Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to Clear the Xenta Application

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Clear the Xenta Application
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • MikaelKrantz
    MikaelKrantz
  • LeeCravens
    LeeCravens
  • Cody_Failinger
    Cody_Failinger
  • Sacco
    Sacco

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
7424 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Clear the Xenta Application

Picard Product_Support
‎2018-09-08 12:04 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-28 05:10 PM

Issue

The Xenta application may crash or become corrupted, resulting in one or more of the following symptoms:

  • Controller not online in Vista Workstation
  • I/O modules fail to associate with the Master
  • Controller does not accept downloads via System Plug-in

Product Line

TAC Vista

Environment

Xenta version 3.61 or higher, Xenta 280 (281, 282, 283), Xenta 300 (301, 302), Xenta 401

Cause

Crashes may occur during interrupted downloads or due to other system anomalies.

Resolution

Step 1: Power Cycle

  • First, try cycling power to the controller to see if the issue resolves.

Step 2: Forced Application Clear (if power cycle fails)

If the controller still refuses to accept downloads from Vista or Menta:

  1. Create a Reset Dongle:

    • Use an old Cat5 network cable.
    • Cut off one end, leaving 4–6 inches of cable.
    • Short-circuit the specific pins required for reset (refer to pinout diagram or manufacturer instructions).

  2. Perform the Reset:

    • Power off the controller or remove it from the base plate.
    • Insert the manufactured RJ45 jack into the RS-232 port.
    • Power on the controller or reinsert it into the base plate.
    • This will trigger a forced Clear Application.
    • Remove the RJ45 jack.
    • Cycle power again to complete a fresh boot-up.
Labels (1)
Labels:
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 5143
  • make
  • MikaelKrantz25
Was this article helpful? Yes No
100% helpful (7/7)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore