Issue
The H909HV-S6 current transformer does not change state, even though current flow is present.
Product Line
Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell BAS & Sigma, Satchwell MicroNetEnvironment
H909HV-S6 Current Transformer
Cause
The issue is due to incorrect wiring between the current transformer and the DDC controller.
The installation instructions may appear to indicate that four connections are required to the DDC controller. However, this is not correct—only two connections are necessary.
Resolution
To resolve the issue:
- Review the wiring diagram in the installation instructions carefully.
- Ensure that only two connections are made between the CT and the DDC controller:
- The status output has two terminal sets, but only one connection is required from each set.
- The status output has two terminal sets, but only one connection is required from each set.
- Correct the wiring to match the proper configuration.