Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

720 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 22
    • 23
    • 24
    • …
    • 36
  • Next »
Label: "Field Devices" Show all articles

Replacement actuator for old TAC M44

Issue Actuator M44 is no longer available (withdrawn in 2000) and needs a replacement. Environment M44 M9B EM9 Forta Cause Depending on application, since the M44 was used for both rotating and sliding valves, a few different replacement actuators could be used. Resolution For valves with rotating stem, (TRV, VTRA, VTRE and STMG), actuators M9/EM9 can be used. For valves with linear moving stems the TAC Forta series actuator is used.
View full article
Picard Product_Support
‎2018-09-06 12:44 PM

Labels:
  • Field Devices
1973 Views

Sensitivity/accuracy of SPD310 sensor

Issue Is the SPD310 sensor accurate all the way down to 0 Pa? Environment SPD sensor Cause Application on lower measurement levels. Resolution The sensor will not be accurate all the way down to zero. Select a sensor that is mid-range for the measurement being made.
View full article
Picard Product_Support
‎2018-09-06 12:43 PM

Labels:
  • Field Devices
851 Views

Max ΔPc M800 and V231 DN25

Issue If using V231 DN25 and a Forta M800, what is the max ΔPc? Environment Forta M800 V231 DN25 Cause In case the ΔPc is too high, the Forta may not be capable of controlling the valve properly. Resolution The combination of V231 DN25 and M800 should have a max ΔPc of appr. 1150kPa (11.5Bar) For more information and details regarding the different applications, please see the data sheets for each product involved.
View full article
Picard Product_Support
‎2018-09-06 12:43 PM

Labels:
  • Field Devices
956 Views

Belimo PICCV equivalent in Schneider Electric portfolio

Issue Is there any Belimo PICCV equivalent in Schneider Electric portfolio? Environment Belimo PICCV Cause Looking for a SE equivalent product to the Belimo PICCV line. Resolution Unfortunately we do not have any matching products in the Schneider Electric portfolio
View full article
Picard Product_Support
‎2018-09-06 12:43 PM

Labels:
  • Field Devices
1224 Views

Repairs procedure for Australia / New Zealand.

Issue What to do and who to contact when a controller needs to be repaired or upgraded. Environment All Product Repairs Cause Require information on what to do and who to contact to arrange repairs of defective product, order Controller option upgrades, order Cyberstation option or software version upgrades. Resolution   PROCESS FOR CONTINUUM REPAIRS   NOTE: Repaired items are set-up in Pronto with the part number prefixed by “4-“. This is done to allow visibility for follow-up if required and costing.   Engineer completes “Andover Continuum Hardware Return Authorisation Form”; one for each controller requiring repair. Email completed form/s to TAC AP – Logistics Replenishment ( NOT the US Repair Centre). Do nothing with the controller/s at this stage. Logistics email the completed forms to US Repair Centre requesting cost to repair and turn-around time. Repair Centre replies with cost, turn-around time and RA number/s Logistics pass this information to the requesting engineer who will decide Y or N. If yes, the engineer enters a Sales Order in Pronto, informs Logistics and forwards the goods to Melbourne DC. Logistics raise a Purchase Order on Repair Centre and instruct Melbourne DC to despatch goods. After the goods are repaired they are returned to Melbourne DC where they are receipted and despatched to requestor.   Repair Forms Fill out one of the forms below (whichever applies) and send to local Logistics. Andover Continuum Return Authorization Forms - Americas & APAC OR Andover Continuum Controller Upgrade Forms - Americas & APAC
View full article
Picard Product_Support
‎2018-09-10 08:39 AM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1206 Views

Sensor pockets material specification nickel plated brass

Issue Material specification for nickel plated brass sensor pockets Product Line Field Devices Environment Sensor pockets Cause Some customers require a specification on the material used for the sensor pockets in nickel plated brass. Resolution Brass nickel plated: Turned part: Ms 58 (Cu Zn 39 Pb3) Pipe + lid: Ms 63 (Cu Zn 37) Surface nickel plated. Guidelines for nickel plating: Galvanica nickel plated ( ca. 6 – 12 µm)  
View full article
Picard Product_Support
‎2018-09-06 12:42 PM

Labels:
  • Field Devices
2016 Views

Wiring detail using STR602 temperature sensor inc. remote adjust with a CXR5805 Controller

Issue Wiring detail using STR602 temperature sensor inc. remote adjust with a CXR5805 Controller Environment STR602 CXR5605 CXR 5605 Cause The STR datasheet instructions are not clear, it details terminals 22, 23 and 24 and not what each terminal is for e.g. 0V Com, Setpoint, 'C. The CXR5805 User Guide details the old part numbers. Resolution The STR602 combines the RPW4425 and DRT3453 into one temperature and setpoint unit. The STR602 is a 3 wire device using a common 0V between the setpoint adjust potentiometer and the temperature sensing thermistor. The terminations are STR602 term 22 (Setpoint) STR602 term 23 (Temp 'C) STR602 term 24 (0Vcom) And if used on a CXR5805 STR602 term 22 (Setpoint) is wired to term 5 on the CXR5805 STR602 term 23 (Temp 'C)  is wired to term 22 on the CXR5805 STR602 term 24 (0Vcom)  is wired to term 27 on the CXR5805 Link terminals 6 and 27 on the CXR5805 
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Field Devices
1418 Views

Cross reference for Controlli MVL56PS56

Issue Schneider Electric portfolio replacement actuator for Controlli MVL56PS56 Environment MVL56PS56 Forta M700 Cause A replacement for Controlli MVL56PS56 is requested by customer. Resolution MVL56 is replaced by the Forta M700. "PS56" is a production specific specification for another manufacturer (unknown). Linkage kit required is depending on application. Part no MVL56 is replaced by MVH56 at Controlli.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Field Devices
1025 Views

SPD910 Hose connectors as spare parts

Issue Requesting replacement hose connectors for SPD910  Environment SPD910 Cause If the hose connectors are lost or broken, they may want to be replaced. Resolution The hose connectors are not listed as replacements or spare parts. However, if there is a need for numerous units, a request to the manufacturer may be done.
View full article
Picard Product_Support
‎2018-09-06 12:38 PM

Labels:
  • Field Devices
852 Views

Damper actuator replacement AM230

Issue In 2006, a new line of damper actuators was presented, replacing the previous generation. Environment M-AM230 (871-0000-010) MD20B-230 (875-1021-000) Cause Replacing old series damper actuator with new. Resolution The M-AM230 (871-0000-010) is replaced by MD20B-230 (875-1021-000). For a complete list of replacements, please see MA-430_0
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • Field Devices
1056 Views

MD10SR-TS power supply options/limitations

Issue Which power supply options are specified on the MD10SR-TS actuator? Environment MD10SR-TS Cause The data sheet may be a bit unclear at some points regarding the requirements on which power supply that can be used on this Universal actuator. Resolution AC 50/60Hz: 19,2-264 V DC: 21,6 -137,5 V
View full article
Picard Product_Support
‎2018-09-06 12:36 PM

Labels:
  • Field Devices
957 Views

Actuator selection for VTRE valves

Issue Selecting the correct actuator for the VTRE valves. Environment VTRE M9B EM9 Cause The data sheet for VTRE is currently listing the following suitable actuators: M9B-24:  860-1010-000 M9B-230:  860-1020-000 EM9:  860-1110-000 Also, it states the following: "NOTE! The VTRE valves require that the  actuators be adjusted for 90° rotational travel." However, the EM9 listed in the data sheet is 180° rotational. Resolution The correct actuators should be the following: M9B-24:  860-1010-000 M9B-230:  860-1020-000 EM9:  860-1100-000
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Field Devices
1032 Views

SPD310/SPD360, value outside of selected measurement range

Issue What happens with the output VDC value if the measured value goes outside of the specified range?  Environment SPD310 SPD360 Cause The selected value is specified by the position of the jumper. Signal output is set to 0-10V. Resolution If jumper is set to 500Pa and read value exceeds this value, the output signal will still show 10VDC. Any control signal above 10VDC is marginal, and should not be used as a measurement reference.
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • Field Devices
843 Views

What is the accuracy of the I/A Series MN-Sx S-Link wall sensors?

Issue What is the accuracy of the I/A Series MN-SX S-Link wall sensors? This information is required for submittal purposes. Environment MN-SX MN-S1 MN-S2 MN-S3 MN-S4 MN-S4-FCS MN-S5 S-Link Cause Published sensor accuracy information required for project submittal Resolution TPA-RKFD-09-0021.00 details sensor accuracy and stability as shipped from the factory and states:- Element Type: Precision Thermistor Operating Temperature Range: 0 – 50 °C (32 to 122 °F) Stability: < 0.02 °C (< 0.04 °F) per year, typical Accuracy Temperature °C Accuracy Temperature °F Accuracy 24 °C ± 0.6 °C 75 °F ± 1.0 °F 0 to 50 °C ± 1.7 °C 32 to 122 °F ± 3.0 °F
View full article
Picard Product_Support
‎2018-09-10 07:54 AM

Labels:
  • Field Devices
  • Satchwell MicroNet
  • TAC IA Series
1204 Views

CZU4201 not controlling. Always in cooling mode.

Issue CZU4201 not controlling. Always in cooling mode. Environment CZU4201 CZU DRT3451 STR611 STR612 STR Cause The CZU controller is not controlling. Resolution A DRT3451, STR611 or a STR612 is used as both temperature sensor and setpoint adjust. Check that the internal setpoint adjust within the controller is set 10'C. If not, set it to 10'C, then the internal setpoint is ignored and the remote setpoint is used.
View full article
Picard Product_Support
‎2018-09-06 12:33 PM

Labels:
  • Field Devices
959 Views

VZ*19E thread type

Issue Which type of thread is used on the VZ*19E valves? Environment VZ219E VZ319E VZ419E Cause There are different types of standards on the market for pipe threads, often depending on regions. Resolution All threaded VZ*19E valves are using BSP (British Standard Pipe) male threads. 
View full article
Picard Product_Support
‎2018-09-06 12:32 PM

Labels:
  • Field Devices
836 Views

Replacement actuator for *M52L*

Issue Valves V354 and V355 requires a specific type of actuator. Environment V354 (7315425000) V355 (7315529000) M52L (8522320000) EM52L (8522221000) EM52L-4 (8522210000) MC52A (8532221010) Cause Due to the design of the V354 and V355 valves, a specific type of actuator is necessary. Resolution MC52A, part no. 8532221010, is designed for use as a replacement actuator. It is delivered together with an adapter to fit the V354 valve.
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Field Devices
1573 Views

Lowest correct measurement SPD310/SPD360

Issue Choosing the correct range of sensor is important in order to provide the most accurate value. Environment SPD310 SPD360 Cause Only the max value is specified for each range. How low is the lowest accurate value? Resolution The reasonable minimum pressure in the 100Pa range should be equal or greater than 40Pa (typically), otherwise the max. error becomes bigger.
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Field Devices
880 Views

Replacement of Drayton DC1000 Energy Controller by SE Satchwell DC1100 Energy Controller due to obsolescence.

Issue Drayton DC1000 Energy Controller requires replacement. Environment Drayton Stand alone DC1000  DC 1000 Discreet  Energy Controller Optimiser Compensator Optimiser/Compensator Optimiser / Compensator Cause Obsolescence of Drayton DC1000 Energy Controller. Resolution There is no direct replacement of the DC1000, the DC1100 and the DC1400 are also obsolete now.
View full article
Picard Product_Support
‎2018-09-06 12:31 PM

Labels:
  • Field Devices
1884 Views

Replacement product for ASense-LON

Issue SCR100 series sensors are intended to be used as replacements for the Senseair ASense series sensors, but there is no SCR100 with LON communication available. Environment Senseair ASense SCR100 Cause There is no SCR100 LON version available. Resolution If LON sensors are required, they will need to be purchased directly from the manufacturer. See http://www.senseair.com/ for more information and details.
View full article
Picard Product_Support
‎2018-09-10 09:58 PM

Labels:
  • Field Devices
988 Views
  • « Previous
    • 1
    • …
    • 22
    • 23
    • 24
    • …
    • 36
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of