Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

What is the difference between an Internal Analog Input (AI) and Pulse Input (PI) when it comes to fractional digits?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the difference between an Internal Analog Input (AI) and Pulse Input (PI) when it comes to fractional digits?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1272 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the difference between an Internal Analog Input (AI) and Pulse Input (PI) when it comes to fractional digits?

Picard Product_Support
‎2018-09-06 03:26 PM

Issue

What is the difference between an Internal Analog Input (AI) and Pulse Input (PI) when it comes to fractional digits?

Environment

I/NET 7700

Cause

It is not always clear the difference between Internal AIs and PIs when it comes to fractional digits. A clarification note will be added to the next release of the I/NET 7700 Operator Manual, but until then, please adhere to the following when you want to display fractional digits for either Internal point types.

Resolution

Internal Analog Inputs (AIs)

Internal AIs are limited to a maximum value of 216 (65535). Internal AIs fractional digits are a direct result of the M value in the conversion coefficient table. If you want to display a value in hundredths (x.xx) the M must be .01 and the B=0 and the highest number to be displayed is 655.35. If you want a number to display a value in tenths (x.x) the M must be .1 and the B=0 and the highest number possible is 6553.5.

Internal Pulse Inputs (PIs)

Internal accumulators can accumulate not only pulses but analog values as well, but when it comes to fractional digits Internal PIs are completely different from Internal AIs. PIs are a floating point type number. This means there is no limit to the magnitude or the number of fractional digits, except that only 6 significant digits may be displayed at any one time. Therefore, the fractional digits are not ruled by the number of decimal places of the M value in the conversion coefficient table. In fact, for a Internal PI to work properly, you must utilize a conversion coefficient pair of M=1 and B=0.

An Internal PI with a calculation of P0+P1, where P0 and P1 are External AIs with values of 34.1234 and 72.5678, would be able to display the 4 decimal places with no trouble. In fact, if you used a conversion coefficient of M=.0001 and B=0 for the Internal PI, and the AIs never changed their value, the Internal PI calculation would start rounding off the value every calculation. This rounding effect would in fact be shown by the value of the Internal PI getting smaller and smaller with every scan of the Internal PI.

Remember, for a Internal PI to work properly, you must utilize a conversion coefficient pair of M=1 and B=0.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1090
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore