How to Transfer an XBuilder Project to a Different Type of Xenta Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Transfer an XBuilder Project to a Different Type of Xenta Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • LeeCravens
    LeeCravens
  • Benji
    Benji
  • sesa115370
    sesa115370
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2624 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Transfer an XBuilder Project to a Different Type of Xenta Server

Picard Product_Support
‎2018-09-06 10:35 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 09:04 PM

Issue

Prior to XBuilder 5.1.1, it was not possible to change the Xenta Server type in an existing XBuilder project. This limitation made it difficult to migrate projects between different Xenta Server models without losing links, bindings, or configurations.

Product Line

Satchwell BAS & Sigma, Satchwell MicroNet, TAC INET, TAC Vista

Environment

  • Xenta Server
  • XBuilder 5.1.0 or earlier
  • Xenta 511, 527, 555, 701, 711, 721, 731, 913

Cause

Earlier versions of XBuilder (prior to 5.1.1) did not support changing the Xenta Server type directly within the project’s network pane. This limitation required a manual workaround to migrate projects between different server types.

Resolution

Option 1: Upgrade to XBuilder 5.1.1 or Later

If possible, upgrade to XBuilder 5.1.1 or newer, which allows direct modification of the target device type:

  1. Save the Project Locally:

    • If the project is stored in a Vista database, open it in XBuilder.
    • Go to File > Save As and save the project to your local machine.
  2. Reopen the Project:

    • Close XBuilder.
    • Reopen XBuilder and load the saved project from your PC.
  3. Change Target Device:

    • In the Project menu, select Change Target Type...
    • Choose the desired Xenta Server model from the drop-down list.

Option 2: Manual Transfer (If Upgrade Is Not Possible)

This method allows transferring an XBuilder project to a different Xenta Server while preserving graphics and object bindings. Ensure the target server supports the same or better Menta and User Graphic capabilities and can handle the existing network types.

Example: Migrating from Xenta 555 (with LonWorks and Modbus networks) to Xenta 731.


Step-by-Step Instructions

1. Create the New Xenta Server in Vista

  • Open the Vista database containing the Xenta 555 project.
  • Right-click the Xenta 555, select Edit to open the XBuilder project.
  • In Vista, create a new Xenta 731 (name it similarly but not identically to the 555).

2. Transfer the LonWorks Network

  • In Vista, drag and drop the LON network from the 555 to the 731.
  • Right-click the 731, select Edit to open its XBuilder project.
  • Rename the default folder in the System pane to match the top-level folder of the 555 project.
  • In the 731 project, right-click the LON object in the Network pane and select Refresh Network from TAC Vista.

3. Transfer the Modbus Network

  • In the 555 project:
    • Right-click each Modbus device, select Edit Device Template.
    • In the Device Editor, go to File > Save As... and save the template.
  • In the 731 project:
    • Recreate the Modbus network using the saved templates.

4. Transfer System Objects

  • In the 555 project:
    • Right-click each object under the top-level folder and select Copy.
  • In the 731 project:
    • Right-click the top-level folder and select Paste.
    • Repeat for all objects and folders (note: selecting a folder includes all nested items).
    • Do not copy the top-level folder itself; it cannot be pasted.

Note: Graphics bindings are preserved. Reference paths are automatically updated (e.g., TAC_Xenta_555 becomes TAC_Xenta_731). However, some bindings (e.g., Time objects) may break and need to be manually rebound.


5. Final Steps

  • Close the 555 project.
  • In Vista, delete the Xenta 555.
  • Generate the 731 project. When prompted to copy original TGML files, select Yes.
  • Download the project to the Xenta 731.

Tip: If the 555 project only contains a Modbus network, a similar process can be followed for standalone projects.


Additional Notes

  • Ensure compatibility between source and target servers regarding network types and resource capabilities.
  • Always back up your projects before performing any migration.
Labels (4)
Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 12734
  • CraigEllis25
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore