Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 19
    • 20
    • 21
    • …
    • 509
  • Next »

AET basic troubleshooting steps

Issue The functionality of the different tools and/or software does not operate as expected. Issues can appear related to controller functionality or possibly issues with how the standard programs work.  Product Line EcoStruxure Building Operation Environment Automated Engineering Tool (AET) Project Configuration Tool (PCT) EcoStruxure Building Operation (EBO) Cause When the latest versions of software and firmware are not being used, previously identified issues can cause problems with downloads or the operation of controllers. In other situations, it is possible that the proper steps or tools are not being used correctly. This could require further instruction and information.  Resolution In most situations, the troubleshooting steps below will address a majority of issues encountered while working with the AET and the standard applications. EBO software and SmartX firmware being used should be at the latest version Between updates and fixes to the software/firmware, you should be using the latest versions found on the Exchange.  AET software should be up to date Between updates and fixes, make sure you are using the latest version of the AET software which can be found on the Exchange.  AET templates should be up to date You can reference the AET Quick Help - Downloading AET Templates video or the SmartVAV: Software Engineering Process document for further direction.  Understanding the proper way to use the Automated Engineering Tool There exist a number of AET Quick Help Videos available on the Community to help with AET user skills. If there are any topics not covered in a video that you are searching for, be sure to leave a post with the new video idea.
View full article
Administrator Cody_Failinger Administrator
‎2019-11-27 07:23 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • Automated Engineering Tool
  • EcoStruxure Building Operation
5664 Views

How to extract an XIF out of a Lon controller

Issue There may be a situation where the External Interface File (XIF) needs to be extracted out of the controller in order to properly set up the controller in a building automation system.  Product Line EcoStruxure Building Operation, TAC IA Series, TAC Vista Environment External Interface File (XIF) NodeUtil Loytec XIF Builder Cause These tools will help with the extraction of an XIF file. An XIF file is used to create a Niagara R2 shadow object, a Niagara G3 LMNL file, LonWorks device template, and a SmartStruxure device template.  Resolution The device manufacturer should provide an XIF, and in most cases, a DRF kit as well. The XIF provided by the manufacturer of the controller should be used first but if issues arise it may be required to extract the file from the controller. There are a number of tools available that will create an XIF, but the DRF kit cannot be created by any tool and must be supplied by the manufacturer. This MUST be provided along with the device. The list below covers some of the tools which are available. NodeUtil                          (header: bad,           NVs: ok,                      DMA/File-SCPTs are omitted) Vista's XIF-builder           (header: bad,           NVs: almost ok..,       DMA/File-SCPTs are omitted)  Loytec plugIn                  (does a perfect XIF from a device using Loytec's stack)   NodeUtil is available from the Echelon website (free registration is required) - The NodeUtilLauncher package attached makes it easy to use NodeUtil with Loytec interfaces. Loytec XIF Builder is available from the Loytec website (free registration is required) Using Lonmaker and the XIF Builder. Using NL220 and the XIF Builder. If the uploaded XIF still contains some detailed prompted error, refer to Error displayed when importing a device XIF into SmartStruxure.
View full article
Picard Product_Support
‎2018-09-11 02:59 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
8899 Views

PT100/PT1000 sensors used with Xenta controllers

Issue Do Xenta controllers support PT100/PT1000 sensors for measuring the temperature? Environment Xenta Controller TAC Menta PT100/PT1000 Temperature sensors Cause Requirement to measure the temperature using PT100/PT1000 Temperature sensors. Resolution PT100/PT1000 sensors are not supported within any of the Xenta controllers.  The following is a method to achieve this using Menta: When using PT100/PT1000 to connect to a thermistor input, Menta Logic is required to add a polynom using the expression block. It is also strongly recommended to implement some calibration software in Menta to allow for fluctuations in resistance for every input that PT100/PT1000 is connected to. If a sensor is replaced / changed, re-calibration will be required. Sample experiment results and Menta Logic's are available here.
View full article
Picard Product_Support
‎2018-09-10 03:04 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • TAC Vista
1806 Views

Technical Tips documentation for I/NET Seven

Issue Links to the Technical Tips Papers Product Line TAC INET Environment I/NET Seven Tech Tip Cause Formerly only available on the FTP site, now available in the Knowledge Base. Resolution Tech Tips linked below. Tech Tip 001   System S7000 Upgrade to I/NET 7700 Tech Tip 002   Calculated Point and Docutrend Operator Rankings Tech Tip 003   MIP01 Memory Interface Processor Installation Tech Tip 005   I/NET 7700 Printer Enhancements Tech Tip 006   Use of LAN Repeater on I/NET 7700 Tech Tip 007   I/NET System Messages Tech Tip 009   I/NET 7700 Setup Tech Tip 010   ICI HHC Memory Addresses Tech Tip 011   S/90 Purging Visitors Tech Tip 012   Shipping MIP Products Tech Tip 013   Mechanical Door Interlock Wiring Tech Tip 014   S90 Graphics PCX File Requirements Tech Tip 015   Indala Reader Card Types Tech Tip 016   New RAM Configuration for MIP Tech Tip 017   Transient Protection On DPUs with I/Disc Tech Tip 018   I/NET 7700 Taps and Building Managers Bias Straps Tech Tip 019   Docutrend and Hard Disk Space Tech Tip 020   Docutrend Reports Tech Tip 021   ADAA Tap Addresses Tech Tip 022   Docutrend:Number of Days of Report Tech Tip 023   S/90 Memory Requirements Tech Tip 024   ADAA System Messages and Docutrend Setup Tech Tip 025   I/NET 7700 Work-Arounds and Known Problems Tech Tip 026   I/NET 7700 Controllers BOOT ROM Compatibility Tech Tip 027   S/90 Color Mapping Tech Tip 028   Controller Battery Back-up Tech Tip 029   I/NET 7700 Host Sign-on/off and Host Lost/restored Messages Tech Tip 030   MR Minimum Trip and Close Tech Tip 031   I/Disc Installation Method Tech Tip 032   ADAA S7000 to I/NET 7700 Upgrade Tech Tip 033   I/DISC Reader Maintenance Tech Tip 034   UCI/UC Use of Bit Offset 08 & 09 Tech Tip 035   MR Memory Usage Tech Tip 036   DPI, MRI & MCI Memory Allocation Tech Tip 037   WIRING AND CONFIGURING CSI CONTROLLERS Tech Tip 038   Programming the 7750 Building Manager Tech Tip 039   7910 and 7920 DPU Memory Usage Tech Tip 040   Lantastic 6.0 Installation for use with S/90 Tech Tip 041   Using pcANYWHERE 5.0 with S/90 Tech Tip 042   MR Memory Usage Correction Tech Tip 043   “P” only Mode of Operation for PID Modules Tech Tip 044   I/STAT Functionality Tech Tip 045   I/NET 7700 Backup Station Tech Tip 046   S/90 and RDTAP Dial Tech Tip 047   Mixing Different Types of ADAA TAPs Tech Tip 048   Universal Asynchronous Receiver-Transmitter Chips Tech Tip 049   Special Days Tech Tip 050   Supervised Inputs Tech Tip 051   I/NET 7700 Ethernet LAN System Tech Tip 052   I/NET 7700 Modem Compatibility Tech Tip 053   I/NET 7700 Modem Compatibility Update Tech Tip 054   SETTING UP THE SITE TAP EDITOR TO CALL A PAGER Tech Tip 055   History Recall Report to DBF File Output Tech Tip 056   Use of I/NET 7700 Message Masking Tech Tip 057   LTS80 Series Lini-Temp Sensors Tech Tip 058   MR55X with Kavlico Transducer Tech Tip 059   I/NET 7700 Controller Interface Cabling Tech Tip 060   Use of DC/DM Points with Sub-Lan Devices MRs and UCs Tech Tip 061   AI and PI Fractional Digits Tech Tip 062   PID and Control Point Tech Tip 066   Momentary Release & Automatic Time Schdl. Release w/ I/NET 7700 used w/ Elevator Tech Tip 063   I/NET Personnel Reports Tech Tip 064   Watermark's in S/90 Video Badging Tech Tip 065   System 90 and Video Badging System Installation Tech Tip 067   12 Steps to I/NET Access Control Tech Tip 068   Application to Disable the “1-OPEN” state of a Supervised DI point Tech Tip 069   TTS100 SERIES THERMISTOR SENSORS Tech Tip 070   BATCH FILES FOR REMOTE SITE GRAPHICS PAGES Tech Tip 071   Access Control Doc-to-DIF Report Tech Tip 072   Standalone MR-VAV-AX Start-up Tech Tip 073   I/NET 7700 Modem Compatibility Tech Tip 074   SETPOINT ADJUSTMENT DEVICE PROGRAMMING Tech Tip 075   Using Belimo NM24 Actuator with MR-ASC’s Tech Tip 076   Running I/NET 4 on a Windows95 Tech Tip 077   How to Convert an Idisc Number Tech Tip 078   How to program a Modem without the use of a TerminalEmulator Tech Tip 079   COMMONLY ASKED ASC QUESTIONS Tech Tip 080   S/90 ACI/DACI Battery Life Tech Tip 081   Integrated I/NET Video Badging Requirements for Single PC Systems Tech Tip 082   How to program Forced Door & Door Open Too Long Alarms Tech Tip 083   How to get started with Integrated I/NET Video Badging
View full article
Picard Product_Support
‎2018-09-07 02:11 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • TAC INET
81606 Views

M&B Conversion Coefficient calculation tool

Issue This tool will help calculate the required M&B conversion coefficient for a given analog value in I/NET. Product Line TAC INET Environment All I/NET Controllers I/NET Resident Point Editor Cause Need to calculate an I/NET Conversion Coefficient (M&B) for a special sensor Resolution Click here to download an Excel spreadsheet that has several functions for calculating the correct M&B.
View full article
Picard Product_Support
‎2018-09-10 02:23 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
2445 Views

Embedded license activation fails

Issue When trying to activate an embedded license on a SmartX Server using Device Administrator, the activation fails with the following error message: Failure (error) received when reclaiming an embedded license on an Automation Server   "Embedded operation: Activate failed: ASEmbeddedAPI internal error: Capability request could not be created." Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Building Operation Automation Server (AS) All of the above v. 3.0 or higher Cause The cause of this problem is that the trusted storage, i.e., the embedded license database on the SmartX server, is corrupt. The embedded licensing framework undertakes internal checking and if it determines there is a consistency problem, it will consider the trusted storage to be corrupt. This means that no operations to the trusted storage, such as activating licenses, will succeed. At the time of writing, it is unclear why the consistency problems happen. In the server log, you may also observe the following error message: 10:08:06: Executing licensing command 10:08:06: Executing embedded operation: Activate ActivationID: ACT-XXXXXXXXXX-XXXXXX-XXXXXXXX 10:08:11: Embedded operation: Activate failed: ASEmbeddedAPI internal error: Capability request could not be created 10:08:11: Licensing command completed 10:08:11: Activating licenses failed (Real Activation ID replaced with ACT-XXXXXXXXXX-XXXXXX-XXXXXXXX)   Although this process is specific to the "Capability request could not be created" error, similar errors can be corrected by following the steps shown in the resolution. Please attempt all steps before contacting support.   Resolution   Building Operation 2022 v4.0.4  and above Upgrading to the above versions will now resolve the trusted storage corruption and inhibit license activation. Building Operation 3.2.X and up to EBO 2022 v4.0.3   Note: Although this process is specific to the "Capability request could not be created" error, similar errors can be corrected by following the below steps. Please attempt all steps before contacting support.    Clear trusted storage within the server Using Device Administrator select the affected server and Open a PuTTY Console An alternative way of connecting to the server is to use WinSCP. Use File protocol SCP and the admin user. When connected, follow the instructions as per the Word Document also attached below Warm or Cold Start the AS-P If failures still occur, attempt the Offline Activation of Licenses Workflow; The key step is that the license is activated offline and then transferred to the server in two different steps, allowing the license activation process to complete successfully.   Warm or Cold Start the AS-P If there are still failures with either of these options, send a support request through your local support center including the errors seen with each activation attempt.     Building Operation version lower than 3.2.X   If the embedded license is a Client license, there is no need to activate the license. Install the EBO Hotfix 3.0.3.2001 (CP1) or later. This will remove the enforcement of SmartX server Clients in the licensing system. See also article Embedded WebStaion client license when logging directly into a SmartX server no longer needed. Other licenses like SmartDrivers, SNMP, and Personal Dashboards may still need to be activated. Contact your local support center to fix this problem.
View full article
Janeway PeterEdvik Janeway
‎2020-03-19 02:35 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
12588 Views

PCT Intel Processor Virtualization Technology Issue

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue PCT client can't start properly with "Hardware virtualization is not enabled" error. Product Line EcoStruxure Building Operation Environment Building Operation Project Configuration Tool (PCT) (All Versions) Cause Hardware Virtualization is Disabled or not available for PCT Resolution  Install "Intel® Processor Identification Utility" then verify the status of "Intel® Virtualization Technology" from the Utility. Using the table below, you can see if your processor supports Intel® Virtualization(provided by Intel).  The above information can also be found on Intel® Virtualization Technology web page If Virtualization is disabled in BIOS then enable it from BIOS else identify other software utilizing the Virtualization and stop the application.  Use Win key or press the Windows Start button Type: cmd Select Run as Administrator  Verify command prompt window title bar is Administrator: Command Prompt Type: shutdown /r /fw/ /f  Press enter and the computer will shut down immediately forcing all applications to close (/f) and restart (/r) into firmware interface (/fw)   If the issue persists, the following article may provide the answer Knowledge Base article - PCT error Hardware-virtualization is not enabled-Please-enable.
View full article
Admiral StephenYang Admiral
‎2020-03-31 06:39 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
5597 Views

FTT-10 LONWorks Network Design Rules - LON Wiring Guidelines

Issue Many LonWorks network installation problems can be avoided if the appropriate network design rules are followed when the network is being designed. Product Line TAC IA Series, TAC Vista, Satchwell Sigma Environment I/A Series MicroNet (LON) Controllers Satchwell Sigma MicroNet series LON Controllers Vista Xenta Controllers Cause The I/A Series MicroNet System Engineering Guide (F-26507) was written as a resource of information for the installation of the I/A Series MNL-100, 200 & VAV controllers as well as the Sigma MicroNet 440 and 620 controllers.  The Resolution, below, is a summary of the LON design rules presented in this document. Resolution FTT-10 LON network wiring must be installed using Echelon-approved wire.  The most common type of wire used is described as Category 4  cable.  This wire is normally unshielded stranded twisted-pair 22AWG (0.65mm).  An example of this wire is the W221P or W222P series cable from Connect-Air International (http://www.connect-air.com).  This type of cable is normally available both in plenum rated and non-plenum rated types.  Consult the job specifications to determine if plenum-rated or shielded cable is required. The LON network can be wired using "Free Topology" or "Bus Topology" wiring segments.   1.  BUS Topology Guidelines BUS Topology LonWorks wiring extends from device to device (daisy chain format) with no branches or stubs. A LON-TERM-2 terminator must be installed at each end of the LON bus. When using standard Category 4 LON cable with the recommended terminators, the bus may be up to 4593 feet (1400 meters) in length. When extending LON wire to the MN-Sx sensor base in a bus topology network, the sensor base must be wired as part of the daisy chain and not as a stub connection. 2. FREE Topology Guidelines Free Topology imposes essentially no restrictions on the layout of the network -- some controllers may be wired point to point and others branching from a common point.  The free-topology LON network must be terminated at one point with a LON-TERM-1 terminator. When using standard Category 4 LON cable, the total wire length in a free topology LON network may not exceed 1641 feet (500 meters).  In addition, the longest wire path between any two controllers on a free topology LON network may not exceed 1312 feet (400 meters). 3. Common LON Network Wiring Guidelines LON wiring can not be part of an active bundled telephone trunk even if the telephone trunk is wired with Category 4 wire. Shielded Category 4 wire may be used in high EMI/RFI environments.  The shield must be wired continuously and grounded through a 470 Kohm resistor at one end. LON wiring must not be bundled with or housed in the same conduit as controller I/O and power wiring.  4. LonWorks Network Wiring and Addressing Guidelines When the number of controllers on a LonWorks network exceeds 60, the network must be split into segments with not more than 64 controllers or devices per segment using LonWorks Repeaters or Routers.  When counting the controllers and devices on a LonWorks network segment, a LonWorks Network Interface Device and the repeater itself must be included in the device count in each segment. In a LonWorks network containing repeaters or routers, each LonWorks network segment must be properly terminated, as described above. Domain / Subnet / Node addressing is used when configuring the LON controllers. A LonWorks Subnet consists of a series of LonWorks controllers all configured within the same LON Subnet number. A single LonWorks Subnet can have a maximum of 127 device and controller Node addresses.  This Node address count includes the LonWorks Network Interface, all controllers on the subnet, and repeater and/or router node addresses.  An allowance is typically made for additional addresses to be used by LonWorks tools connected to the Subnet.
View full article
Picard Product_Support
‎2020-12-02 06:52 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC Vista
25875 Views

Modicon Switch Ordering and RSTP Configuration using EBO with MPX/RPX

Issue Modicon Switch Ordering options and how to configure the Ethernet Switch for RSTP for EBO Product Line EcoStruxure Building Operation Environment Modicon RSTP Switch (Not Connexium) Building Operation Automation Server Premium MPX and/or RPX Controllers Ethernet Switch Configurator Cause Schneider Electric Industry Offers an RSTP enabled Ethernet Switch that can be used with EBO instead of 3rd party Switches Resolution The following video will illustrate the following steps for Ordering and installing the Modicon Ethernet Switch with EBO The Modicon Connexium Ethernet Switch has been replaced by the updated Modicon Switch Modicon Switch Part Numbers and Email address for ordering Connect and use the SE Ethernet Switch Configurator executable for Switch configuration Set the Time and use the Syslog for troubleshooting Configure EBO and the controllers (MPX/RPX) for RSTP Test the Modicon Switch, EBO, and the MPX/RPX controllers for RSTP     Related Links: Modicon Switch Part Numbers and Ordering Information - (see attached Part Number slide) MCSESM Switch Installation Manual MCSESM Switch Configuration Manual Ethernet Switch Configurator Software - look for  SchneiderElectricEthernetSwitchConfigurator2303_Windows_x86.zip Other Modicon Switch documents RSTP Troubleshooting Community Thread TGML Graphic Setup Video (Training Department)
View full article
Admiral Alan_Wood Admiral
‎2022-07-06 08:35 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
3580 Views

SPU1201 and SPU1202 obsolescence

Issue SPU 1201 Universal Pressure Switch – Specification No. 131-1-201 SPU 1202 Universal Pressure Switch – Specification No. 131-1-202 Product Line Field Devices Environment Site requesting a Universal Pressure Switch Cause SPU1201 and SPU1202 obsolescence Original PDF specification sheet is available here: DS21602-0203.pdf. Resolution The SPU1201 and SPU1202 have been made obsolete per the supplier. The closest replacement options that we have are listed below: SPU1201 is a 0.2 – 4.0 Bar device. The replacement options are SPP920 Series SPU1202 is a 12 – 250 mBar device. The replacement options are SPP920 Series Refer to Product Announcement PA-00166 for the SPP920 series Differential Pressure Switches for neutral and slightly aggressive liquids and gases.
View full article
Picard Product_Support
‎2018-09-11 05:52 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • Field Devices
4840 Views

WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility

Issue WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility Product Line TAC IA Series Environment WorkPlace Tech Tool Software release 5.8.x, 5.9.x, 5.10x, and 5.11.x Microsoft Windows and Microsoft Office Visio requirements, see the "Resolution" section, below. Visio 2010, 2013, 2016, 2019, 2021(.msi install)  Visio 2013, 2016, 2019, 2021 (subscription "Click to Run", Plan 2) Office 2010, 2013, 2016 (.msi install) Office 2013, 2016, 365 (subscription "Click to Run", Plan 2) Support for Workplace Tech 5.10 / previous and Workplace Tech Editor Note: Visio 2019 and Visio 2021 are not supported in 5.9.4 or EBO versions before EBO 2022.  Visio 2019 and Visio 2021 are supported when using Workplace Tech 5.10.x and EBO 2022. Cause What Microsoft Windows operating systems and what versions of Microsoft Visio are compatible with the WorkPlace Tech Tool version 5.8.x, 5.9.x, 5.10.x, and 5.11.x? Resolution Microsoft Windows WorkPlace Tech Tool releases 5.8 through 5.8.6 are certified to run on the following versions of Microsoft Windows: Microsoft Windows XP Professional with Service Pack 2 or Service Pack 3 Microsoft Windows Vista 32-bit Business, Ultimate or Enterprise Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional WorkPlace Tech Tool release 5.8.7 is certified to run on the following versions of Microsoft Windows: Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional Microsoft Windows 8.1 32-bit Pro or Enterprise Microsoft Windows 8.1 64-bit Pro or Enterprise Microsoft Windows Server 2012 64-bit WorkPlace Tech Tool releases 5.9.1 to 5.9.4 are certified to run on the following versions of Microsoft Windows: Microsoft Windows 7   32-bit Professional Microsoft Windows 7   64-bit Professional Microsoft Windows 8.1   32-bit Pro or Enterprise Microsoft Windows 8.1   64-bit Pro or Enterprise Microsoft Windows 10    32-bit Professional Microsoft Windows 10    64-bit Professional Microsoft Windows Server 2012   64-bit WorkPlace Tech Tool release 5.10.0 to 5.10.x is certified to run on the same as WorkPlace Tech 5.9.x and the following versions of Microsoft Windows: Microsoft Windows Server 2016 64-bit Microsoft Windows Server 2019 64-bit Microsoft Windows Server 2022 64-bit Microsoft Windows 11 Professional (Workplace Tech 5.10.4 only) WorkPlace Tech Tool release 5.11.0 is certified to run on the following versions of Microsoft Windows: Microsoft Windows 10 64-bit Professional Microsoft Windows Server 2022 64-bit Microsoft Windows 11 Professional Microsoft Visio Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional Microsoft Windows 8 32-bit Pro or Enterprise Microsoft Windows 8 64-bit Pro or Enterprise Microsoft Windows 8.1 32-bit Pro or Enterprise Microsoft Windows 8.1 64-bit Pro or Enterprise Microsoft Windows Server 2012 64-bit WorkPlace Tech Tool releases 5.8 through 5.8.6 require one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2003 with Service Pack 3 (officially supported for WPT 5.8.0, WPT 5.8.1, no known issues with WPT 5.8.2 through 5.8.5) Microsoft Office Visio 2007 with Service Pack 1 or Service Pack 2 Microsoft Office Visio 2010 with or without Service Pack 1 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool release 5.8.7 requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2007 with Service Pack 3 Microsoft Office Visio 2010 with Service Pack 2 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool release 5.9.1 through 5.9.4 requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2010 with Service Pack 2 Microsoft Office Visio 2013 with Service Pack 1 Microsoft Office Visio 2016 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool releases 5.10.0 through 5.10.x requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2016 Microsoft Office Visio 2019 Microsoft Office Visio 2021 Microsoft Office Visio Office 365 Subscription Plans 2 WorkPlace Tech Tool releases 5.11.x requires one of the following versions of Microsoft Visio (64-bit version ONLY) Microsoft Office Visio 2019 64-bit Microsoft Office Visio 2021 64-bit Microsoft Office Visio Office 365 Subscription 64-bit Plans 2 Warning: WorkPlace Tech 5.11 is not compatible with EBO WorkPlace Tech Editor. Do not install WP Tech 5.11 on a PC that has EBO WorkPlace Tech Editor installed. Continue to use WP Tech 5.10 on PCs where EBO WorkPlace Tech Editor is required.   Note: Workplace Tech Tool 5.10.0 and later releases require .NET Framework 4.8 to support Open LDV 5.1 which is included in the installer.  .NET Framework 3.5 Sp1 is no longer required.   Follow the instructions in the article link for the security updates required. Workplace Tech 5.10.x and previous / Workplace Tech Editor (EBO) Microsoft Security Updates required for Visio and Office For the Visio requirements for earlier versions of the WorkPlace Tech Tool software, see What versions of Visio are required for WorkPlace Tech?.
View full article
Picard Product_Support
‎2020-12-15 10:46 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • TAC IA Series
15230 Views

Additional information needed on the FLEXnet licensing system

Issue For further information, refer to the FLEXnet Licensing End User Guide, available on the Flexera website. Product Line TAC Vista Environment Vista 5 Workstation FLEXnet Licensing Cause If you get this error and attempt to find the End User Guide, you will discover that the company that produces the FLEXnet software has gone through several name changes: Macrovision to Acresso to Flexera. Resolution If you would like a copy of this document, you can find the FLEXnet License Administration Guide (previously called the End User Guide) here.
View full article
Picard Product_Support
‎2018-09-07 11:43 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • TAC Vista
7014 Views

Modbus Protocol Information

Issue What resources are available to get more information on the Modbus protocol? Product Line Andover Continuum,EcoStruxure Building Operation,Field Devices,Satchwell BAS & Sigma,Satchwell MicroNet,TAC IA Series,TAC INET,TAC Vista Environment Modbus ASCII/RTU Modbus TCP/IP Cause The Modbus protocol information is available on www.modbus.org Use the menu on the left and select Technical Resources. Select the Modbus Specifications. Resolution Found on www.modbus.org are the protocol specifications: Modbus ASCII/RTU Modbus TCP
View full article
Picard Product_Support
‎2018-09-10 01:26 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
8176 Views

Managing Licensing distribution using the Option's file

Issue How can we exclude Hosts or Users from accessing the Workstation Professional license i.e. Script, Function Block and Graphic editors from another Workstation? Product Line EcoStruxure Building Operation Environment Building Operation License Server FLEXnet Cause When accessing various editors from within Workstation a particular license does not differentiate host or user who should have access to which editors. Using the option file taclic.opt allows you to exclude certain Host / Users of StruxureWare Building Operation from accessing these Workstation clients. The Workstation clients referenced are as follows: client.station (Workstation) client.script (Script Editor) client.functionblock.view (Function Block Editor) client.graphiceditor (Graphic Editor) Resolution FLEXnet Licensing provides the options file to be included in the License Server directory. Each time the License Server service is started this file is checked. Syntax and use can be found in the attached document - Chapter 13 The following option file must reside on the License Server in the following path: Building Operation 1.9 and below: C:\Program Files(x86)\Schneider Electric StruxureWare\Building Operation 1.x\License Server Building Operation 2.0 and above: C:\Program Files(x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server Once this file is copied into the License Server folder, you must restart the license service (via the Windows Control Panel, Administrative Tools, Services). Examples: # The following text excludes the features from Workstation Professional # # Use the following 3 Exclude statements if you wish to exclude an entire Workstation from accessing editors # EXCLUDE client.script HOST enter_host_name EXCLUDE client.functionblock.view HOST enter_host_name EXCLUDE client.graphiceditor HOST enter_host_name # # Use the following 3 Exclude statements if you wish to exclude a Building Operation User from accessing editors # (remove #'s below as required) # # EXCLUDE client.script USER enter_user_name # EXCLUDE client.functionblock.view USER enter_user_name # EXCLUDE client.graphiceditor USER enter_user_name # Notes: The HOST can be defined by either DNS or IP Address The USER is the user name as defined in Building Operation, this may be the same as the Windows username if using Windows Domain.
View full article
Picard Product_Support
‎2018-09-11 04:39 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • EcoStruxure Building Operation
5049 Views

Troubleshooting LON Network Communication

Issue Troubleshooting LON Network communications. Product Line EcoStruxure Building Operation, TAC Vista, TAC IA Series Environment Xenta Controllers MNL I/A Controllers EcoStruxure Building Operation AS-P LPA Protocol Analyzer Cause Intermittent communication failures, high bandwidth, error packages, noise on the line -- these can be difficult to pin down and identify. Resolution These two documents attached produced by Loytec are invaluable resources in troubleshooting a LON network.  The first deals with common causes of noise on LON Wires.  The second details what to do once you've procured an LPA protocol analyzer -- how to use it and interpret data.   For a Vista system, also see Actions for reducing Bandwidth in a Vista network. For an EcoStruxure Building Operation system, also see Bandwidth Throttling.    If an LPA protocol analyzer is not available there is also an option to log the Lon communication to and from the ES, AS-P, or AS-B. To do that you change the debug level from "Information" to "Trace" for: /Automation Server/System/Modules/Trace/Loggers/nsp/nsp.pin/nsp.pin.lon/nsp.pin.lon.comm After the investigation make sure to set the debug level back to "Information" again. For debugging assistance a Tool called SBO Lon Decoder can be used.
View full article
Picard Product_Support
‎2018-09-07 03:27 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
27925 Views

Integrating Windows Active Directory user accounts with EcoStruxure

Issue Setting up, using, and troubleshooting Windows Active Directory with Building Operation Workstation and WebStation. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation WebStation Windows Active Directory Windows Server Cause When integrating EcoStruxure with Windows Active Directory, NO user accounts need to be created in EcoStruxure, all that needs to be done is map the EcoStruxure User Account Group(s) with the Windows group(s) that will be used.  You can map Windows Active Directory groups to Building Operation user account groups if Building Operation runs on a network that uses this directory to manage users and user account groups. A Building Operation user account group that includes a Windows account group can also be a member of another Building Operation user account group. Mapping Windows Active Directory account groups to Building Operation user account groups has advantages both for administrators and operators. Administrators can manage the user accounts in the Windows Active Directory, rather than managing the accounts in two places. Any changes are instantly implemented to the mapped Building Operation user account group. Operations only have to remember the Windows login. Once logged in to a Windows user account that is mapped to a Building Operation account, the user is authenticated to access WorkStation without having to log in a second time. Note: The Building Operation domain used to map the Windows Active Directory user account groups must be a member of the Windows domain where the Active Directory is located. Windows Active Directory account groups can only be mapped on servers that are based upon Microsoft Windows operating system. Automation Servers, cannot map Windows Active Directory groups. For example, the Windows Active Directory user account groups Main Admin and Main User are mapped to the Building Operation user account groups Administrators and External Users. The External Users user account group is a member of the Operator user account group. The Administrators account group, which is a member of the External Users, inherits access to the Operation workspace. The user will then log into Windows on the PC where the WorkStation is installed. When logging into EcoStruxure Workstation the authentication is automatically done from the Windows user account. Resolution NOTE: Active Directory association cannot be achieved using the inbuilt Local Domain Create a new EBO Domain and associate it with your active windows Domain. NOTE: It is best to only use the Domain (Netbios) name (as shown above) when adding the Windows Domain name to this property.  Using the full DNS Domain name, for example, eur.gad.schneider-electric.com will cause issues when utilizing other features that require active directory authentication.  One example where this has been identified is with Change Control.   Create an EBO Domain Group within that new Domain and associate it with the Windows Domain Group in which the Windows Active Directory user(s) reside. Log in using Windows Username, Password, and Domain rather than EBO credentials. When logged on to the Enterprise Server PC as a Domain User it is also possible to select the "Log on as" box. See WebHelp: How to Create and Configure a Domain Conceptual Information on Windows Active Directory User Groups How to Create User Account Groups Troubleshooting Windows Active Directory with Workstation Log in Error: Wrong user name or password If the EcoStruxure Building Operation Domain has the same name as the Windows Active Directory domain name, it will expect the user account to exist locally in the Building Operation domain. Log in Error: "User account not associated with a group. Contact your Administrator." Verify that the Windows user is a part of the Windows group configured in the Building Operation Group settings. In order to identify every group that the current windows user belongs to, run the command: whoami /groups Once the Windows user has been confirmed as a member of the configured Windows group, try changing the Log On as credentials for the Enterprise Server service. The default user that is used when installed is the "Local System account". The Windows account used to run the Enterprise Server service needs "read access" to all places (e.g. OUs) in the Active Directory where user groups potentially involved in an EBO Windows log-on can be found. Note: By default, all domain users in an Active Directory have read access to Active Directory "Users and Computers" objects so it is the sites that have restricted this in some way that may face issues. You do not need to use “domain admin” type accounts for this as they are granted way too much authority in general. An account that has read access to sufficient parts of the AD while having only normal local user privileges on the machine where the Enterprise Server is running will suffice. From the Windows Start menu, launch Computer Management. In Computer Management go to Services and Application > Services. Find Building Operation X.X Enterprise Server, select it and Stop the service. Right-click on Building Operation X.X Enterprise Server and go to Properties. Select the Log On tab. Under Log On as select "This account". Enter a Windows user login that has sufficient Windows rights for the Enterprise Server to log on as. Click OK and then start the service again. Log in to Workstation again using Active Directory. Troubleshooting Windows Active Directory with WebStation From version 1.5.0 and up, using Windows Domain accounts is supported in WebStation. However, the following must be done in order to log in. Must use HTTPS. Must enter your Windows username and password. Must enter the domain as the Windows domain as defined within Building Operation.  See below: An example log-on format is shown below when using the above configuration when using WebStation:    Alternatively, if the following is configured in Building Operation: WebStation log-on will look as follows:  Download a TVDA for Single Sign-On Instructions
View full article
Picard Product_Support
‎2020-11-04 03:42 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • EcoStruxure Building Operation
19607 Views

Reseting an ACX 57xx model controller

Issue How to reset an ACX 57xx model controller Product Line Andover Continuum Environment ACX 57xx Cause While upgrading/downgrading the controller firmware, communications were lost and the controller is not communicating afterwards. Resolution Consult How to reset a ACX 57xx controller to reset the controller and then re-commission.
View full article
Picard Product_Support
‎2018-09-07 10:44 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • Andover Continuum
4090 Views

How to calculate storage used by Extended Trend Logs

Issue A site is required to store Extended Trend Log historical data for an extended period of time, in order to make sure the system has enough capacity for all the data  it is necessary to calculate the storage needed ahead of time Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Workstation Cause Understanding the storage requirements for long term trend storage Resolution Formula to calculate the storage capacity needed for Extended Trend Log data. Storage in bytes (S)  = Number Of Records (N) x 70 bytes. EXAMPLE: Consider a trend log of 1000 records with a 10-minute interval, if the requirement is to keep 5 years of data, how much storage capacity will be required? The number of records would (N)  be... 6 records per hour times 24 hours per day times 365 days per year*** times 5 years (*** leap years must be taken into account) N =  6 X 24 X 365 X 5 = 262800 bytes This equates to: S = N X 70 S = 262800 X 70 S = 18396000 bytes or approximately 18 megabytes   Note - The calculations above are for the native SQLite database used by EBO. There are two alternatives to using the ES database for long-term trend storage. Report Server - See the WebReports Database Usage Calculator Knowledge base article for storage calculations External Log Storage is possible from EBO v3.0 using TimescaleDB database - The EBO External Log Storage Installer tool from the community provides a databases size estimator located under the Tools menu item
View full article
Picard Product_Support
‎2018-09-06 09:59 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • EcoStruxure Building Operation
4935 Views

Using Sysman Alert Server with EcoStruxure Building Operation

Issue Is it possible to use Sysman Alert Server with EcoStruxure Building Operation? Product Line EcoStruxure Building Operation Environment Alarms and Events Cause Customers may wish to send important alarms to duty staff via SMS. Sysman Alert Server is one way of doing this and is easy to configure.  Resolution This is possible. The following document details the setup procedure: Sysman Alert Server with StruxureWare Building Operation The configuration will depend on the setup and location of the SysMan Server, but will generally involve "Write to File" Notifications if the Enterprise Server and Sysman Servers are installed on the same PC, or Emails to the SysMan Server (from Enterprise or Automation Server) More information can be found on Sysman's website. Part Numbers: SysManSMS ALERT SERVER: 900800600 SysManSMS GSM Modem: 900800610 In the UK when ordering please use the below part numbers. SysManSMS ALERT SERVER: 802000 SysManSMS GSM Modem: 100002
View full article
Picard Product_Support
‎2018-09-11 06:17 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • EcoStruxure Building Operation
5892 Views

Documentation on the MSC-MPC Microsmart controller and its associated modules

Issue Documentation on the MSC-MPC Microsmart controller and its associated modules. Product Line TAC I/A Series Environment Microsmart controller MSC-MPC MPC-4AO MPC-8AI MPC-2PO MPC-SSR MPC-4CO Cause Obsolete controller Resolution Click here to view the installation instructions on the MSC-MPC. Click each associated module part number below to view its installation instructions: MPC-4AO MPC-8AI MPC-2PO MPC-SSR MPC-4CO
View full article
Picard Product_Support
‎2018-09-10 03:48 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • TAC IA Series
8534 Views
  • « Previous
    • 1
    • …
    • 19
    • 20
    • 21
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of