Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Configuring a NIC-IP to be used in Vista

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring a NIC-IP to be used in Vista
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1704 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring a NIC-IP to be used in Vista

Picard Product_Support
‎2018-09-11 05:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:24 PM

Issue

Steps to setup a NIC-IP for Vista

Product Line

TAC Vista

Environment

NIC-IP

Cause

Setting UP a NIC-IP

Resolution

1. Download and install the latest NIC software. Here is a link to this site

2. Start the LConfig application. This is located in the LOYTEC Network Interfaces menu.

3. Select the NIC-IP/RNI tab.

4. Select the Assignment & Configure button.

5. The next popup screen will search for the NIC-IP. If your NIC-IP is powered up and plugged in to the network it should appear in this list.

6. Select the NIC-IP and then select the Configure button.

7. Setup the IP address, IP Netmask, IP Gateway and DNS servers if required. Select the OK and the device will write the new configuration to the NIC-IP

8. Take note of the Assignment and change if required. Press OK and the Assignment & Configure screen will close.

9 In the LConfig application select the Device from drop down list that matches the notes assignment from step 8.

10. Press the Test Device/Serial Number button to check for the correct setup of the NIC-IP. The return screen should look like this.

11.Close the LConfig application by selecting the OK button.

12. Start the Vista server and log into Vista workstation

13. Under the Vista server object add a new Device-communications Port - Loytec

14. Select the properties of the new Communication port and select the Network interface from the dropdown list. this should be the same interface noted in step 8.

15. You can the add Lonworks networks under the NIC-IP device. 

 

If your NIC-IP does not appear in the dropdown list, Configuring Loytec NIC in Vista discusses this related issue.

 

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 13680
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore