Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 19
    • 20
    • 21
    • …
    • 501
  • Next »

Performance Degradation After Applying Service Provider (SP) Certificate in EBO

Issue After applying a third-party (SP) certificate to the EBO workstation, users experienced significant performance degradation. Symptoms included: - Slow login times (over one minute) - Laggy graphics interaction - Trend logs and charts loading slowly or failing to load Product Line EcoStruxure Building Operation  Environment EcoStruxure Building Operation (EBO)  Service Provider (SP) Certificate applied to EBO Cause The applied SP certificate contained DNS names in its extension fields (e.g., CRL Distribution Points and Authority Information Access) that the EBO system could not resolve. These unreachable DNS names caused delays during certificate validation, leading to the observed performance issues.   Expanded Technical Explanation Certificate Extensions and Their Role Digital certificates often include extensions that provide additional metadata. Three key extensions involved in this issue are: a. CRL Distribution Points (CDP) Specifies where the system can find the Certificate Revocation List (CRL) to check if the certificate has been revoked. If the URL in this field is unreachable (e.g., internal DNS like http://xxxxxprod1.xxx.local/...), the system may hang or delay while trying to access it. b. Authority Information Access (AIA) Indicates where to retrieve the issuing CA certificate or access OCSP responders. Similar to CDP, if the AIA URL is unreachable, the system will repeatedly attempt to connect, causing login delays and UI lag. c. Subject Alternative Name (SAN) Lists additional identities (e.g., DNS names, IPs) for which the certificate is valid. If these names are internal or misconfigured, they may trigger unnecessary DNS lookups, further slowing down operations. Why This Affects Building Operation Performance When the certificate includes unreachable URLs in CDP, AIA, or SAN: EBO attempts to resolve these URLs. If DNS fails or times out, it causes delays of several seconds to minutes. These delays accumulate across multiple components, leading to system-wide sluggishness. Resolution To identify URLs embedded in a certificate: Use an online certificate decoder, such as SSL Shopper Certificate Decoder. Upload the certificate file (e.g., .pem or .crt) and review the output for fields like: CRL Distribution Points Authority Information Access (AIA) Subject Alternative Name Alternatively, ask Copilot: Upload the certificate file (e.g., .pem, .crt, or .cer) - In some instances, the certificate file may need to be opened in a Text Editor such as Notepad++ and the text copied to allow CoPilot to interrogate the certificate files. Ask: "Can you extract all URLs from this certificate?" Copilot will return a list of URLs found in the certificate's extensions. Some (edited) examples should be shown as follows:   CRL Distribution Points: http://xxxxxprod1.xxx.local/AIA/SPAuth.crt http://xxxxxprod2.xxx.local/AIA/SPAuth.crt Authority Information Access (AIA): http://xxxxxprod1.xxx.local/AIA/SPMAuth.crt http://xxxxxprod2.xxx.local/AIA/SPMAuth.crt LDAP URLs: ldap:///cn=SPAuth,cn=AIA,... ldap:///cn=SPMAuth,cn=AIA,... Best Practices to Avoid This To prevent this issue: Avoid including internal-only or unreachable DNS names in certificate extensions. Use publicly resolvable URLs or omit non-essential extensions. Validate certificates using tools like: SSL Shopper Certificate Decoder OpenSSL ( openssl x509 -in cert.pem -text -noout ) Regenerate certificates with only the necessary fields: Common Name (CN) Valid SAN entries Minimal or no CDP/AIA if not required Additional Resources Configure the CDP and AIA Extensions on CA1 | Microsoft Learn Configure & Troubleshoot CDP And AIA | Encryption Consulting Scheneider Electric WebHelp - Certificates  
View full article
Picard RobertAndriolo Picard
‎2025-10-29 04:16 PM

Labels:
  • EcoStruxure Building Operation
250 Views

Zoning is reverting to the original state

Issue Zoning is reverting to the original state set on the RP-C controller after deployment or runtime changes. Product Line EcoStruxure Building Operation RP-C Series Controllers Environment Building Operation Workstation  RP-C firmware version: any Zoning configuration applied within a Custom Type Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Cause Zoning functionality is being used within a Custom Type, which causes the zoning configuration to revert to its original state. This occurs because Custom Types are designed to enforce consistency across instances, and any runtime changes to zoning are overridden by the base definition of the Custom Type. Resolution To prevent zoning from reverting: Avoid using zoning within Custom Types. Zoning should be configured directly on individual RP-C controller instances rather than within a Custom Type. Recommended Practice: Create zoning configurations on the RP-C controller outside of any Custom Type. If a Custom Type is necessary for other aspects of the configuration, exclude zoning from the type definition and apply zoning manually to each instance.
View full article
Sisko GavinHe Sisko
‎2025-10-28 05:29 PM

on ‎2025-10-28 05:29 PM

Labels:
  • EcoStruxure Building Operation
234 Views

Problems When Copying Menta Code from Xenta 280 or Xenta 300 to Xenta 401

Issue When attempting to directly download Menta code from a Xenta 280 or Xenta 300 controller to a Xenta 401 or Xenta 401:B controller, users may encounter the error: PARSER IO ERROR 13 Environment TAC Menta TAC Xenta 280 / Xenta 300 TAC Xenta 401 / Xenta 401:B Cause The Xenta 280 and 300 controllers have physical I/O points (e.g., M0-X1, M0-U2) directly on the device. These are referenced in the Menta application as M0 terminals. However, the Xenta 401 series does not have onboard physical I/O. When code containing M0 references is copied into a Xenta 401 Menta application, these I/O points become invalid. Since the points were copied manually (not created within the application or imported from a library), simulation mode does not detect the terminal mismatch. This leads to failed downloads and the PARSER IO ERROR 13 during direct serial communication. Resolution To resolve this issue: Open the Menta application for the Xenta 401. Navigate to Options > IO Configuration Table. Sort the table by the "Bound to" column to identify physical I/O references. Locate all points referencing M0 terminals. Reassign these points to valid physical I/O terminals appropriate for the Xenta 401 application.
View full article
Picard Product_Support
‎2018-09-06 01:22 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-28 05:26 PM

Labels:
  • TAC Vista
2077 Views

Use a TAC Xenta OP with a Xenta 100-series controller

Issue How can the TAC Xenta OP be used with a TAC Xenta 100-series controller? How does the OP identify which TAC Xenta 100 controller it's communicating with? Which OP mode should be used? Product Line TAC Vista Environment TAC Xenta OP TAC Xenta 101 TAC Xenta 102 TAC Xenta 121 TAC Xenta 122 Cause   The TAC Xenta OP panel allows access to input and output signals from a TAC Xenta 100-series controller. Identification of the specific controller is achieved via a Service Pin message. If connected directly to a TAC Xenta 100-series controller or a STR100-series device attached to it, the controller automatically sends a Service Pin message. If connected elsewhere on the network, you may need to manually press the Service Pin on the desired controller. For troubleshooting connectivity issues, refer to: “No Answer” on an OP when connecting to a Xenta 280/300/400 Resolution 1. Configure the TAC Xenta OP Plug in the TAC Xenta OP. Hold Back and Enter for 3 seconds to access the OP Service Menu. Scroll to Option 10: OP Mode. Set “Xenta 100” to ON using the + key. Press Enter. Set “Mode” to TAC using the + key. Press Enter twice to restart the OP. 2. Connect to a TAC Xenta 100-series Device Plug the OP into the OP jack on the TAC Xenta 100 controller or a connected STR100 device. When prompted “Press to access Xenta 100”, press Enter. At “Connecting to Xenta 100…”, wait or press the Service Pin on the controller. Press Down to proceed. 3. View and Modify Network Variables At the NV Index? prompt, use +/- to select the desired network variable index. Press Enter to view the signal. If the value is an input: Use +/- to modify the value. Press Enter to accept. If the signal is a bit-based application option: Press Enter to navigate between bits. Use + to change the bit value. Press Enter to confirm.
View full article
Picard Product_Support
‎2018-09-07 02:34 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-28 05:21 PM

Labels:
  • TAC Vista
3044 Views

1.8k Thermistor Compatibility with Xenta Controllers

Issue Certain Xenta controllers and I/O modules are compatible with 1.8k thermistor temperature inputs. Users often seek clarification on which models support this and the specific temperature vs. resistance characteristics. Product Line TAC Vista Environment Xenta 122-FC Xenta 122-HP Xenta 121-FC Xenta 121-HP Xenta 200 Xenta 300 Xenta 420A Xenta 450A Cause Users need to understand the temperature vs. resistance curve for the 1.8k thermistors used in Xenta controllers, especially for the Xenta 300 series. Resolution All Xenta controllers and I/O modules except the Xenta 102-AX use the same 1.8k thermistor type: 1.8KA1. Below is a summarized Temperature vs. Resistance table for the 1.8KA1 thermistor: Temp (°C) Minimum kΩ Nominal kΩ Maximum kΩ -50.0   60.87  63.88  67.03  -45.0   45.41  47.5   49.68  -40.0   34.23  35.68  37.2   -35.0   26.04  27.07  28.13  -30.0   19.99  20.72  21.47  -25.0   15.48  16.0   16.54  -20.0   12.09  12.46  12.84  -15.0   9.512 9.779 10.05  -10.0   7.541 7.733 7.929 -5.0   6.021 6.16  6.301 0.0   4.84  4.94  5.042 5.0   3.916 3.988 4.061 10.0   3.189 3.24  3.293 15.0   2.612 2.649 2.686 20.0   2.151 2.177 2.209 25.0   1.782 1.8   1.818 30.0   1.478 1.496 1.514 35.0   1.233 1.25  1.267 40.0   1.033 1.049 1.065 45.0   0.8698 0.8848 0.9001 50.0   0.7357 0.7497 0.7639 55.0   0.6251 0.638 0.6511 60.0   0.5334 0.5453 0.5573 65.0   0.457 0.4679 0.479 70.0   0.3931 0.4031 0.4132 75.0   0.3395 0.3485 0.3578 80.0   0.2942 0.3025 0.311 85.0   0.2559 0.2634 0.2712 90.0   0.2233 0.2302 0.2373 95.0   0.1956 0.2019 0.2083 100.0   0.1718 0.1775 0.1835 105.0   0.1514 0.1566 0.1621 110.0   0.1338 0.1386 0.1436 115.0   0.1186 0.123 0.1276 120.0   0.1054 0.1095 0.1136 125.0   0.094 0.0977 0.1015 130.0   0.084 0.0874 0.0909 135.0   0.0753 0.0784 0.0816 140.0   0.0676 0.0705 0.0735 145.0   0.0609 0.0635 0.0663 150.0   0.0549 0.0574 0.0599
View full article
Picard Product_Support
‎2018-09-06 02:18 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-28 05:14 PM

Labels:
  • TAC Vista
6406 Views

How to Clear the Xenta Application

Issue The Xenta application may crash or become corrupted, resulting in one or more of the following symptoms: Controller not online in Vista Workstation I/O modules fail to associate with the Master Controller does not accept downloads via System Plug-in Product Line TAC Vista Environment Xenta version 3.61 or higher, Xenta 280 (281, 282, 283), Xenta 300 (301, 302), Xenta 401 Cause Crashes may occur during interrupted downloads or due to other system anomalies. Resolution Step 1: Power Cycle First, try cycling power to the controller to see if the issue resolves. Step 2: Forced Application Clear (if power cycle fails) If the controller still refuses to accept downloads from Vista or Menta: Create a Reset Dongle: Use an old Cat5 network cable. Cut off one end, leaving 4–6 inches of cable. Short-circuit the specific pins required for reset (refer to pinout diagram or manufacturer instructions). Perform the Reset: Power off the controller or remove it from the base plate. Insert the manufactured RJ45 jack into the RS-232 port. Power on the controller or reinsert it into the base plate. This will trigger a forced Clear Application. Remove the RJ45 jack. Cycle power again to complete a fresh boot-up.
View full article
Picard Product_Support
‎2018-09-08 12:04 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-28 05:10 PM

Labels:
  • TAC Vista
7419 Views

Can we use RTD-DI-16 with a 3-wire PT100 sensor in a freezer that operates below -50°C?

Issue A user wants to deploy the RTD-DI-16 module with a 3-wire PT100 sensor in an environment where temperatures drop below -50°C. The concern is whether the module can accurately read such low temperatures. Product Line Field Devices. EcoStruxure Building Operation, Environment Building Operation I/O Module 16 Ch RTD Cause The RTD-DI-16 module is designed to operate within a temperature measurement range of -50°C to +150°C. This limitation is defined in the product datasheet and reflects the module’s internal resolution and calibration capabilities. Temperatures below -50°C fall outside the supported range, which means: Resolution and accuracy are guaranteed only within this specified range. Values below -50°C will not be read and may result in inaccurate or undefined behavior. Resolution Do not use RTD-DI-16 for applications requiring measurements below -50°C. Consider alternative modules or solutions that support extended temperature ranges, such as those designed for cryogenic or ultra-low temperature environments. While the PT100 sensor itself may be capable of measuring lower temperatures, the RTD-DI-16 module cannot process those values accurately.
View full article
Guinan MikaelKrantz Guinan
‎2025-10-28 05:00 PM

on ‎2025-10-28 05:00 PM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
209 Views

TC900 BACnet Protocol Network Limits

Issue How many TC900 thermostats can be connected to a single BACnet MS/TP network on an AS-P? Product Line EcoStruxure Building Operation, Field Devices. Environment Building Operation Automation Server Premium. Building Operation Automation Server Bundled. TC900 Protocol Series Thermostat Cause Understanding system limitations for a single COM port when using BACnet MS/TP protocol. Resolution   Maximum Number of TC900 BACnet Devices per MS/TP Network Port Device Type Baud Rate Max Devices AS-P 9600 bps 7   19200 bps 16   38400 bps+ 26 AS-B 9600 bps 4   19200 bps 10   38400 bps 15   76800 bps 20 Additional Notes Performance Optimization: MS/TP field buses perform better with an RS-485 repeater. This may be necessary depending on the network layout and connected devices. Device Load Consideration: All devices (including TC900 and third-party BACnet devices) should present a 1/8 Unit Load to ensure proper bus performance. Recommended Baud Rate: For optimal balance between speed and reliability, 38400 bps is typically the best choice.
View full article
Guinan MikaelKrantz Guinan
‎2025-10-27 08:13 PM

on ‎2025-10-27 08:13 PM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
306 Views

Can a Delay Be Configured for EE_mess Alarms in TAC Vista?

Issue Users may want to configure a delay on EE_mess alarms in TAC Vista to avoid unnecessary or premature alarm triggers. Product Line TAC Vista Environment TAC Vista Server TAC Vista Workstation Cause The EE_mess object in TAC Vista does not support a delay attribute. This limitation means that alarms triggered by EE_mess events occur immediately, which can lead to excessive or unwanted alarm notifications. Resolution It is not possible to configure a delay on an EE_mess alarm in TAC Vista. The EE_mess object lacks a delay attribute and therefore cannot be modified to include one.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-27 08:04 PM

Labels:
  • TAC Vista
1407 Views

Manually Adding a Xenta Device with Group Bindings in NL220

Issue When managing a large site, adding a new Xenta controller can be time-consuming if using the System Plug-in to create group bindings. This process often requires taking controllers offline. This article outlines a manual method to add group bindings efficiently without downtime. Product Line TAC Vista Environment TAC Vista Server NL2220 Cause The manual method is effective and reliable if the steps are followed correctly. It allows integration of a new Xenta controller into existing TAG 0 and TAG 1 bindings. Resolution Follow these steps to manually bind a new Xenta controller in NL220: Step 1: Enable Message Tags Connections Tree Open NL220 and go to Project Settings. Under the Trees tab, enable Message Tags Connections Tree. This will add a new tree view labeled Message Connections. Step 2: Add to TAG 0 Binding In the Message Connections tree, locate the TAG 0 connection (covers all Xenta controllers). Right-click TAG 0 and select Edit. In the Connection Window, switch to Subsystem View. Drag the TAG 0 from the new Xenta controller into the window. Click Update to apply changes to the database. Step 3: Add to TAG 1 Binding Locate the appropriate TAG 1 Xenta group for the new controller. Identify the correct TAG 1 connection by the controller name. Right-click the TAG 1 connection and select Edit. In the Connection Window, switch to Subsystem View. Drag the TAG 1 from the new Xenta controller into the window. Click Update to apply changes to the database.
View full article
Picard Product_Support
‎2018-09-06 03:57 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-27 07:59 PM

Labels:
  • TAC Vista
1453 Views

Using One Common Transformer to Power Full-Wave and Half-Wave Devices

Issue Can a single transformer be used to power both full-wave and half-wave devices, such as an AS-P controller and a DuraDrive actuator? Product Line Field Devices, EcoStruxure Building Operation, Andover Continuum, Satchwell MicroNet, TAC INET, TAC Vista Environment Full-wave and half-wave devices Cause There may be a need to simplify power distribution by using a single transformer for multiple device types. Understanding Rectifier Types Full-Wave Rectifiers Function: Converts both halves of the AC waveform into DC. Components: Uses four diodes in a bridge configuration. Efficiency: More efficient than half-wave rectifiers, providing a smoother DC output with less ripple. Half-Wave Rectifiers Function: Converts only one half of the AC waveform into DC. Components: Uses a single diode. Efficiency: Less efficient, resulting in higher ripple in the output voltage. Resolution Yes, a common transformer can be used to power both full-wave and half-wave devices provided the following conditions are met: External Isolation Transformers Non-isolated, connected devices of varying rectifier types require their own external isolation transformers. Use external isolation transformers for each device if there is doubt regarding whether an installation may cause equipment damage Transformer Sizing: Ensure the transformer’s VA rating exceeds the combined power requirements of all connected devices. Undersized transformers can lead to voltage drops, overheating, or device malfunction. Installation Guidelines: Before installation, refer to the document titled “Guidelines for Powering Multiple Actuators From a Common Transformer - Integration Guide.” Isolation & Compatibility: Confirm that devices do not interfere with each other’s operation when sharing a transformer. Avoid connecting devices with incompatible grounding or isolation requirements.
View full article
Picard Product_Support
‎2018-09-07 02:21 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-27 03:09 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
1639 Views

Using the 'PowerFail' System Variable in b3 Controller Script Programs

Issue When manually binding the PowerFail system variable via a Numeric Input in the program header of a b3 controller, the value shown in the Binding Variables window may appear incorrectly (e.g., 1536 instead of a binary value like 1 or 0 ). Product Line EcoStruxure Building Operation Environment b3 controllers Script Program Editor Cause The Script Program Editor for b3 controllers does not recognize PowerFail as a predefined system variable. As a result, it displays an unexpected integer value in the Binding Variables window. Resolution Despite the incorrect display (e.g., 1536 ), the PowerFail variable functions correctly when bound to a Numeric Input. During compilation and execution, the system properly interprets the value. Best Practices for Scripting Treat PowerFail as a binary input: use logic based on True/False or ON/OFF . Ignore the displayed integer value in the Binding Variables window. Be aware that PowerFail is only active for one scan cycle immediately after power is restored following a loss. Example Usage Additional Notes This behavior is expected and does not impact the actual functionality of the PowerFail variable.
View full article
Picard Product_Support
‎2018-09-10 02:02 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-27 02:42 PM

Labels:
  • EcoStruxure Building Operation
1515 Views

Understanding the “Couldn't find a matching record in the internal storage, re-reading everything” Log Message in EBO with External Log Storage

Issue When using External Log Storage in EBO, the following log message may appear: "Couldn't find a matching record in the internal storage, re-reading everything." Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation External Log Storage Cause This message indicates a failed synchronization attempt between EBO’s internal log storage and the configured external log storage system. It does not imply a misconfiguration or data corruption. EBO attempts to locate the last successfully transmitted record in its internal storage. If that record is missing—typically due to log purging based on retention settings—EBO cannot resume from that point and instead re-sends all available data to the external storage to ensure continuity. Common Scenario EBO is configured with a short log retention period (e.g., 1 day). The external log storage system is unavailable for a period longer than the retention window. The last record previously sent to external storage is purged from EBO’s internal storage before synchronization resumes. EBO cannot find the matching record and re-transmits all current log data. Resolution No action is required. This behavior is expected and intentional. It ensures that the external log storage receives all available data, even if some records were purged from internal storage during downtime. Recommendations Review and adjust log retention settings in EBO to align with the availability and recovery time objectives of the external log storage system. Ensure high availability of the external storage to minimize downtime and avoid unnecessary data re-transmission.
View full article
Administrator CraigEl Administrator
‎2025-10-26 09:25 PM

on ‎2025-10-26 09:25 PM

Labels:
  • EcoStruxure Building Operation
272 Views

How to Transfer an XBuilder Project to a Different Type of Xenta Server

Issue Prior to XBuilder 5.1.1, it was not possible to change the Xenta Server type in an existing XBuilder project. This limitation made it difficult to migrate projects between different Xenta Server models without losing links, bindings, or configurations. Product Line Satchwell BAS & Sigma, Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Server XBuilder 5.1.0 or earlier Xenta 511, 527, 555, 701, 711, 721, 731, 913 Cause Earlier versions of XBuilder (prior to 5.1.1) did not support changing the Xenta Server type directly within the project’s network pane. This limitation required a manual workaround to migrate projects between different server types. Resolution Option 1: Upgrade to XBuilder 5.1.1 or Later If possible, upgrade to XBuilder 5.1.1 or newer, which allows direct modification of the target device type: Save the Project Locally: If the project is stored in a Vista database, open it in XBuilder. Go to File > Save As and save the project to your local machine. Reopen the Project: Close XBuilder. Reopen XBuilder and load the saved project from your PC. Change Target Device: In the Project menu, select Change Target Type... Choose the desired Xenta Server model from the drop-down list. Option 2: Manual Transfer (If Upgrade Is Not Possible) This method allows transferring an XBuilder project to a different Xenta Server while preserving graphics and object bindings. Ensure the target server supports the same or better Menta and User Graphic capabilities and can handle the existing network types. Example: Migrating from Xenta 555 (with LonWorks and Modbus networks) to Xenta 731. Step-by-Step Instructions 1. Create the New Xenta Server in Vista Open the Vista database containing the Xenta 555 project. Right-click the Xenta 555, select Edit to open the XBuilder project. In Vista, create a new Xenta 731 (name it similarly but not identically to the 555). 2. Transfer the LonWorks Network In Vista, drag and drop the LON network from the 555 to the 731. Right-click the 731, select Edit to open its XBuilder project. Rename the default folder in the System pane to match the top-level folder of the 555 project. In the 731 project, right-click the LON object in the Network pane and select Refresh Network from TAC Vista. 3. Transfer the Modbus Network In the 555 project: Right-click each Modbus device, select Edit Device Template. In the Device Editor, go to File > Save As... and save the template. In the 731 project: Recreate the Modbus network using the saved templates. 4. Transfer System Objects In the 555 project: Right-click each object under the top-level folder and select Copy. In the 731 project: Right-click the top-level folder and select Paste. Repeat for all objects and folders (note: selecting a folder includes all nested items). Do not copy the top-level folder itself; it cannot be pasted. Note: Graphics bindings are preserved. Reference paths are automatically updated (e.g., TAC_Xenta_555 becomes TAC_Xenta_731 ). However, some bindings (e.g., Time objects) may break and need to be manually rebound. 5. Final Steps Close the 555 project. In Vista, delete the Xenta 555. Generate the 731 project. When prompted to copy original TGML files, select Yes. Download the project to the Xenta 731. Tip: If the 555 project only contains a Modbus network, a similar process can be followed for standalone projects. Additional Notes Ensure compatibility between source and target servers regarding network types and resource capabilities. Always back up your projects before performing any migration.
View full article
Picard Product_Support
‎2018-09-06 10:35 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 09:04 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
2613 Views

IP Protection and NEMA Ratings for Products

Issue What are the NEMA or IP ratings for a specific product? Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell BAS & Sigma, Satchwell MicroNet, TAC IA Series, TAC INET, TAC Vista Environment All devices Cause Users often need to know whether a product is protected against: Water ingress Intrusion by foreign objects (e.g., dust, fingers) Resolution To determine a product’s protection level, refer to the Degrees of Protection document, which includes: IP Rating Chart NEMA Enclosure Rating Chart 🔹 Understanding IP Ratings An IP rating consists of two digits: First digit: Protection against solid foreign objects Second digit: Protection against water Examples: IP20: Protected against fingers (≥12.5 mm), no water protection IP10: Protected against objects up to 50 mm, no water protection If a product datasheet does not specify water ingress protection, the second digit defaults to 0. 🔹 Typical Building Products Many building automation products: Prevent insertion of fingers (≥12.5 mm) Do not offer water protection → Common rating: IP20 📎 Attachment Degrees of Protection.pdf (Includes full IP and NEMA charts)
View full article
Picard Product_Support
‎2018-09-06 09:02 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 09:00 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
5639 Views

Microsoft Visual Studio Triggers Just-In-Time Debugging

Issue When using a Windows PC with Microsoft Visual Studio installed, an unexpected error message appears referencing Just-In-Time (JIT) Debugging. This can interrupt normal operations and confuse users unfamiliar with debugging tools. Product Line Andover Continuum, EcoStruxure Building Operation, Satchwell BAS & Sigma, Satchwell MicroNet, TAC IA Series, TAC INET, TAC Vista Environment Windows Operating System Cause Visual Studio includes a feature called Just-In-Time Debugging, which attempts to launch the debugger when a program crashes or encounters a critical error. If enabled, this feature can interfere with other applications or workflows by prompting unexpected debug dialogs. Resolution To disable Just-In-Time Debugging, follow these steps: Open Visual Studio. Go to the Tools menu and select Options. In the Options dialog box: Expand the Debugging section. Select the Just-In-Time page. In the Enable Just-In-Time debugging of these types of code box, uncheck the relevant options: Managed Native Script Click OK to apply changes. Note: Disabling JIT debugging modifies a registry key. You must have Administrator privileges to make this change.
View full article
Picard Product_Support
‎2018-09-10 07:55 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 08:55 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
5610 Views

Errors Encountered When Trying to Run LonMaker

Issue When attempting to run LonMaker, the following errors may occur in succession: Could not listen on poet/tcp: The address specified is already in use (Error -2532) Database error: (Subsystem: LNS, #25) [DB #-2506] The global database is not open. (Subsystem: LNS, #64) Additional errors that may be caused by the same underlying issue: Problem connecting with the database server process: (Subsystem: LNS, #36) [DB#-2523] Error opening LCA Global database Product Line EcoStruxure Building Operation, Satchwell BAS & Sigma, TAC IA Series, TAC Vista Environment LonMaker for Windows 3.1 and 3.2 Sentinel Protection Installer 7.6.1 Cause  The issue is typically caused by a conflict between the Sentinel Protection Server and the POET Server, as both attempt to use the same port(s). Sentinel Protection Installer 7.6.1 installs the Sentinel Protection Server, which manages Sentinel SuperPro and UltraPro keys used with Satchwell Sigma and other products This service is not required for the dongle driver to function and can interfere with LonMaker’s operation. Refer to: Error: LNS #25 lcaErrDatabase for more technical details. Resolution To resolve the issue: Stop the Sentinel Protection Server: Open the Windows Services console: Press Windows + R , type services.msc , and press Enter. Locate Sentinel Protection Server. Right-click and select Stop. (Optional): Disable the service if not needed: Right-click > Properties > Set Startup type to Disabled. ✅ This will allow POET Server to operate without port conflicts.
View full article
Picard Product_Support
‎2018-09-09 11:53 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 08:49 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC Vista
2433 Views

Estimating Thermal Load (BTU/hr or Watts) for Controllers and Equipment

Issue How to estimate the thermal load (in BTU/hr or Watts) that your controllers and equipment will produce. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell BAS & Sigma, Satchwell MicroNet, TAC IA Series, TAC INET, TAC Vista Environment Applicable to all electrical equipment used in building automation systems. Cause Understanding the thermal load is essential for: Sizing air conditioning systems Ensuring proper ventilation Avoiding overheating in enclosures Not all equipment datasheets provide thermal dissipation values, so manual calculation may be necessary. Resolution You can estimate the thermal load using the power consumption of each device. Formula To convert power (in Watts) to thermal load: BTU/hr = Power (W) × 3.412141633 Watts = Power (W) (already known) Note: 1 Watt = 3.412141633 BTU/hr Example Calculation Using the Continuum AC-1 I/O module: Power consumption: 2.6 W (without attached reader) Thermal load: BTU/hr = 2.6 × 3.412141633 = 8.87 BTU/hr Watts = 2.6 W If the reader is powered by the AC-1, include its power consumption in the total. International Units Reference Unit Conversion 1 Watt 3.412 BTU/hr 1 BTU/hr 0.293 Watts Additional Notes Use this method for any device where power consumption is known. For grouped equipment, sum the total wattage before converting. Consider using an online calculator for quick conversions.
View full article
Picard Product_Support
‎2018-09-11 05:42 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 08:42 PM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2648 Views

Can a BS5308 Part 1 Type 1, 2-Pair Individually Screened Cable Be Used for M-Bus Communications?

Issue A BS5308 Part 1 Type 1 cable was installed under the assumption it would be used for Modbus communications. However, it was later determined that the application required M-Bus communication. This raised the question: Is the BS5308 cable suitable for M-Bus? Product Line Andover Continuum, EcoStruxure Building Operation, Satchwell BAS & Sigma, TAC Vista Environment M-Bus communication systems BS5308 Part 1 Type 1 cable (2-pair, individually screened) Cause The incorrect assumption that the communication protocol would be Modbus led to the installation of a BS5308 cable. Upon discovering that M-Bus was required, concerns arose regarding the cable’s compatibility with M-Bus communication standards. Resolution While the recommended cable for M-Bus communication is J-Y(ST)Y, which is specifically designed for indoor telephone applications and optimized for analog/digital signal transmission, the BS5308 Part 1 Type 1 cable can still be used for M-Bus under certain conditions. Key characteristics of J-Y(ST)Y cable: Designed for indoor telephone and data transmission Aluminium-laminated plastic foil static screen with tin-plated drain wire to minimize high-frequency electromagnetic interference Twisted pair (TP) structure to reduce crosstalk BS5308 Part 1 Type 1 cable considerations: Originally designed for instrumentation and control applications Features individually screened pairs, which can help reduce interference Electrical characteristics must be evaluated to ensure compatibility with M-Bus requirements Conclusion: Yes, the BS5308 Part 1 Type 1, 2-pair individually screened cable can be used for M-Bus communications, provided that its electrical characteristics meet the M-Bus system requirements. Refer to the attached calculation chart and datasheets for detailed compatibility analysis.
View full article
Picard Product_Support
‎2018-09-10 11:22 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 08:33 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC Vista
3211 Views

H909HV-S6 Current Transformer Does Not Change State

Issue The H909HV-S6 current transformer does not change state, even though current flow is present. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell BAS & Sigma, Satchwell MicroNet Environment H909HV-S6 Current Transformer Cause The issue is due to incorrect wiring between the current transformer and the DDC controller. The installation instructions may appear to indicate that four connections are required to the DDC controller. However, this is not correct—only two connections are necessary. Resolution To resolve the issue: Review the wiring diagram in the installation instructions carefully. Ensure that only two connections are made between the CT and the DDC controller: The status output has two terminal sets, but only one connection is required from each set. Correct the wiring to match the proper configuration. 📄 Download the H909HV-S6 Datasheet
View full article
Picard Product_Support
‎2018-09-11 06:01 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 08:25 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
3261 Views
  • « Previous
    • 1
    • …
    • 19
    • 20
    • 21
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore