STR-150 does not support full duplex communication with base unit
  • STR-150 does not support full duplex communication with base unit
  • LeeCravens
    LeeCravens
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
‎2018-09-10 05:09 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:21 PM
It is not possible to make any configurations or calibrations within a Xenta controller that will reflect on the STR-150.
TAC Vista
  • STR-150
  • Vista
  • Xenta 121
  • Xenta 104-A
Communication between any Xenta controller and STR-150 is only one-way. The STR-150 can communicate to the controller but the controller cannot communicate back to the STR-150.
Any parameters that can be changed on the STR-150 must be changed at the stat itself. Complete information on the various available parameters can be found in STR-150 Manual Configuration.
It is not possible to perform a calibration on the STR-150 stat in a way that will affect the readout of the STR-150 in a version prior to 1.4. The Xenta 104-A can have the space temperature calibrated within the application by changing nciTempOffset. However, when a version prior to 1.4 of the STR-150  is used with the Xenta 121 the space temperature cannot be calibrated. For more information see STR-150 Calibration Feature.