Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

STR-150 Calibration Feature

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • STR-150 Calibration Feature
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2365 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

STR-150 Calibration Feature

Picard Product_Support
‎2018-09-11 01:53 PM

Issue

In the past there was no way to calibrate the space temperature from a STR-150 when used with a Xenta 121 FC/HP. 

Environment

  • STR-150
  • Xenta 104A
  • Xenta 120
  • Xenta Programmables

Cause

Any calibration applied to the temperature of a STR-150 had to be done downstream of the stat in the controller. In the past when the STR-150 room stat was wired up to a Xenta 121 there was no way to calibrate the space temperature as the Xenta 121 FC/HP had no kind of Temp Offset in the controller.

Resolution

Starting with version 1.4 (released September 2013) of the STR-150, there is a calibration feature built into the stat. This feature allows the calibration to be applied before the temperature is sent down to the controller (Example: Xenta 121 controller). Below you can find out how to check the version number of the stat and how to perform the calibration.

There is not a way to upgrade older versions of the STR-150 to 1.4 or greater.


Checking the STR-150 version number

The version number of the stat can be found as parameter P0.

  1. View version:
    1. Push the fan and bypass button simultaneously for 2 seconds to display P0.
    2. The version number will be displayed here.

Using the STR-150 Calibration Feature

  1. Enter Configuration:
    1. Push the fan and bypass button simultaneously for 2 seconds to enter P0.
       
    2. In P0, hold down the bypass button and push the fan button three times to enter configuration mode.
      Note: the wrench symbol is lit when the STR-150 is in configuration mode.
       
  2. In Configuration Mode:
    1. Press the fan button repeatedly until you reach parameter F0.
      Note: The two digits farthest to the left on the display show the parameter, while the two digits farthest to the right show the value.
       
    2. Use the increase or decrease button to adjust the value. The offset scale ranges from 0-99 which corresponds to -5.0 to +4.9 degrees. If the STR-150 is setup for degrees C, then the offset is exact. If the STR-150 is setup for degrees F, then the offset is recalculated to a corresponding value.

       
  3. Exit Configuration Mode:
    1. Push the fan and bypass button simultaneously for 2 seconds or allow the idle timeout to exit configuration mode on its own.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 17064
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore