Zoning is reverting to the original state
  • Zoning is reverting to the original state
  • GavinHe
    GavinHe
Sisko GavinHe Sisko
‎2025-10-28 05:29 PM
on ‎2025-10-28 05:29 PM
Zoning is reverting to the original state set on the RP-C controller after deployment or runtime changes.
    RP-C Series Controllers
  • Building Operation Workstation
  • RP-C firmware version: any
  • Zoning configuration applied within a Custom Type
Warning
Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.
Zoning functionality is being used within a Custom Type, which causes the zoning configuration to revert to its original state. This occurs because Custom Types are designed to enforce consistency across instances, and any runtime changes to zoning are overridden by the base definition of the Custom Type.
To prevent zoning from reverting:
  1. Avoid using zoning within Custom Types.
    Zoning should be configured directly on individual RP-C controller instances rather than within a Custom Type.
  2. Recommended Practice:
    • Create zoning configurations on the RP-C controller outside of any Custom Type.
    • If a Custom Type is necessary for other aspects of the configuration, exclude zoning from the type definition and apply zoning manually to each instance.
  • GavinHeward25