Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How to Clear the Xenta Application

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Clear the Xenta Application
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • LeeCravens
    LeeCravens
  • Cody_Failinger
    Cody_Failinger
  • Sacco
    Sacco

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
6380 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Clear the Xenta Application

Picard Product_Support
‎2018-09-08 12:04 AM

Issue

Xenta application has crashed or become corrupted and may exhibit one or more of the following symptoms:

  • Controller not online in Vista Workstation
  • I/O modules will not associate with Master
  • Xenta controller will not accept download through System Plug-in

Reset the Xenta controller by wiring a reset dongle. Clear the application/memory by shorting certain pins on the RS-232 port.

Product Line

TAC Vista

Environment

  • Xenta version 3.61 or higher, Xenta 280 (281, 282, 283), Xenta 300 (301, 302), Xenta 401
  • Menta
  • System Plug-in
  • Vista Workstation
  • RJ45 Reset Tool
  • Reset Dongle

Cause

  • Xenta may have crashed during download especially if interrupted during download.
  • There are various other possible causes.

Resolution

Verify whether cycling power corrects problem. If that fails then perform the following steps:

 

If a Xenta 280/300/401 application has crashed and refuses to accept a new download, both from Vista and Menta, there is a way to clear the application (Xenta version 3.61 or higher).

  1. Manufacture a RJ45 jack with the following pins short-circuited:

    Note: This can be done by cutting off the end of an old Cat5 network cable, leaving approximately 4-6" of cable, and connecting the wires that correspond to the pins shown above.
     
  2. Turn off power to the controller or remove it from the base plate.
  3. Put the manufactured RJ45 jack in the RS-232 port.
  4. Turn on power to the controller or re-insert it into the base plate. A forced Clear Application will be made.
  5. Remove the jack.
  6. Cycle power to the device to perform a fresh boot-up.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 5143
  • make
Was this article helpful? Yes No
100% helpful (7/7)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of