Check the size of the SQL database for Vista trend logs and events

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Check the size of the SQL database for Vista trend logs and events
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1501 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Check the size of the SQL database for Vista trend logs and events

Picard Product_Support
‎2018-09-07 02:30 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:33 PM

Issue

Check the current size of the SQL database associated with a Vista database to ensure that it hasn't become full.

Product Line

TAC Vista

Environment

SQL

Cause

The SQL database that installs automatically with Vista has limitations on the amount of data it can hold.  Most often, this is plenty of space for many years of trending without issue.  But if a site is very old or has many trend logs defined, it can out grow the SQL database.  Limits are:

  • Vista IV - Vista 5.0.0 MSDE:  2 GB
  • Vista 5.0.1 - 5.1.6 SQL 2005 Express:  4 GB
  • Vista 5.1.7 and newer SQL 2008 Express:  10 GB

Resolution

This procedure checks the log size from the Vista Workstation:

  1. In Vista Workstation, click on the Vista Server in the folder pane
  2. Right click on $Backup_LDB and select Properties
  3. Scroll to the bottom and make note of the Database Size property (shown in grey).  This is the size of the database in MB.

This procedure checks the file size on the hard drive.  The assumption has been made that this is not a custom install, but the default SQL installed with Vista Server:

  1. Open Windows Explorer
  2. Navigate to C:\Program Files\Microsoft SQL Server\MSSQL.1\MSSQL\Data
  3. Locate files:
    • taclogdata.mdf
    • taclogdata_log.ldf
    Note:  If there are multiple instances of SQL installed on the PC, there may be MSSQL.1, MSSQL.2, MSSQL.3, etc.  Find the SQL instance that contains the file names listed above.
  4. Highlight both files and look at the bottom of the window on the status bar.  The combined size of these two files is shown.  This can be used to determine is the SQL database is full and requires a purge. 

To purge a Vista IV SQL database, see How to create a new database or purge a full SQL (i.e. it has hit the limit of 2G) in Vista IV.
To purge a Vista 5 SQL database, see Vista 5 full SQL database issue.

If purging is not an option, then the SQL will need to be upgraded to a full version of SQL (not express).  To see the different options, see Vista Database Sizing and SQL Server Selection.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4933
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore