Issue
Users may want to configure a delay on EE_mess alarms in TAC Vista to avoid unnecessary or premature alarm triggers.
Product Line
TAC Vista
Environment
- TAC Vista Server
- TAC Vista Workstation
Cause
The EE_mess object in TAC Vista does not support a delay attribute. This limitation means that alarms triggered by EE_mess events occur immediately, which can lead to excessive or unwanted alarm notifications.
Resolution
It is not possible to configure a delay on an EE_mess alarm in TAC Vista. The EE_mess object lacks a delay attribute and therefore cannot be modified to include one.