Vista reports can not be edited from a remote workstation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Vista reports can not be edited from a remote workstation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1462 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Vista reports can not be edited from a remote workstation

Picard Product_Support
‎2018-09-10 08:30 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:37 PM

Issue

Vista reports fail to save to the server when they are being edited from a remote workstation.

Product Line

TAC Vista

Environment

  • Vista
  • Microsoft Excel

Cause

When setting up remote workstations on a LAN or WAN, there are certain steps that must be taken. If the proper DCOM settings are not set up on every remote workstation as well as the computer that runs Vista server, there can be authority issues. Vista reports can be created but will not allow values or trends to be saved into the report. In some cases this has generated the error "The RPC Server is unavailable" as seen in Error: The RPC server is unavailable.

Resolution

On ALL remote workstations and the main server:

  1. Run DCOM Config 1.0.2.2.exe found in Helpful Vista Utilities - Configure DCOM instantly, Register ASP.NET. Either select Server-Workstation or Server-Workstation-Webstation.

On the main server that will be used to run Vista Workstation:

  1. Run > dcomcnfg
  2. Expand Component Services
  3. Open Computers
  4. Right-click My Computer and choose properties
  5. Go to COM Security pane
  6. For Access Permissions and Launch and Activation Permissions choose to edit both Edit Limits... and Edit Default...
  7. Add users Anonymous and Everyone with Remote Access
  8. Go back to Component Services and open My Computer
  9. Open DCOM Config
  10. Browse for OPCEnum right-click and choose properties
  11. Go to Security pane
  12. Change the three options to
    1. Launch and Activation Permissions   -Use Default
    2. Access Permissions                        -Use Default
    3. Configuration Permissions                -Customize
      • Choose Edit > add Anonymous and Everyone with Remote Access
  13. Go back to DCOM Config and browse for TACOS right-click and choose properties
  14. Go to Security pane
  15. Change the three options to
    1. Launch and Activation Permissions  -User Default
    2. Access Permissions                       -User Default
    3. Configuration Permissions               -Customize
      • Choose Edit > add Anonymous and Everyone with Remote Access
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7742
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore