Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 102
  • Next »
Label: "TAC Vista" Show all articles

Vista crashes when attempting to open a TGML Graphic

Issue When opening a TGML graphic page you get an error and Vista Shuts Down. Product Line TAC Vista Environment Windows 7 Vista 5.1.X Cause The monitor is using the DIVI Digital Video Input. Resolution If Vista Crashes when you attempt to open a TGML graphic then change to the analog VGA output on your video card. Here is A DVI lead Here is a VGA lead Hardware acceleration on you video card can also cause a similar issue. Please see Vista Workstation is crashing/shutting down when graphics begin to load for more information on hardware acceleration issues.
View full article
Picard Product_Support
‎2018-09-09 10:08 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:38 PM

Labels:
  • TAC Vista
1722 Views

Check the size of the SQL database for Vista trend logs and events

Issue Check the current size of the SQL database associated with a Vista database to ensure that it hasn't become full. Product Line TAC Vista Environment SQL Cause The SQL database that installs automatically with Vista has limitations on the amount of data it can hold.  Most often, this is plenty of space for many years of trending without issue.  But if a site is very old or has many trend logs defined, it can out grow the SQL database.  Limits are: Vista IV - Vista 5.0.0 MSDE:  2 GB Vista 5.0.1 - 5.1.6 SQL 2005 Express:  4 GB Vista 5.1.7 and newer SQL 2008 Express:  10 GB Resolution This procedure checks the log size from the Vista Workstation: In Vista Workstation, click on the Vista Server in the folder pane Right click on $Backup_LDB and select Properties Scroll to the bottom and make note of the Database Size property (shown in grey).  This is the size of the database in MB. This procedure checks the file size on the hard drive.  The assumption has been made that this is not a custom install, but the default SQL installed with Vista Server: Open Windows Explorer Navigate to C:\Program Files\Microsoft SQL Server\MSSQL.1\MSSQL\Data Locate files: taclogdata.mdf taclogdata_log.ldf Note:  If there are multiple instances of SQL installed on the PC, there may be MSSQL.1, MSSQL.2, MSSQL.3, etc.  Find the SQL instance that contains the file names listed above. Highlight both files and look at the bottom of the window on the status bar.  The combined size of these two files is shown.  This can be used to determine is the SQL database is full and requires a purge.  To purge a Vista IV SQL database, see How to create a new database or purge a full SQL (i.e. it has hit the limit of 2G) in Vista IV. To purge a Vista 5 SQL database, see Vista 5 full SQL database issue. If purging is not an option, then the SQL will need to be upgraded to a full version of SQL (not express).  To see the different options, see Vista Database Sizing and SQL Server Selection.
View full article
Picard Product_Support
‎2018-09-07 02:30 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:33 PM

Labels:
  • TAC Vista
1538 Views

How to solve a system alarm that is Physical device not defined/configured?

Issue In the alarm window of TAC Workstation, there is a system alarm that is Physical device no defined/configured. After you acknowledge it, it will occur again. Product Line TAC Vista Environment TAC Vista workstation Xenta 280/300/401 Xenta server LOYTEC NIC-USB Cause The controller address cannot be verified correctly in TAC Workstation. For example, a TAC Xenta Group name or number is in conflict with another TAC Xenta Group’s. Resolution If multiple TAC Xenta Groups or Lonworks networks are created, you must verify the Lonworks network’s name or TAC Xenta Group name and number is unique. The TAC Xenta Group default number is 254. The different number must be given to the different TAC Xenta Group even though the TAC Xenta Groups are beneath the different Lonworks network.   You can also reference to the articles System alarm message, Physical device not defined/configured and Physical device not defined/configured about this issue.
View full article
Picard Product_Support
‎2018-09-11 05:34 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:30 PM

Labels:
  • TAC Vista
1563 Views

Continuous "Waiting for unit to restart" when downloading application in Vista Classic network

Issue When using the "Commission and Download" command in Vista Workstation the controller being downloaded is failing with a "Completion Event Failure" and has multiple "Waiting for unit to restart" error messages. Product Line TAC Vista Environment Vista Server/Workstation Classic Network Cause The controller being downloaded and presenting with this error message typically has been functioning and communicating on the network and an application update is being downloaded. The unit is busy responding to other communication (TAC network variables, Xenta group communication, etc) and can not devote full attention to the application download. By setting the neuron status to unconfigured, the controller can focus only on the application download. Resolution Right click on the Xenta programmable controller and select Advanced Operation > Neuron Unconfigured. Right click on the Xenta programmable controller and select Commission and Download. It is unnecessary to set the Neuron status back to Configured because this is part of the Commission and Download process. Similar steps are available for a LNS network and are discussed in "Completion event failure" and/or "Waiting for device to restart" errors when downloading a previously commissioned controller.
View full article
Picard Product_Support
‎2018-09-10 12:26 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:26 PM

Labels:
  • TAC Vista
1637 Views

Using Demo License to Configure 3rd party OPC Server in Vista 5.1.8

Issue The demo license used to access the OPC server configuration must be removed from the license Files folder in the new Flexnet License Server for the service to start. Upgrade to a Vista 5.1.8 will not allow access to the OPC Server Configuration. Product Line TAC Vista Environment Vista 5.1.8 using 3rd Party OPC where Vista is a client Cause Vista.OPCTool = Allows accessing the OPC Server for configuration Vista.Server.OPCClient license= Allows a connection to get the configured OPC points into Vista. Systems engineered to use 3rd Party OPC Server may only contain a Client license for connectivity, using the Demo for the initial configuration and servicing of the OPC Server. In Vista 5.1.8, the  Flexnet License Software  will not allow a Demo license to be present in conjunction with a Site License. This is corrected in Vista 5.1.9. More information can be found in License troubleshooting in Vista 5.1.8 or greater. Resolution Purchase the Vista.OPCTool to add to the existing Site License file. Best practice is to have a separate folder for your demo licenses, and reference the physical path to that folder. See below:  WSDKHE9781;C:\Program Files (x86)\Schneider Electric\License Files Demo
View full article
Picard Product_Support
‎2018-09-07 11:38 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:56 PM

Labels:
  • TAC Vista
1462 Views

Which signal types can be connected to a UI on a Xenta I/O Modules?

Issue Which signal types can be connected to a UI on a Xenta I/O Modules? Product Line TAC Vista Environment Xenta 451A/452A, 421A/422A Cause UI is short for universal input, which means that these inputs are compatible with many different input types. Resolution Supported input signal types are: Thermistor: 1.8 KΩ at 25 °C or 10KΩ at 25 °C; Voltage: 0 to 10VDC; Current: 0 to 20mA; Digital Input. Refer to the following link about 1.8KΩ and 10KΩ thermistor compatibility: 1.8k Thermistor compatibility with Xenta controllers 10k Thermistor compatibility with Xenta controllers
View full article
Picard Product_Support
‎2018-09-10 05:16 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:53 PM

Labels:
  • TAC Vista
3718 Views

Are 8 byte unsigned integers (UI8) supported in Vista OPC client?

Issue Are 8 byte unsigned integers (UI8) supported in Vista OPC client? Product Line TAC Vista Environment TAC Vista 5.1.X Vista OPC tool Cause Not all OPC data types (canonical data types) are supported by OPC server. UI8 variables show a question in OPC tool. If the Canonical Type column shows a question mark for the variable (or tag) then this means that Vista has been unable to identify or does not support the data type. Resolution If possible divide the OPC tag/variable into 2 x 4 byte registers. It could also be worth checking what the expected maximum value is for that register and seeing if that value will fit in a UI4 (unsigned integer 4 byte). An alternative solution, although the functionality must be checked by the engineer is to create the variable object manually and use the canonical type "string". To do this follow the steps below: Note the name of the OPC variable to be added to Vista in the OPC tool browser window. Under the OPC server object in Vista create a 'Value - String' and give it the same name as the OPC variable. Hold down shift and ctrl and right-click the string value -  select properties. Locate the Property RA and fill in the name of the folder, variable name and the data type in the following format: folder name.variable name|data type Example of OPC naming convention including data type, in TAC Vista. Click on OK and the variable should start updating after refreshing the folder. More information on OPC data types can be found in What does the "| n" mean when viewing the properties of an OPC variable in Vista workstation?.
View full article
Picard Product_Support
‎2018-09-10 01:04 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:52 PM

Labels:
  • TAC Vista
1552 Views

NS Errors #59, #64, #51 in a row on download attempt through System Plug-In

Issue Trying to download a Xenta programmable controller through System Plug-In fails.  Errors shown are default LNS type errors shown as: (Subsystem: NS, #59). Click okay and the next error appears (Subsystem: NS, #64). Click okay and the next error appears (Subsystem: NS, #51). Product Line TAC Vista Environment TAC System Plug-In Xenta programmable controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause The steps defined in this article only relate to the NS #59 error when it is received on an attempt to download a controller through the TAC Vista System Plug-In.  It does not cover when this error is shown as a result of a commission attempt in an LNS environment.  For the commissioning error, please see The new program interface does not match the previously defined program interface. (Subsystem: NS, #59). The cause of this particular set of errors is unknown at this time, but has been witnessed a number of times.  Various troubleshooting techniques have resolved the issue. The best course of action is to try each of these methods in the order of least to most disruptive. As new techniques and procedures are discovered, they will be documented here. Resolution Remove the controller from the Vista database In the Vista System Plug-In, locate the offending controller in the right-hand TAC Pane Right click and delete the controller Update the Vista database Locate the controller in the left-hand LNS Pane Drag and drop it back into the TAC Pane Update the Vista database Attempt the download again.  Remove the controller from the LNS database In LonMaker or NL220, locate the offending controller Right click and delete the controller In the Vista System Plug-In, locate the controller (which now has a red X over it) Right click and delete the controller Update the Vista database Add the controller back to the LNS database In the Vista System Plug-In, locate the controller in the left-hand LNS Pane Drag and drop it back into the TAC Pane Update the Vista database Attempt the download again Replace the controller Physically replace the controller This should be performed in conjunction with the steps listed above for removing the controller from the LNS database.
View full article
Picard Product_Support
‎2018-09-07 11:39 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:51 PM

Labels:
  • TAC Vista
1953 Views

Failed to Read Event From Event Log Database - Vista IV

Issue Periodically a computer with Vista 4.5 will start generating the message "Failed to Read Event From Event Log Database" when opening Vista Workstation. Error: "Event Receiver Failed - Could not retrieve any events from the event log". Product Line TAC Vista Environment Vista IV Vista Workstation Windows Server 2003 Windows XP Cause Vista IV uses 2 users, TACA and TACM (appended with an underscore followed by the PC name e.g. "TACA_PCname"), to manage its SQL connection. Certain Automatic IT security procedures will either remove these users or revoke their administrator privileges. Resolution Option 1 Reinstall Vista. This will be required if the users TACA and TACM no longer exist. Option 2 Modify User rights for accounts TACA and TACM. This is only possible if the local user accounts have not been deleted. To do this you will need to follow the following steps: Log in as an Administrator Go to the control panel and look for the program User Accounts (also called User Profiles)   Find the User TACM Select Properties In the Group Membership tab, add the user TACM to the administrator group Option 3 Upgrade to Vista 5 For either Option 1 or Option 2, you will need to contact the site IT department to ensure that this issue will not come up again. Event Receiver Failed - Could not retrieve any events from the event log may also be of interest.
View full article
Picard Product_Support
‎2018-09-07 03:35 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:48 PM

Labels:
  • TAC Vista
1950 Views

Vista reports can not be edited from a remote workstation

Issue Vista reports fail to save to the server when they are being edited from a remote workstation. Product Line TAC Vista Environment Vista Microsoft Excel Cause When setting up remote workstations on a LAN or WAN, there are certain steps that must be taken. If the proper DCOM settings are not set up on every remote workstation as well as the computer that runs Vista server, there can be authority issues. Vista reports can be created but will not allow values or trends to be saved into the report. In some cases this has generated the error "The RPC Server is unavailable" as seen in Error: The RPC server is unavailable. Resolution On ALL remote workstations and the main server: Run DCOM Config 1.0.2.2.exe found in Helpful Vista Utilities - Configure DCOM instantly, Register ASP.NET. Either select Server-Workstation or Server-Workstation-Webstation. On the main server that will be used to run Vista Workstation: Run > dcomcnfg Expand Component Services Open Computers Right-click My Computer and choose properties Go to COM Security pane For Access Permissions and Launch and Activation Permissions choose to edit both Edit Limits... and Edit Default... Add users Anonymous and Everyone with Remote Access Go back to Component Services and open My Computer Open DCOM Config Browse for OPCEnum right-click and choose properties Go to Security pane Change the three options to Launch and Activation Permissions   -Use Default Access Permissions                        -Use Default Configuration Permissions                -Customize Choose Edit > add Anonymous and Everyone with Remote Access Go back to DCOM Config and browse for TACOS right-click and choose properties Go to Security pane Change the three options to Launch and Activation Permissions  -User Default Access Permissions                       -User Default Configuration Permissions               -Customize Choose Edit > add Anonymous and Everyone with Remote Access
View full article
Picard Product_Support
‎2018-09-10 08:30 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:37 PM

Labels:
  • TAC Vista
1462 Views

Navigating to a TAC Vista TGML Graphic from a SmartStruxure TGML Graphic through TAC Vista Webstation

Issue The TGML page is dynamic but looks static. Product Line EcoStruxure Building Operation, TAC Vista Environment Vista StruxureWare Interface Cause In the Release Note, page 30 says: It is possible to navigate to a TAC Vista Webstation TGML Graphic through a link in a SmartStruxure TGML Graphic. To achieve this connection a link object is created in the SmartStruxure TGML Graphic which is linked to a SmartStruxure hyperlink object that holds the TAC Vista Webstation TGML Graphic page address. Example of a hyperlink objects address in SmartStruxure that is linked to a TGML Graphic in TAC Vista: HTTP://ip_address/webstation/LoginPage.aspx?page=TgmlGraphicsPage.aspx?objectId=3074949137 Note: This will always require a login by a valid TAC Vista user, even if the TAC Vista Webstation auto login feature has been activated. Resolution The example link above is referring to a static page. For example, if the TGML page is dynamic, you will see the following in the copied link (see bold). HTTP://ip_address/webstation/LoginPage.aspx?page=TgmldynamicGraphicsPage.aspx?objectId=3074949137 You can also read the following in the release note: In order to determine the TAC Vista Webstation URL for a TAC Vista Webstation TGML Graphic the following TAC Vista Web Setting configuration must be in place: Optimized TGML Loading is deactivated Folders pane is set to Standard HTML With these settings it is possible to right-click a TGML object in the folders pane and select "Copy Shortcut." This will copy the TAC Vista Webstation URL to the clipboard and it can then be pasted into a SmartStruxure hyperlink object address field. After the shortcut has been pasted, it will have to be modified in order for the TAC Vista TGML Graphic to be displayed properly in SmartStruxure. The modification is marked with bold in the example below: Copied: HTTP://ip_address/webstation/TgmlGraphicsPage.aspx?objectId=3074949137 Modified: HTTP://ip_address/webstation/TgmlGraphicsPage.aspx?objectId=3074949137 If the link you copied was a dynamic TGML the link will look like: HTTP://ip_address/webstation/TgmldynamicGraphicsPage.aspx?objectId=3074949137 and should be modified as this HTTP://ip_address/webstation/LoginPage.aspx?page=TgmldynamicGraphicsPage.aspx?objectId=3074949137 Also reference the TAC Vista Webstation Graphics Links and SmartStruxure Integration tool on the Community.
View full article
Picard Product_Support
‎2018-09-11 11:25 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:31 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1718 Views

Use multiple license files simultaneously for Vista 5

Issue How can multiple licenses work simultaneously in Vista 5? Product Line TAC Vista Environment Vista 5 Licensing LMTools Cause Licenses may have been purchased separately and either contain different features, or additional seats. The license server can read multiple licenses and serve them up appropriately. Resolution Option 1 - Use multiple .lic files Since the filenames are the same for all .lic files sent via schneider-electric.flexnetoperations.com, you must first rename the files Put them in the License Files folder Make sure the license server is pointing to that folder (not an individual file) Reboot or Stop/Start/Reread license server using the LMTools utility. Option 2 - Merge into one .lic file Complete instructions in Manually Consolidating License Files Open each license file using a text editor. Cut and paste the "Features" into one of the files (Do not copy the file "header") Place this file in the License Files folder Reboot or Stop/Start/Reread license server using the LMTools utility.
View full article
Picard Product_Support
‎2018-09-07 03:10 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:28 PM

Labels:
  • TAC Vista
1415 Views

Limit the number of Vista workstation instances that can be opened on a PC

Issue Is it possible to limit the number of Vista workstation instances that can be opened on a PC? Product Line TAC Vista Environment TAC Vista 5.1.X Cause On a site with a number of workstation and workstation remote it is possible that all licenses will be checked out by one user on one PC, if multiple instances are running, leaving no licenses available for other users in the network. Resolution It is possible to use a license options file to reserve licenses for specific users. In this way it is possible to guarantee that a license will be available for each user. There is also an option to set the maximum number of licenses a user can use. Click on the following link to open Controlling distribution of license modules in Vista 5which contains a link to the FlexNet Licensing User Guide.
View full article
Picard Product_Support
‎2018-09-10 10:58 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:25 PM

Labels:
  • TAC Vista
1513 Views

Configuring a NIC-IP to be used in Vista

Issue Steps to setup a NIC-IP for Vista Product Line TAC Vista Environment NIC-IP Cause Setting UP a NIC-IP Resolution 1. Download and install the latest NIC software. Here is a link to this site 2. Start the LConfig application. This is located in the LOYTEC Network Interfaces menu. 3. Select the NIC-IP/RNI tab. 4. Select the Assignment & Configure button. 5. The next popup screen will search for the NIC-IP. If your NIC-IP is powered up and plugged in to the network it should appear in this list. 6. Select the NIC-IP and then select the Configure button. 7. Setup the IP address, IP Netmask, IP Gateway and DNS servers if required. Select the OK and the device will write the new configuration to the NIC-IP 8. Take note of the Assignment and change if required. Press OK and the Assignment & Configure screen will close. 9 In the LConfig application select the Device from drop down list that matches the notes assignment from step 8. 10. Press the Test Device/Serial Number button to check for the correct setup of the NIC-IP. The return screen should look like this. 11.Close the LConfig application by selecting the OK button. 12. Start the Vista server and log into Vista workstation 13. Under the Vista server object add a new Device-communications Port - Loytec 14. Select the properties of the new Communication port and select the Network interface from the dropdown list. this should be the same interface noted in step 8. 15. You can the add Lonworks networks under the NIC-IP device.    If your NIC-IP does not appear in the dropdown list, Configuring Loytec NIC in Vista discusses this related issue.  
View full article
Picard Product_Support
‎2018-09-11 05:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:24 PM

Labels:
  • TAC Vista
1787 Views

Memory Usage in TAC Menta/TAC Xenta

Issue How to check the amount of used memory in a TAC Menta/TAC Xenta application. Product Line TAC Vista Environment TAC Menta Xenta 281 Xenta 301 Xenta 401 Cause When programming applications for TAC Xenta, you may want to be able to check the size of your application, to verify that it can be downloaded to the device. Resolution To be able to check how much memory an application is using, the application needs to generated. In TAC Menta, edit mode: Select Option, Simulate to enter Simulate mode. In Simulate Mode, select Commands, Generate, to generate the application. To be able to check the Memory usage, you have to return to Edit mode, Select Options, Edit. Now you can check the Memory usage by selecting Options, Memory Usage... As this calculation is done on your PC, and not in the device, and that the memory in the TAC Xenta device is dynamic allocated, it is a recommendation to have at least 10% free memory in each category to avoid future problems. For more information about the Advanced button, please see TAC Menta Advanced Memory Usage: BPR Size Calculator.
View full article
Guinan MikaelKrantz Guinan
‎2019-05-15 03:30 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:23 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1671 Views

STR-150 does not support full duplex communication with base unit

Issue It is not possible to make any configurations or calibrations within a Xenta controller that will reflect on the STR-150. Product Line TAC Vista Environment STR-150 Vista Xenta 121 Xenta 104-A Cause Communication between any Xenta controller and STR-150 is only one-way. The STR-150 can communicate to the controller but the controller cannot communicate back to the STR-150. Resolution Any parameters that can be changed on the STR-150 must be changed at the stat itself. Complete information on the various available parameters can be found in STR-150 Manual Configuration. It is not possible to perform a calibration on the STR-150 stat in a way that will affect the readout of the STR-150 in a version prior to 1.4. The Xenta 104-A can have the space temperature calibrated within the application by changing nciTempOffset. However, when a version prior to 1.4 of the STR-150  is used with the Xenta 121 the space temperature cannot be calibrated. For more information see STR-150 Calibration Feature.
View full article
Picard Product_Support
‎2018-09-10 05:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:21 PM

Labels:
  • TAC Vista
1556 Views

Rename a Vista Server

Issue Renaming a Vista Server. Product Line TAC Vista Environment Vista Server Cause The Vista Server name will default to the PC name where the database is created. To rename the server to any desired name of fewer than 40 characters. This can be customer-appropriate or more generic than an individual's PC name; follow the steps below. Resolution Shut down Vista Server Open Vista Server setup and navigate to the Vista Database tab. Enter the desired server name in the text field "Rename Vista Server to"   Click OK Restart Vista Server.  Within a few seconds, the server's name shown at the top of the window will be updated to reflect the new name.  It will also show up in the folder view of the Vista Workstation. Note: Changing the Vista Server name after graphics have been created and bound will break the binding path for all points.  To fix up the binding paths for all graphics at once, use Change References, as shown in Change all bind paths for all bindings on a TGML or OGC graphic at once.
View full article
Picard Product_Support
‎2018-09-06 01:58 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:18 PM

Labels:
  • TAC Vista
1848 Views

TAC Vista end user licenses in virtual environment.

Issue Which licenses are required when TAC Vista is used in a virtual environment? Environment TAC Vista Cause Running a TAC Vista system in a virtual environment. Resolution No special end user licenses are necessary. License requirements are the same as if run in regular environment. Also, please see: Problems installing Vista on virtual PC and Running Vista software on an emulated environment for more details on the subject of running TAC Vista in a virtual environment.
View full article
Picard Product_Support
‎2018-09-11 12:58 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:14 PM

Labels:
  • TAC Vista
1540 Views

Regional settings might differ when TAC Vista server runs as a service

Issue Regional settings might differ when TAC Vista server runs as a service. Product Line TAC Vista Environment TAC Vista Server set to run as a service Cause If TAC Vista Server is configured to run as Windows service it might have different regional settings. This is because the TAC Vista server service needs to be configured to use a specific user account (See Registering/Unregistering TAC Vista Server as a Windows service). One common symptom would be that the date and Time stamp might have another format. Resolution To make sure that TAC Vista server is using the correct regional settings: Log on to the system once using the credential that TAC Vista server is configured to use Check the regional settings for this account.
View full article
Picard Product_Support
‎2018-09-07 01:21 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:01 PM

Labels:
  • TAC Vista
1752 Views

BMS Application assistance

Issue Need help with programming Need help to make graphic Installation questions Forum Environment BMS Security Video Cause A great way of getting help with various application programming and graphic making is to spread knowledge between all the great technician out there. A forum exist for this and people worldwide that works with SE Solution share their knowledge here. Resolution Please enter the forum by the link below. http://community.se.com/welcome
View full article
Picard Product_Support
‎2018-09-06 12:13 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:59 PM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Operation
  • Field Devices
  • TAC IA Series
  • TAC INET
  • TAC Vista
3491 Views
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore