-06 09:29 PM

Labels:
  • TAC INET
1243 Views

Set up a two wire LTS80 Lini-Temp sensor on a 7740 and 7741 DCU

Issue Set up a two wire LTS80 Lini-Temp sensor on a 7740 and 7741 DCU. Environment 7740 DCU 7741 DCU LTS80 Lini-Temp sensor Cause Conversion coefficients must be set properly for correct reading of temperatures. Resolution For Fahrenheit: M = 0.17582 B = -279.4 For Centigrade: M= 0.09768 B = -173.0 Refer to TCON 097 for 10K resistor placement
View full article
Picard Product_Support
‎2018-09-06 10:54 PM

Labels:
  • TAC INET
922 Views

View the routing table and delete entries on a host that is part of a network using TCP/IP

Issue How can I view the routing table on a host that is part of a network using TCP/IP? How can I remove entries in the host's routing table? Environment I/NET Host IP Network Cause Troubleshooting IP communication often involves viewing the current routing tables at a host station. This will help determine if they need to be cleared. Resolution View the Host Routing Tables  Go to Start > Run > and type "cmd" to open a DOS screen Type "route print" and hit Enter Delete an entry from the Host Routing Tables Example to delete address 157.0.0.0: Go to Start > Run > and type "cmd" to open a DOS screen Type the following: route delete 157.0.0.0 and hit Enter Type "route print" and hit Enter. This address should not appear. 
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1289 Views

Limit what is available to the user on a dedicated I/NET host on the Ethernet

Issue Limit what is available to the user on a dedicated I/NET host on the Ethernet. For example, I do not want the user to be able to get to a DOS prompt then modify the Routing Table. Environment I/NET site Cause Limit what is available to the user on a dedicated I/NET host on the Ethernet. For example, I do not want the user to be able to get to a DOS prompt then modify the Routing Table. Resolution This can be done. Remove the DOS icon from Windows. Or, it may be better to edit the permission rights of the user.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
960 Views

On Screen Indication of a Telnet session into a NPR

Issue On Screen Indication of a Telnet session into a NPR Environment Telnet NPR Cause Indicating to the user when a telnet session has been initiated into an NPR. Resolution "CSI NetPlus Router Telnet Server" "Connected to remote NPR” (Name of the NPR) followed by version number, build, and date "Type help for a list of commands"
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
897 Views

Add entries in the host's routing table

Issue How to add entries in the host’s routing table Environment Command Prompt Cause Routing Table Errors Resolution As an example: add the address 157.0.0.0 Go to a DOS screen and type the following: Route add 157.0.0.0 Then type: Route Print This address should appear.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
957 Views

Site has a I/NET 2000 PCU set as an 06 TAP for ADAA, and the PCU has a synchronous EPROM and synchronous BIN file loaded. Do they need to change the EPROM and BIN file to Asynchron...

Issue Site has a I/NET 2000 PCU set as an 06 TAP for ADAA, and the PCU has a synchronous EPROM and synchronous BIN file loaded. Do they need to change the EPROM and BIN file to Asynchronous if they install an integrated dial modem on the serial port of the same PCU? Environment I/NET site Cause Site has a I/NET 2000 PCU set as an 06 TAP for ADAA, and the PCU has a synchronous EPROM and synchronous BIN file loaded. Do they need to change the EPROM and BIN file to Asynchronous if they install an integrated dial modem on the serial port of the same PCU? Resolution No, but you do need to use the correct modem, cables, settings, profiles, etc.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1144 Views

The Process Control Unit (PCU) is set as a 06 TAP. Will it still function as a 01 TAP?

Issue The Process Control Unit (PCU) is set as a 06 TAP. Will it still function as a 01 TAP? Environment I/NET site Cause The Process Control Unit (PCU) is set as a 06 TAP. Will it still function as a 01 TAP? Resolution Yes, by design the 78010 TAP emulation is still functional.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1287 Views

Site has I/NET 2000 PCU set as an 06 TAP for ADAA, and PCU has a synchronous EPROM and ASYNCHRONOUS BIN file loaded

Issue Site has I/NET 2000 PCU set as an 06 TAP for ADAA, and PCU has a synchronous EPROM and ASYNCHRONOUS BIN file loaded Environment I/NET site Cause Should the site change the EPROM? Resolution We strongly recommend you do. If the PCU goes to “Boot-State”, the SYNCHRONOUS EPROM in the PCU will not reset the asynchronous ADAA modem correctly. You won’t be able to dial into the ADAA port of this controller until this is corrected by doing a download or changing the EPROM.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
933 Views

Add a stand-alone 7798 to the existing controller LAN

Issue Add a stand-alone 7798 to the existing controller LAN Environment I/NET site Cause How to add a stand-alone 7798 to the existing controller LAN Resolution A CLX card is required. Refer to TCON 138.
View full article
Picard Product_Support
‎2018-09-06 11:09 PM

Labels:
  • TAC INET
1125 Views

Sync LED on FOI still on after correcting the line fault on the output of the CRR.

Issue I never reset the "Sync" LED on the FOI after I corrected the line fault on the output of the CRR. Will this cause any communication problems? Environment I/NET CRR Cause Line Fault Resolution Reset the sync LED If you can NOT extinguish the Sync LED you should find the fault. Leaving this light “on” does not cause communication problems.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1001 Views

ADAA problems: can not dial in or out of the site

Issue ADAA problems: can not dial in or out of the site A PCU is set up as a 06 TAP. The RX and TX LEDs are flashing on the RS-232 card. A CBL048 cable is connected from the RS-232 card to the modem. The RD and SD lights are flashing. Environment ADAA Cause The wrong BIN file is in the PCU. Resolution You have the wrong BIN file in the PCU. If the PCU is at the “Boot State”, you may have the wrong EPROM too. Install the correct BIN file; and it is strongly recommend to put in a compatible Asynchronous EPROM.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
931 Views

Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU

Issue Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU Environment I/NET Site Cause Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU Resolution The outputs from these locations are DC. This may cause the AC relays to “chatter” or not work at all. It is recommended to use a P8UI8DO at the expansion board or place DC powered, form “C” contacts, pilot relays on the outputs of the PCU. Refer to TCON106 for more details.
View full article
Picard Product_Support
‎2018-09-06 11:12 PM

Labels:
  • TAC INET
1256 Views

Door show Deny Entry Schedule after deleting a special day schedule on the special day

Issue Door show Deny Entry Schedule after deleting a special day schedule on the special day Environment I/NET Access Control Cause The process to execute the Special Day begins at midnight on the first day of the duration, and ends at the end of the last day of duration. If you delete the Special day while it is running you will get denied entry. Resolution Do not Delete special Day schedules on special days Modify the special day schedule to match the desired access control results. On the next non-special day, Delete the schedule If you have already deleted the special Day or special Schedule Option A - Delete the special day from the Host and the Controller     Perform a station restore to force the controller to use the current programming Option B - Determine which special day schedule type the controller is operating on Modify or create a schedule for that special day with the desired access privileges On the next non-special business day, enter the desired programming for special days.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1079 Views

Docutrend data import fails while connected to a physical 78010 tap.

Issue Docutrend data import fails while connected to a physical 78010 tap. Environment I/NET site Cause Docutrend data import fails while connected to physical 78010 tap. Resolution The system or hardware number in your active profile is different compared to the 78010 tap. Change the profile to match the site 78010 tap.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1096 Views

DPU required signal to add fingerprint verification to a card read before access is granted

Issue In addition to a card read, add fingerprint verification before access is given. What kind signal is required from this third party device to the DPU? Environment I/NET Access Control Site Cause In addition to a card read, add fingerprint verification before access is given. What kind signal is required from this third party device to the DPU? Resolution DPUs require a 26-bit Wiegand format.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1127 Views

Does Configuration Server for an i.Lon 1000 have to be running all of the time?

Issue Does Configuration Server for an i.Lon 1000 have to be running all of the time? Environment i.LON 1000 Cause The Config Server provides the path for communication to the iLon when used as an RNI. Resolution If using the i.Lon 1000 as an RNI to communicate with the LonWorks network, then the Config Server must be open.   If the i.Lon 1000 is being used as a router (not RNI), it is not necessary to have Config Server running unless you are in the configuration process for the router.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1163 Views

Dial Network and LNS Network in the same Vista Network

Issue Is it possible to have a Dial Network and LNS Network in the same Vista Network? Environment Vista Network Dial Network LNS Network Cause  A dial up network communicates via the PC comport directly (no LTA driver), therefore there is no conflict with LTA card drivers (like the conflict that occurs between Classic and LNS networks). Resolution There is no problem having both types of communication in a single Vista network.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1298 Views
  • « Previous
    • 1
    • …
    • 263
    • 264
    • 265
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of