Can a BS5308 Part 1 Type 1, 2-Pair Individually Screened Cable Be Used for M-Bus Communications?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can a BS5308 Part 1 Type 1, 2-Pair Individually Screened Cable Be Used for M-Bus Communications?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3211 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can a BS5308 Part 1 Type 1, 2-Pair Individually Screened Cable Be Used for M-Bus Communications?

Picard Product_Support
‎2018-09-10 11:22 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 08:33 PM

Issue

A BS5308 Part 1 Type 1 cable was installed under the assumption it would be used for Modbus communications. However, it was later determined that the application required M-Bus communication. This raised the question: Is the BS5308 cable suitable for M-Bus?

Product Line

Andover Continuum, EcoStruxure Building Operation, Satchwell BAS & Sigma, TAC Vista

Environment

  • M-Bus communication systems
  • BS5308 Part 1 Type 1 cable (2-pair, individually screened)

Cause

The incorrect assumption that the communication protocol would be Modbus led to the installation of a BS5308 cable. Upon discovering that M-Bus was required, concerns arose regarding the cable’s compatibility with M-Bus communication standards.

Resolution

While the recommended cable for M-Bus communication is J-Y(ST)Y, which is specifically designed for indoor telephone applications and optimized for analog/digital signal transmission, the BS5308 Part 1 Type 1 cable can still be used for M-Bus under certain conditions.

Key characteristics of J-Y(ST)Y cable:

  • Designed for indoor telephone and data transmission
  • Aluminium-laminated plastic foil static screen with tin-plated drain wire to minimize high-frequency electromagnetic interference
  • Twisted pair (TP) structure to reduce crosstalk

BS5308 Part 1 Type 1 cable considerations:

  • Originally designed for instrumentation and control applications
  • Features individually screened pairs, which can help reduce interference
  • Electrical characteristics must be evaluated to ensure compatibility with M-Bus requirements

Conclusion:
Yes, the BS5308 Part 1 Type 1, 2-pair individually screened cable can be used for M-Bus communications, provided that its electrical characteristics meet the M-Bus system requirements. Refer to the attached calculation chart and datasheets for detailed compatibility analysis.

Labels (4)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC Vista
Attachments
M-Bus_BS5308 part 1 type 1_20121127.zip
Tags (2)
  • Find more articles tagged with:
  • 11916
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore