NS Errors #59, #64, #51 in a row on download attempt through System Plug-In

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • NS Errors #59, #64, #51 in a row on download attempt through System Plug-In
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1957 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

NS Errors #59, #64, #51 in a row on download attempt through System Plug-In

Picard Product_Support
‎2018-09-07 11:39 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:51 PM

Issue

Trying to download a Xenta programmable controller through System Plug-In fails.  Errors shown are default LNS type errors shown as:

  • (Subsystem: NS, #59). Click okay and the next error appears
  • (Subsystem: NS, #64). Click okay and the next error appears
  • (Subsystem: NS, #51).

Product Line

TAC Vista

Environment

  • TAC System Plug-In
  • Xenta programmable controllers
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B

Cause

The steps defined in this article only relate to the NS #59 error when it is received on an attempt to download a controller through the TAC Vista System Plug-In.  It does not cover when this error is shown as a result of a commission attempt in an LNS environment.  For the commissioning error, please see The new program interface does not match the previously defined program interface. (Subsystem: NS, #....

The cause of this particular set of errors is unknown at this time, but has been witnessed a number of times.  Various troubleshooting techniques have resolved the issue. The best course of action is to try each of these methods in the order of least to most disruptive. As new techniques and procedures are discovered, they will be documented here.

Resolution

Remove the controller from the Vista database

  1. In the Vista System Plug-In, locate the offending controller in the right-hand TAC Pane
  2. Right click and delete the controller
  3. Update the Vista database
  4. Locate the controller in the left-hand LNS Pane
  5. Drag and drop it back into the TAC Pane
  6. Update the Vista database
  7. Attempt the download again.

 Remove the controller from the LNS database

  1. In LonMaker or NL220, locate the offending controller
  2. Right click and delete the controller
  3. In the Vista System Plug-In, locate the controller (which now has a red X over it)
  4. Right click and delete the controller
  5. Update the Vista database
  6. Add the controller back to the LNS database
  7. In the Vista System Plug-In, locate the controller in the left-hand LNS Pane
  8. Drag and drop it back into the TAC Pane
  9. Update the Vista database
  10. Attempt the download again

Replace the controller

  1. Physically replace the controller
  2. This should be performed in conjunction with the steps listed above for removing the controller from the LNS database.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5113
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.