STR-150 Manual Configuration
  • STR-150 Manual Configuration
‎2018-09-07 06:20 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:57 AM
How to change the STR-150 temperature display, setpoint adjustment range, etc.
TAC Vista
  • STR-150
  • STR Sensor
The communication between the STR-150 and the TAC Xenta 121/122 device is one way, space temperature and setpoints are sent from the sensor to the controller. Therefore some STR-150 functions (for example, the setpoint adjustment) can not be configured though Zbuilder, but needs to be done manually in the STR 150 device.
Buttons on the thermostat:
Increase Button
Decrease Button
Bypass button
Fan button
Wrench symbol
Steps of changing the STR-150 configuration are listed below:
  1. Enter Configuration:
    1. Push the fan and bypass button simultaneously for 2 seconds to enter P0
    2. In P0, hold down the bypass button and push the fan button three times to enter configuration mode.
      NOTE: the wrench symbol is lit when the STR-150 is in configuration mode.
  2. In configuration mode:
    1. Press the fan button repeatedly until reaches desired parameters (refer to the configuration table below).
      NOTE: the two digits farthest to the left on the display show the parameters, while the two digits farthest to the right show the value
    2. Use increase button or decrease button to change the value.
  3. Exit configuration mode:
    1. Push the fan and bypass button simultaneously for 2 seconds. Or, the timeout will exit configuration mode if idle.
Configuration Options:
Parameter
Function
Value/Range
Default value
P0
Software Version
P1
°C or °F temperature display
1=°C, 2=°F
1=°C
P2
Reference temperature (Reftemp)
15-30°C / 60-90°F
22°C / 72°F
P3
Setpoint or room temp.
1=Setpt, 2=Room
1=Setpt
P4
Timeout
5-90 seconds
10 seconds
P5
Fan Settings
0=No fan
1=On/Off fan
2=Two-speed fan
3=Three-speed fan
3=Three-speed fan
P6
Room temperature and setpoint display resolution
0.1 or 0.5 °C
0.2 or 1.0 °F
0.5 °C or 0.2 °F
P7
Max adjustable setpoint span above or below Reftemp (P2).
+/- 0 - +/- 5°C
+/- 0 - +/- 10°F
+/- 3° or +/- 6°F
P8
Bypass button and occupancy indication When = 2, no bypass command is sent  to the controller
1= Symbol on, off
Or flashing
2=Symbol always off
Default 1=on, off
Or flashing
P9
Setpoint as Absolute or Offset value
1=Absolute
2=Offset
1=Absolute
Click here to read STR-150 user's manual.