Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,837
  • TAC IA Series 1,820
  • TAC INET 1,458
  • Field Devices 720
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 11
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2045 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 103
  • Next »
Label: "TAC Vista" Show all articles

RAM, Remote Alarm Manager

Issue RAM, Remote Alarm Manager Environment Sigma, Micronet, BAS, Vista, RAM 1.2 Cause Configuration Controller Monitoring Scripts Output Interfaces Resolution There are 3 guides to assist in configuring RAM: Operators Manual Engineers Manual (more comprehensive than the Operators Manual) Script Editors Guide Note: There are scripts that are used in RAM. These can adapted to suit specific requirements. Copy the relevant script and rename. Use the renamed version. The scripts can be found in C:\Satchwell\Binary\Remote Alarm Manager and have the .scr extension. 
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
3795 Views

Adding startup delay for TAC Vista Server

Issue Is it possible to set a startup delay for TAC Vista server? Product Line TAC Vista Environment TAC Vista 5.1.X 32-bit Windows operating systems Cause Delaying the startup of the Vista Server is typically done to allow for other software to get up and running first. Example: LConfig needs to be running prior to Vista Server. Resolution There is two ways of adding a delay, either you do it manually like described below. Or there is a tool you can use called "Tacos Startup Delay", see community post TACOS Startup Delay Open the registry editor. Click on Start\Run and type regedit. Locate the TAC Vista 5.1.X registry key (where 'X' is the installed version of Vista) My Computer\HKEY_LOCAL_MACHINE\SOFTWARE\TAC AB\TAC Vista\5.1.X Add a string value named "TacosStartupDelay" Enter a value in seconds for the startup delay.     Additionally, this helpful utility can be used to set the delay without going into the registry editor.
View full article
Picard Product_Support
‎2018-09-10 02:59 AM

Labels:
  • TAC Vista
1329 Views

Implement temperature sensor and override on two wires of an STR-104 to a Xenta Programmable

Issue An STR-104 can be used to monitor space temperature with a Xenta programmable controller. If a zone override is also required, the most straight-forward solution is to wire the override button to a digital input on the same controller. However, if those wires were not installed, or sufficient inputs are not available on the controller, the override button can be sent via the temperature sensor wires. Environment STR-104 Xenta programmable controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause If enough wires were not run, or sufficient inputs are not available on the controller, the override button can be sent via the temperature sensor wires. Resolution The override signal sent via temperature sensor wires is accomplished by shorting the temperature sensor reading to ground. The Menta application senses this short and interprets it as a zone override. On the STR-104, short terminals 12 to 14 (Therm to Switch) On the STR-104, short terminals 11 to 15 (M to MX) Terminals 11 and 12 on the STR-104 go to M and B1 on a Xenta programmable (for example). Download this Menta macro for use in the programmable Menta application. While the button is pressed, the temperature will jump to a failed-shorted value of 300+ °F.  The attached Menta app will read in this jump, filter it out from a failed sensor, and enable an override for an adjustable duration.
View full article
Picard Product_Support
‎2018-09-06 01:21 PM

Labels:
  • TAC Vista
1619 Views

Detailed I/NET alarm data in Vista alarm queue

Issue When integrating I/NET into Vista; by default I/NET alarms do not show the station name, link name, or device name (point name). Environment I/NET Seven Vista 4.5 and up Cause The settings on the $AlarmColumns object in Vista do not have the I/NET column fields checked by default. Resolution To customize the Vista alarm queue with the proper fields for I/NET alarms please follow these steps. Click on the root level TAC Vista object in the Vista tree. Right click on the $AlarmColumns object and choose properties. Check the desired boxes in the Columns fields. Note: The link name selection will display the I/NET link name that the alarm originated from. Example: Link 5 South Campus The station name field will display the I/Net station name that the alarm originated from. Example: AHU5 The device name field will display the physical point name programmed within the I/NET controller. Example: OA Damper The site field is only needed when using DLA (distributed link architecture) and will display the name of the DLA site Example: Site 1 North Campus
View full article
Picard Product_Support
‎2018-09-10 01:59 AM

Labels:
  • TAC INET
  • TAC Vista
1089 Views

PT100/PT1000 sensors used with Xenta controllers

Issue Do Xenta controllers support PT100/PT1000 sensors for measuring the temperature? Environment Xenta Controller TAC Menta PT100/PT1000 Temperature sensors Cause Requirement to measure the temperature using PT100/PT1000 Temperature sensors. Resolution PT100/PT1000 sensors are not supported within any of the Xenta controllers.  The following is a method to achieve this using Menta: When using PT100/PT1000 to connect to a thermistor input, Menta Logic is required to add a polynom using the expression block. It is also strongly recommended to implement some calibration software in Menta to allow for fluctuations in resistance for every input that PT100/PT1000 is connected to. If a sensor is replaced / changed, re-calibration will be required. Sample experiment results and Menta Logic's are available here.
View full article
Picard Product_Support
‎2018-09-10 03:04 AM

Labels:
  • TAC Vista
1733 Views

Self-Registration Error while installing Remote Workstation

Issue Self-Registration Error while installing Remote Workstation (some of the "dll" files are not installed). The following files did not self-register or unregister. Environment TAC Vista 5.0.X Remote Workstation Cause When uninstalling the TAC Vista Remote Workstation some of the "dll" files will not un-install from "TAC Shared" folder (Find the TAC Shared folder in "C:\Program Files\Common Files). Due to this, while reinstalling the Remote Workstation pop-up an error-"Self-Registration" and few "dll" cannot install, then the Installation terminates. Resolution Uninstall the Remote Workstation. Delete the TAC Shared folder from C:\Program Files\Common Files Reinstall Remote Workstation. Note: Install .NET Framework 2.0 before installing the Remote Workstation software.
View full article
Picard Product_Support
‎2018-09-10 01:33 AM

Labels:
  • TAC Vista
1997 Views

Detect timeout in a Menta application

Issue How can a communication heartbeat time be detected in Menta? Can you detect if a value has not changed for more then a specified time period? Environment Menta Cause There are multiple methods to detect a timeout scenario and which method to use will likely depend on the specific criteria of your application. The included examples are intended to indicate some of the options available that can be built upon to customize your application. Resolution These methods can be used to detect if another device has stopped communicating or if another portion of your process logic is stuck. Timeout Simple (Click image for AUT file) This macro block will output a value of one when the input value has not changed for the DelayOn time period and you do not require the previous value for processing. Timeout Complex (Click image for AUT file) This macro block will preserve the last value for use in your process logic if that is necessary.
View full article
Picard Product_Support
‎2018-09-10 01:32 AM

Labels:
  • TAC Vista
1373 Views

Sensors for Clean Room, Swimming Pool, Outdoor Temperature, Explosion Proof, and Color

Issue What sensors can be used in Clean Rooms  What sensors can be used outdoors for temperature measurement What sensor can be used in a swimming pool What sensor would be explosive proof What color is the wall sensor and are custom colors available Environment Building Automation System such as I/NET, Vista, or Continuum at a site containing a clean room, swimming pool, or outdoors Cause Questions concerning the uses of Schneider Electric sensors in Clean Room applications Questions concerning temperature sensors for Outdoor installations Questions concerning temperature sensors for swimming pools Questions concerning explosion proof sensors* Questions concerning color and custom colors for sensors Resolution All the Schneider Electric temperature sensors found in the HVAC Sensor Catalogue as well as on iPortal provide high accuracy and can be mounted on the wall, in ducts, or in a J-Box. Appendix A provides the accuracy for each of the temperature sensors. Color: STR series wall sensors are: Front Cover: White NCS S-0500 N Core Plate: White NCS S-0500 N and Gray NCS S-2500 N Base Plate: Gray NCS S 1502-R Manufacturing in custom colors in not available. One option could possibly to have the sensors locally custom finished to meet customer's requirements. While there is not a direct cross reference to RAL colors, our engineering team has found the closest alternates. Please see the attached pdf. Clean Room: Depending on the specified limits of the clean room, the variety of sensors offered by Schneider Electric are possible solutions. Thing you may want to research are the standards required for the site. Clean rooms are a controlled environment where products are manufactured. It is a room in which the concentration of airborne particles is controlled to specified limits. Eliminating sub-micron airborne contamination is really a process of control. These contaminants are generated by people, process, facilities and equipment and must be continually removed from the air. The level to which these particles need to be removed depends upon the standards required. The most frequently used standard is the ISO 14644 Standards, which were first formed from the US Federal Standard 209E Airborne Particulate Cleanliness Classes in Cleanrooms and Clean Zones.  ISO 14644 is a document that establishes standard classes of air cleanliness for airborne particulate levels in cleanrooms and clean zones. Strict rules and procedures are followed to prevent contamination of the manufactured product. The only way to control contamination is to control the total environment. Air flow rates and direction, pressurization, temperature, humidity and specialized filtration all need to be tightly controlled. Outdoor:  Schneider Electrics selection of Outdoor Temperature Sensors are the STO100, 200, 500, & 600. These outdoor sensors are intended for outdoor wall mounting. Variants are available for Vista, I/NET, Continuum and Satchwell systems. The body has a 20mm conduit entry and the product is supplied with a conduit gland. Range -40 to +90 °C Accuracy See Appendix A: Table A, C, F in the attached HVAC Sensor Catalog.pdf Outdoor Temperature Sensor STO100 Order Code 5141100010 Part Number STO100 System Vista, Xenta Outdoor Temperature Sensor STO200 Order Code 5123246000 Part Number STO200 System I/NET Outdoor Temperature Sensor STO500 Order Code 5141104010 Part Number STO500 System Continuum Outdoor Temperature Sensor STO600 Order Code 5126060000 Part Number STO600 System Satchwell Outdoor Temperature Sensor STO600D Order Code 5126000000 Part Number STO600D System Drayton Outdoor Temperature Transmitters STO300 The STO300 transmitter is supplied as a complete unit, comprising a sensing element and an amplifier mounted in a housing which is resistant to ultraviolet light. The transmitter is intended for mounting on an outside wall, on the north side where possible. The transmitter is connected over a 2-wire cable, which serves both as power supply and signal transmission. The reading of the measured signal is made over an external load resistance. Outdoor Temperature Sensor STO300 -50/50 Order Code 006920501 Part Number STO300 -50/50 System All Note for each of these outdoor sensors, find the Description, the Order Code, Part Number, and the System it works with for the iBAS (intelligent Building Automation System) Please note the difference in Weatherproof and Outdoor. I put a lot of these outdoor sensors in at a university in Texas, and always installed in places that were a little protected. I found that under porches, up under the eves and out of the sun, or along a loading dock out of the rain and ice gave me accurate readings. Swimming Pool: In the piping system of a swimming pool is a corrosive environment with steadily harmful and gradually destructive minerals and chlorine in the water which present a challenge finding sensors able to withstand for extended periods of time. Schneider Electric makes several immersion temperature sensors. Beginning on page 12 of the above HVAC Catalogue, there is a variety of immersion sensors for the different iBMS lines.  One example is the STP660 is a Temperature Sensor for the European market, and intended for immersion mounting in pipe or the circulating systems. The stainless steel probe is a good solution but remember,  if the sensor is to be installed in pool water that contains chlorine, the best bet is to use a stainless steel pocket. I suppose it all depends on if sensor is in pipe associated with the secondary pool side of the system or the heating side of the system. If the sensor head is in an area exposed to Chlorine, then there may be an issue.  Chlorine may attack the solder connections of the wired joints inside the sensor. In the old days products from Satchwell used to produce special sensors for such applications where the wire connections were varnished in order to prevent corrosion. I think at the end of the day, our sensor would have a similar life expectancy to other devices in the plant that were no designed for use in such corrosive atmospheres. Explosion proof sensors: Schneider Electric does not manufacture explosion proof sensors. We do not partner with another manufacturer who provides such sensors. The closest is an 3rd party explosion proof enclosure with one of our available sensors. Our sensors are designed for building installations and if in extreme environments, we suggest enclosures.  
View full article
Picard Product_Support
‎2018-09-10 12:44 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • TAC INET
  • TAC Vista
3394 Views

EGL, EGRL, EGLL5 Temperature Sensors and Resistance Chart

Issue Using the EGL, EGRL, EGLL5 which are obsolete Environment Vista Cause temperature/resistance data of EGRL, EGRLL, EGRL5 temperature sensors, or customer needs data to calibrate the sensors. Resolution EGL is replaced by the STD100-250 EGRL - STR100 EGLL  (2 thermistors) was not really replaced, as the average temp calc nowadays is done in the controller. The room version was named EGRLL. All these are for the Vista series. For more information regarding sensors, please visit Exchange Extranet.    Click here for the temperature/resistance chart for the old EGL, EGRL, EGLL5 Click here for the original Product and Installation pdf.
View full article
Picard Product_Support
‎2018-09-10 12:54 AM

Labels:
  • TAC Vista
4468 Views

Schneider Electric Building Automation Systems and FDA Compliance

Issue The FDA requires Building Automation systems to meet their standards which are outlined in Chapter 21 CFR and FDA Part 11. Environment Vista I/NET Andover Continuum TAC I/A-series Satchwell Sigma Cause Finding documentation on Schneider Electric Building Automation Systems which comply to The Food and Drug Administration rules. Resolution Vista 21CFRPart11 support in TAC Vista 5.pdf FL-VISTA-REGIND-A4 mod RO.pdf I/NET - currently unavailable Andover Continuum With the addition of the 21 CFR Part 11 compliance pack, Continuum can meets these requirements. Satchwell Sigma SoftwareOverview.pdf Advanced Security Module.pdf Note: Validation to 21CFR Part 11 can only be performed on whole operational systems and as such, a sub-system comprising the Satchwell Sigma building management system cannot be validated in it own right. Satchwell Sigma would normally be validated as part of a whole operational system. TAC I/A Series - currently unavailable
View full article
Picard Product_Support
‎2018-09-10 12:30 AM

Labels:
  • Andover Continuum
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
4349 Views

Check Xenta Trend Log impact on Vista performance

Issue Trend logs that are stored in a Xenta Programmable must be uploaded to the Vista Server at certain intervals/when certain capacities of memory are reached. If there are many Xenta Trends all trying to upload to the server simultaneously, it can bog down the network and cause communication problems. This utility will help diagnose these situations by providing a summary of all trends and flagging any areas of concern. Environment Vista Server Xenta Programmable controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Xenta Trend Logs Cause Setting a Xenta trend to log values too frequently Setting a Xenta trend to upload at too low of a memory capacity Resolution This utility was created by Benjamin Roswall at Schneider Electric Denmark. It is not an official release, nor is it supported by Schneider Electric. While it has been tested and used successfully, it should be used at your own risk. Click here to download the TAC Vista Check Log Utility. Run the .exe file Choose Open File on a .des file (instructions for generating the .des shown below) Choose Check Logs, evaluate any highlighted line items. Create a network description (.des) of Xenta Trends Open the Database Generator In Vista Workstation, click on Tools > TAC Vista Database Generator Or go to Start > All Programs > Schneider Electric > TAC Tools X.X.X > Database Generator Log in to TAC Vista Server   Select Database > Export Data from Database...   Click on Browse in the Object box   Select Device navigation and select the TAC Vista node you want to analyze. Click OK.   Click on Browse in the Object type box. Select "Trend Log - Xenta" in the drop down box. This is VERY important. The check log program will crash if you choose anything else.   Leave the text boxes in the Object data box as they are. This is also important. Click on OK.   Your export should be generated. Click on OK.   Save the .des file with File > Save As... You can now open the TAC Vista Check Log utility to analyze the trend logs.
View full article
Picard Product_Support
‎2018-09-10 12:13 AM

Labels:
  • TAC Vista
1304 Views

Utility to verify TGML graphic links and bindings

Issue This utility, TAC Vista Check References, will check references (every binding and every link) on every graphic at once and provide a summary of any empty or invalid database paths. It will also allow you to correct these broken or missing links and bindings. Environment TGML Graphics Vista Workstation Links/Bindings Cause Viewing the bindings or links of a TGML graphic can traditionally only be done on individual graphics one at a time. In addition, to see if a network path is invalid, it must be clicked on and will turn red if there is a problem. Resolution This utility was created by Benjamin Roswall at Schneider Electric Denmark. It is not an official release, nor is it supported by Schneider Electric. While it has been tested and used successfully, it should be used at your own risk. Download the TAC Vista Check References Utility by clicking here. Unzip the file onto the harddrive, view extracted files Double click TAC Vista Check References.exe Make sure Vista Server is running, click Login and log in to the database Choose whether to check for empty paths, and whether to validate .[OBJECT] bindings Click Check A summary of the network can be viewed and saved by switching between tabs.
View full article
Picard Product_Support
‎2018-09-06 01:41 PM

Labels:
  • TAC Vista
1657 Views

Creating I/NET gpg, Vista IV OGC "Symbols" functionality in TGML graphics

Issue Large libraries of jpg and bmp graphics exist that have frames of damper movement, or different colors for a pump depending on status. How can these be brought into TGML and used in the same way that they were once used in I/NET gpg or Vista IV OGC graphics? Environment TGML Cause TGML has a rich set of animation and rotational tags for vectored images, however if a large library of jpg or bmp files exists, it can be imported into TGML and used like it was before in other graphics programs. Resolution Click here to download a sample TGML graphic that contains the two examples below. They use jpg images to represent a damper at different angles of rotation. The first example deals with an open/close damper and the second with an analog output. The four images used are: 0° 30° 60° 90° In TGML, these would be imported using the "Insert Picture" tool and then stacked on top of each other. Open/Close Damper A 0° image on the bottom, 90° image on top. Binding on the 90° image toggles the Visibility attribute of the fully open image using ConvertValue tags. If the value equals 0 the "open" image is hidden, displaying the closed image. If the value is 1, the "open" image is visible, hiding the closed image below, and showing the damper fully open. Analog Damper A 0° image on the bottom, stacked on top with 30°, 60°, 90° images. Instead of using SignalEqualTo attribute of ConvertValue, used SignalMoreThan and SignalLessOrEqualTo to create "bands" around which each image would become visible. Because of how they are stacked on stop of each other, only one will ever show.
View full article
Picard Product_Support
‎2018-09-06 01:44 PM

Labels:
  • TAC Vista
963 Views

Selection of a Schneider Electric Heat Meter.

Issue Using the selection tool to select the correct meter. Environment Heat Meters Cooling Meters Cause Selecting the incorrect meter can lead to loss of water flow and increased system pressure. Resolution Selecting an appropriate Heat Meter can be achieved using the selection tool. To view or download the tool click here. For the Product Announcement click here. To view the Online version of the tool please click here. The selection of a Heat Meter requires the following information; 1 - The maximum water flow through the system. 2 - The location of the meter, (Flow or Return). 3 - The size of pipe work where Heat Meter is to be installed. 4 - The media type, heating, cooling or both. 5 - Using the selection tool is made easier by using the Auto filter drop down selection arrows. These allow you to filter the selection on a particular area, i.e. "Flow Rate" as shown below. The Heat Meter part number is established as follows; 1 - Digits 1,2 - Heating, Cooling or Combined. 2 - Digits 3,4 - Flow rate. 3 - Digits 5,6 - Body length and connections. 4 - Digit 7 - Threaded/Flanged. 5 - Digit 8 - Heat Meter location Flow / Return. 6 - Digit 9 - Communications type. 7 - Digit 10 - Display option. 8 Digits 11,12,13 - Revision. To view a warning about the under sizing of Heat Meters, please click here. New serial communication modules are now available for Modbus RTU and BACnet MS/TP interfaces.
View full article
Picard Product_Support
‎2018-09-11 09:03 AM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
2670 Views

Supplemental Documentation on the Menta SEQ block

Issue Supplemental Documentation on the Menta SEQ (sequence) block Environment Menta Cause The document is intended to clarify the inputs and configuration parameters of the Menta SEQ block and when/how to use them. Resolution Click here to download a copy of this document in PDF format Click here to download the example Menta macro   Supplemental Documentation: Menta SEQ   A Brief Overview of Sequence Block The Sequence block is used to start N of M stages based on a percentage input. Each stage is represented by a single bit in the output of the block which requires calculation to determine if each stage is off or on. The Sequence block also provides the ability to rotate the stages, specify a delay between multiple stages activating, and a hysteresis to adjust the activation or deactivation of stages. The Sequence block is ideal for rotating operating stages that have high frequency of change. It is not the proper block to use for run time balancing between multiple stages. Input of the SEQ Block The input expects a 0-100 value where a 0 represents zero stages active and 100 represents all stages are active. Configuration Parameters of the SEQ Block Stages The number of stages to activate at 100% input. Rotate Rotation Flag. If Rotate is set to 0 then the first stage will always be active if 1 stage is required. If Rotate is set to 1 then the first stage to activate will be the first stage to deactivate. Period Time delay(ms) between multiple stages activating. Hysteresis Hysteresis is used to offset the activation or deactivation % for each stage. If the Hysteresis is positive then it will shift the activation % higher by that amount. If the Hysteresis is negative then it will shift the deactivation % lower by that amount. Normal Operation of 4 Stages:    Stage 1 Activation Stage 2 Activation Stage 3 Activation Stage 4 Activation Input 20% 40% 60% 80%  Hysteresis of 10%    Stage 1 Activation Stage 2 Activation Stage 3 Activation Stage 4 Activation Input 30% 50% 70% 90%  Hysteresis of -15%    Stage 1 Deactivation Stage 2 Deactivation Stage 3 Deactivation Stage 4 Deactivation Input 5% 25% 45% 65% Output of the SEQ Block The number of stages active is based on the following formula: Active Stages = ((Maximum Stages +1) * Input) / 100 The number of active stages is then encoded into an Integer as the output of the SEQ block where each bit represents whether each stage is active or inactive. Since this is a single value it must be decoded using expression blocks to detect if each bit is active.
View full article
Picard Product_Support
‎2018-09-06 01:48 PM

Labels:
  • TAC Vista
1984 Views

How to deactivate a NIC852-SW license to allow it to be transferred to another PC?

Issue How is an active Orion Stack license transferred to another PC? Environment Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Loytec network interfaces Cause If you need to move your databases from one workstation to another then you must follow these procedures.  Resolution You will need to deactivate the License form your existing PC first. To carry out this follow these steps. Run up the LConfig application Select the register deactivate button Select the Deactivate NIC852-SW button Save the *.lac file on your PC Email this file to sales@loytec.com Once the license has been deactivated you can send an activation code request for the new PC. This procedure is described in the Loytec manual. Here is the NIC 852-SW extract   8.2 Product Activation When purchasing a LOYTEC product, which must be activated (e.g. NIC852-SW), you will have to go through the following steps for activation: - Start the LConfig Tool, click on 'Register / Activate'. The dialog as shown in Figure 36 will open. - If you have already purchased a NIC852-SW license, please enter your Serial Number (shipped with the NIC852-SW product) and click on ‘Request Activation File by Email’. Alternatively, write an e-mail to sales@loytec.com with both the Activation Target ID and your Serial Number in the subject. - If you have not yet purchased a NIC852-SW license, you can still send the e-mail as described in the previous point. Just click ‘not purchased yet’ before generating the email or indicate the missing Serial Number in the e-mail body. - You will receive a LOYTEC Activation file, which you import by clicking on ‘Activate NIC852-SW License...’. - Click on ‘OK’, close the LConfig tool with ‘OK’ and re-open the LConfig tool. - Configure the new NIC852 as described in Section 3.6. Here is a link to the Full NIC User manual
View full article
Picard Product_Support
‎2018-09-09 10:36 PM

Labels:
  • TAC Vista
4743 Views

License error when opening Lonmaker

Issue When opening Lonmaker a license error indicates that the license has not been activated or expired. LonMaker License Wizard This license has not been activated, or has expired. Applications using the license will not function unless you register the license. The information below shows the current usages for this license. Click Next> to activate the license: Environment NL220 Lonmaker Cause Corrupted LNS Credits on your PC Resolution Occasionally, software errors may prevent the licensing mechanism used by the LonMaker tool or LNS Applications from working properly. Use the license checking procedure below to locate your license problem, then download and install the LNS License update 2006 This will NOT fix your already corrupted license files; however, this will help prevent the license from becoming corrupted in the future. To fix the problem, use one of the following procedure : Procedure -- Checklic command: Open a Windows command prompt. To open a command prompt, click Windows Start > Run, and type cmd for Windows XP and Windows 2000, or type command for Windows 98. Then click OK. Type in the following commands, depending on the software product you are fixing (you can execute this command from any location). Press the Enter key at the end of the command:   Product Command  LNS Application checklic nsseng.exe An example of a working license is shown below. C:\>checklic nsseng.exe If you get an error in this screen Click Here for a list of errors and related repairs.
View full article
Picard Product_Support
‎2018-09-09 10:19 PM

Labels:
  • TAC Vista
1783 Views

Using an STR-350/351 as a Menta I/O Module: Menta Macro

Issue When using the STR-350/351 as an I/O module in Menta (Options > Device Specification > IO Expansion and Wall Module Table) some programming consideration must be made to keep the occupancy and setpoint in sync between the stat and the program. Both STRIN and STROUT Menta simple blocks should be used for the most robust synchronization. Environment STR-350/351 as an I/O Module Menta Cause The STR-350 takes roughly 30 seconds to recover from a power failure. The Xenta is much faster than that resulting in reading an invalid setpoint from the STR-350 on a power cycle. By storing the last known setpoint in a DELR block with the "backup" option set, the setpoint will be restored (provided the power has not been off longer than 3 days, in which case it would default back to the initial value of the backed up value). Resolution Click the pictures of the Menta macro below to download the source file. Occupancy To control occupancy from the programmable controller time schedule, the occupancy must be sent to the STR-350. In order to allow for local override commands from the stat, the occupancy must be read in from the STR-350. By allowing the programmable controller to control both the schedule and the override, the stat stays in synch with the program. Setpoint The setpoint requires a little bit of extra programming to account for a power failure. The stat will report invalid setpoints for the first 30 seconds, which will cause it to come back in an undesired state. By letting the programmable hold onto the last known setpoint, and write it back to the stat on power up, there is no change in the setpoint after a power loss. Looping the setpoint in/out from the stat keeps everything in synch with the program, including stat adjustments. Note: This code protects against unwanted behavior following a power failure. A download the Xenta base unit will not trigger the Reset block protection and will cause the stat to go outside the bounds of, and then be limited by, either the high or low setpoint limit. Precaution should be taken following a download to manually reset the setpoint to the desired value. Additional logic for controlling the setpoint remotely could be incorporated into this code. If these macros are going to be used with a STR-350/351 set in degrees Celsius; make sure to change all initial values within the setpoint range. If the initial values are outside of the setpoint range, then the setpoint will always default back to the last known value.
View full article
Picard Product_Support
‎2018-09-09 10:06 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1301 Views

How to Retrieve Log values from TAC Vista MSSQL Database

Issue How to Retrieve Log values from TAC Vista MSSQL Database Environment TAC Vista and MSSQL Database Cause Requires third party access to retrieve Log Values from TAC Vista MSSQL Database Resolution 1. Refer to the attached PDF document for the procedure 2. Note: You’re limited to retrieve only one log object at a time
View full article
Picard Product_Support
‎2018-09-09 09:48 PM

Labels:
  • TAC Vista
1482 Views

Configure Xenta 102-AX using TGML in a Vista Classic Network (no LNS plug-in available)

Issue Configuring and monitoring the Xenta 102-AX is traditionally done through the LNS Xenta 102-AX Plug-In, but how can it be done in a Vista Classic Network where no LNS plug-ins are available? Environment Vista 5 Classic Network TGML Xenta 102-AX Vista Workstation ONLY -- This plug-in is not compatible with Webstation or XBuilder graphics at this time. Cause LNS Plug-ins are not available in a Vista Classic Network. Resolution All of the values that are written to by the LNS Plug-In are public and available through the Vista front end. So if only one or two signals need to be set for each box, this can be accomplished by locating them in the Vista network and writing the desired values to them.  This does require some fairly intimate knowledge of the Xenta 102-AX and Plug-In. The alternative is: Download the Xenta 102-AX TGML Plug-in by clicking the image below.  Unzip the contents to the hard drive. Open the TGML file. Select File > Save As > Vista Database Object Navigate to the first Xenta 102-AX in the network. Drill down into the 102-AX on the same level with Node_Object and VAV_Controller modules. Give the plug-in graphic a name and save. Right click on the Graphic object in Vista Workstation and select Copy Navigate to the next Xenta 102-AX and select Paste Shortcut. Since all bindings are automatically populated with relative bindings, copying and pasting shortcuts will automatically display data for the associated Xenta 102-AX. Repeat Step 8 for all Xenta 102-AXs in the network.
View full article
Picard Product_Support
‎2018-09-09 09:22 PM

Labels:
  • TAC Vista
1693 Views
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 103
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of