Use a TAC Xenta OP with a Xenta 100-series controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Use a TAC Xenta OP with a Xenta 100-series controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • CraigEl
    CraigEl
  • MikaelKrantz
    MikaelKrantz
  • Cody_Failinger
    Cody_Failinger
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3041 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Use a TAC Xenta OP with a Xenta 100-series controller

Picard Product_Support
‎2018-09-07 02:34 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-28 05:21 PM

Issue

How can the TAC Xenta OP be used with a TAC Xenta 100-series controller?

  • How does the OP identify which TAC Xenta 100 controller it's communicating with?
  • Which OP mode should be used?

Product Line

TAC Vista

Environment

  • TAC Xenta OP
  • TAC Xenta 101
  • TAC Xenta 102
  • TAC Xenta 121
  • TAC Xenta 122

Cause

 

The TAC Xenta OP panel allows access to input and output signals from a TAC Xenta 100-series controller. Identification of the specific controller is achieved via a Service Pin message.

  • If connected directly to a TAC Xenta 100-series controller or a STR100-series device attached to it, the controller automatically sends a Service Pin message.
  • If connected elsewhere on the network, you may need to manually press the Service Pin on the desired controller.

For troubleshooting connectivity issues, refer to:
“No Answer” on an OP when connecting to a Xenta 280/300/400

Resolution

1. Configure the TAC Xenta OP

  1. Plug in the TAC Xenta OP.
  2. Hold Back and Enter for 3 seconds to access the OP Service Menu.
  3. Scroll to Option 10: OP Mode.
  4. Set “Xenta 100” to ON using the + key. Press Enter.
  5. Set “Mode” to TAC using the + key. Press Enter twice to restart the OP.

2. Connect to a TAC Xenta 100-series Device

  • Plug the OP into the OP jack on the TAC Xenta 100 controller or a connected STR100 device.
  • When prompted “Press to access Xenta 100”, press Enter.
  • At “Connecting to Xenta 100…”, wait or press the Service Pin on the controller.
  • Press Down to proceed.

3. View and Modify Network Variables

  • At the NV Index? prompt, use +/- to select the desired network variable index.
  • Press Enter to view the signal.

If the value is an input:

  • Use +/- to modify the value.
  • Press Enter to accept.

If the signal is a bit-based application option:

  • Press Enter to navigate between bits.
  • Use + to change the bit value.
  • Press Enter to confirm.
Labels (1)
Labels:
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 5003
  • MikaelKrantz20
  • MikaelKrantz25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore