Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1688 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 81
    • 82
    • 83
    • 84
    • 85
  • Next »
Label: "TAC IA Series" Show all articles

Trying to purchase a Network 8000 conversion from the TAC I/A Series Migrator and the "Add to Cart" button is missing?

Issue Trying to purchase a Network 8000 conversion from the TAC I/A Series Migrator and the "Add to Cart" button is missing? Environment iPortal and TAC I/A Series Migrator tool Cause This can happen if someone adds a conversion file to a cart and leaves that cart without checking out or if a conversion file is added to a cart and then deleted from the cart. Resolution When this occurs the file migration must be done again.  Once the conversion is complete the "Add to Cart" button will be displayed and the file can be purchased.
View full article
Picard Product_Support
‎2018-09-06 09:46 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1055 Views

Is SIGNAL supported on Windows 2000?

Issue Is SIGNAL supported on Windows 2000? Environment SIGNAL version 4.4.1 and 5.0.0 Cause Windows 2000 was not included in testing Resolution SIGNAL 4.4.1 is compatible with Windows 95/98. SIGNAL 5.0.0 is compatible with Windows XP.
View full article
Picard Product_Support
‎2018-09-06 09:46 AM

Labels:
  • TAC IA Series
845 Views

On a SE7600 controller, is the nciSccModel snvt read-only or will it modify the controller's profile?

Issue On a SE7600 controller, is the nciSccModel snvt read-only or will it modify the controller's profile?  Customer has replaced the HVAC equipment such that the existing profile does not match up with the existing SE7600. Environment SE7600 VT7600 Cause Mechanical equipment was replaced with a different design Resolution The nciSccModel snvt does not modify the SE7600 profile.  It is a read-only. A different model of controller is the best option for the new mechanical design. An external solution may also work (i.e. the use of a relay).
View full article
Picard Product_Support
‎2018-09-06 09:45 AM

Labels:
  • TAC IA Series
1267 Views

I/A Series Micronet BACnet controllers (MNB) support for BACnet Schedules

Issue I/A Series Micronet BACnet controllers (MNB) support for BACnet Schedules Environment I/A Series Micronet BACnet (MNB) controllers  Cause There is a requirement for the BACnet controllers to support BACnet schedules.  Resolution Currently, I/A Series Micronet BACnet controllers do not support BACnet schedules. 
View full article
Picard Product_Support
‎2018-09-06 09:45 AM

Labels:
  • TAC IA Series
1377 Views

When MicroSmart tunneling with Operator Interface, an error appears indicating that there are no MicroSmart controllers under the selected DCM.

Issue A site has a UNC-520 with ibsMs Service and approximately 20 MicroSmart controllers.  A serial tunnel is successfully established to the UNC.  From the Operator Interface main page, MicroSmart is accessed.  After a few seconds, an error appears indicating that there are no controllers under the currently selected DCM. A DCM is a board that works with a DMS350A.  However, the site has no DMS installed, just a UNC and MicroSmart controllers. Environment Niagara R2 DMS MicroSmart controllers Cause Polling is not enabled in the UNC's MicroSmart Service.  Resolution Re-enable polling and reboot the UNC. 
View full article
Picard Product_Support
‎2018-09-06 09:43 AM

Labels:
  • TAC IA Series
1121 Views

With the availability of TreeTech 3.2, can the version embedded with InVue be upgraded?

Issue Site has InVue with embedded TreeTech version 1.1.  Now that a newer version of TreeTech is available (version 3.2), can version 1.1 be upgraded? Environment InVue Wonderware for Intelligent Buildings (WIB) TreeTech Cause Product upgrade question Resolution TreeTech version 3.2 is not compatible with InVue.  TreeTech version 1.1 is the only compatible version with InVue. TreeTech version 3.2 is designed to run 'stand-alone'.  It is not designed to run with any other software package. It is used to backup GCM databases.
View full article
Picard Product_Support
‎2018-09-06 09:43 AM

Labels:
  • TAC IA Series
1366 Views

Can MOVs (metal oxide varistors) be installed on the main AC power connector of a MNL controller?

Issue Can MOVs (metal oxide varistors) be installed on the main AC power connector of a MNL controller? Site has dirty power issues. Environment MNL controllers Cause Site has dirty power issues which are causing damage to the MNL controllers Resolution Although it's not a supported configuration, the MOVs are electronically capable of being installed on the MNL controller's main AC power connector.
View full article
Picard Product_Support
‎2018-09-06 09:43 AM

Labels:
  • TAC IA Series
1052 Views

Can an analog value be totalized in a MNL controller?

Issue On a jobsite, an energy meter was converted from a pulse output to a voltage output.  Can the analog input be totalized in the associated MNL controller like the pulse input was previously? Environment MNL Cause Changes on-site Resolution Analog values cannot be totalized in the MNL controller.  The next best option is to send the real-time analog value to the area controller (i.e. Niagara UNC or ENC) via a nvo and use the features available at that level for totalization.
View full article
Picard Product_Support
‎2018-09-06 09:43 AM

Labels:
  • TAC IA Series
945 Views

How can the command and status of a start/stop point be separated in a Niagara G3 MicroSmart integration?

Issue In order to meet the requirements of a graphic display, the command and status of a fan are to be plotted individually.  A MicroSmart SS point integrates both command and status into one point.  When it's mapped to an ENC, the command "element" is not available.  How can they be separated and represented individually on a graphic? Environment MicroSmart Niagara G3 Cause The 'command' element is CTCMD but the Niagara G3 MicroSmart driver does not map it at the station level.  So, it's not available. Resolution Since CTCMD is not available, the best option is to modify the programming in the MicroSmart controller.  Remove the status feedback from the start/stop point and put it into its own point.  In this case, create a ST point.  Now, the STATS element for the start/stop point can be used to represent the fan command and the STATS element for the ST point can used to represent the fan status.  In Niagara G3, they exist as separate points and can, therefore, be mapped individually on a graphic.
View full article
Picard Product_Support
‎2018-09-06 09:42 AM

Labels:
  • TAC IA Series
1154 Views

I/A Series G3 mail service error: 'java.net.UnknownHostException: smtp.mail.yahoo.com - Authoritative Answer Host not found.

Issue I/A Series G3 mail service error: 'java.net.UnknownHostException: smtp.mail.yahoo.com - Authoritative Answer Host not found.  This error Indicates that the mail service in the I/A Series G3 platform is unable to establish communications to the SMTP mail server. Environment I/A Series G3 - all platforms Cause This error is typically related to the DNS settings where the URL cannot be resolved to an IP address. Resolution Verify and correct the DNS settings for the I/A Series G3 platform.
View full article
Picard Product_Support
‎2018-09-06 09:42 AM

Labels:
  • TAC IA Series
1723 Views

An upload of a GCM with TreeTech failed with this error: DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP1;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object nam...

Issue After initiating an upload of the GCM-86xxx database, the upload aborts and the following errors are displayed in the Notepad pop-up window: Finished Load of E:001.GCM_01 - ASDGCM5                 Request=Upload, Status = ABORTED. Load Time: 3 Min 53 Sec PANEL LOAD STATUS REPORT FOR: E:001.GCM_01.LCM_00: LOCAL                   Panel UpLoad Started at 03/04/2014 11:46:27 AM GETLIST:context=E:001.GCM_01.LCM_00 Build block list Create database records for blocks. DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP1;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object names must be all alpha-numeric or '_'.  DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP2;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object names must be all alpha-numeric or '_'.  DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP3;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object names must be all alpha-numeric or '_'.  Upload blocks from device. UPLDBLKS[9672]: error in locate of E:001.GCM_01.LCM_00.LABEL.^SSEP1;errnum1=-1,xffffffff;[xe012000d]Object not found  UPLDBLKS[9672]: error in locate of E:001.GCM_01.LCM_00.LABEL.^SSEP2;errnum1=-1,xffffffff;[xe012000d]Object not found  UPLDBLKS[9672]: error in locate of E:001.GCM_01.LCM_00.LABEL.^SSEP3;errnum1=-1,xffffffff;[xe012000d]Object not found  Panel UpLoad FAILED Time of Completion: 03/04/2014 11:50:17 AM UpLoad Time: 3 Min 50 Sec Environment TreeTech (all versions) Network 8000 Cause TreeTech only recognizes alpha-numeric characters and the underscore '_'. Resolution Rename the blocks listed.  In the example above, rename the three LABEL blocks from ^SSEP1, ^SSEP2, and ^SSEP3 to legal names.
View full article
Picard Product_Support
‎2018-09-06 09:42 AM

Labels:
  • TAC IA Series
1632 Views

Identify part number EMSC-603

Issue Identify part number EMSC-603 Environment SIGNAL software Cause Replacement Resolution Part # EMSC-603 is the hasp plug that's installed on a LPT1 port of a Windows XP or Windows 95/98 computer. It is no longer available for purchase.
View full article
Picard Product_Support
‎2018-09-06 09:42 AM

Labels:
  • TAC IA Series
1046 Views

In a G3 MicroSmart station, does the station point name have to match the point name in the MicroSmart controller?

Issue In a G3 MicroSmart station, does the station point name have to match the point name in the MicroSmart controller? Environment Niagara G3 MicroSmart driver Cause Replacing a MicroSmart controller database with a copy that has identical programming (including I/O assignments) but with different point names Resolution The MicroSmart driver does not use the point name as the link between the G3 station's point and the MicroSmart controller's point. If the I/O assignment is the same, then commands will work.
View full article
Picard Product_Support
‎2018-09-06 09:42 AM

Labels:
  • TAC IA Series
1054 Views

How can the time in a Niagara G3 ENC or Jace be changed from a web browser?

Issue How can the time in a Niagara G3 ENC or Jace be changed from a web browser? Environment Niagara G3 Cause Workbench not available Resolution It will require a change to the ENC/Jace license for Embedded Workbench. Then use Platform Services to edit the date/time. Drag Platform Services to a PX page, select Workbench View > System and Time Editor.
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • TAC IA Series
1247 Views

Can the setpoints on a SE7600 Room Controller be locked out on the keypad so no one can modify it?

Issue Can the setpoints on a SE7600 Room Controller be locked out on the keypad so no one can modify it? Environment SE7600 or VT7600 room controllers Cause Design feature Resolution There are three keypad lockout levels: 0 = Full access to both occupied and unoccupied setpoints 1 = Temporary override capability for both occupied and unoccupied setpoints 2 = No access to both occupied and unoccupied setpoints Review the engineering guide specifications at www.viconics.com.
View full article
Picard Product_Support
‎2018-09-06 09:41 AM

Labels:
  • TAC IA Series
1468 Views

Does the MNL controller line have any built-in surge protection for main AC power?

Issue Does the MNL controller line have any built-in surge protection for main AC power? Environment MNL controllers Cause Design specification Resolution No main AC power surge protection is part of the MNL controllers' design.  It will have to be externally applied.
View full article
Picard Product_Support
‎2018-09-06 09:40 AM

Labels:
  • TAC IA Series
945 Views

Values on graphic pages constantly showing 'down' momentarily

Issue Values on graphic pages constantly showing 'down' momentarily The following message can be seen in the standard output. "duplicate server session kills" Environment I/A Series R2 Enterprise Server Cause There is another copy of the same Enterprise Server station running on the network. In this particular case, there is a another computer on the network that has been licensed as an Enterprise Server and it has a copy of the Enterprise Server station. This computer is meant as a standby computer and the Enterprise Server station should not be running.  Resolution In this particular case, there is a another computer on the network that has been licensed as an Enterprise Server and it has a copy of the Enterprise Server station. This computer is meant as a standby computer and the Enterprise Server station should not be running.  Stop the Enterprise Server station that is running on the standby computer. From the Admin Tool, connect to the localhost and right click on the Enterprise Server station. Make sure auto run is uncheck. 
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • TAC IA Series
1667 Views

Niagara G3 Fails To Send Alarm Emails. Email Are Discarded with Null Pointer Exception

Issue Niagara G3 station fails to send out emails and discards to the email with this error message: "BOutgoingAccount could not dequeue in-memory email: null" Environment Niagara G3 (AX) ENC and ENS stations (all versions) Cause After watching the output with debug turned on, the station connects to the email server and authenticates. When it tires to send out an email there is a null pointer exception and it discards the email. There is a trailing semicolon in the To Field of the EmailRecipient under Alarm Service. The email handler is looking for another email address after the last semicolon and sees a null when trying to add the last non-existent email address.   Resolution Remove the trailing semicolon.  
View full article
Picard Product_Support
‎2018-09-06 09:39 AM

Labels:
  • TAC IA Series
3908 Views

Disabling Device Ping Alarms in Niagara G3 (AX)

Issue Would like the ability to disable "Ping Failed" alarms in G3 Environment Tridium Niagara G3 (AX) network controllers (ENC, JACE-645, JACE6, JACE7) Cause Network communication issues sometimes causes device to timeout on a ping request, but quickly recovers. This failure causes an unnecessary alarm to be generated. Resolution 1.  Go to the Property Sheet of the appropriate network (e.g.. Lonworks Network, Bacnet Network) 2.  Expand Monitor, and set the Alarm on Failure field to False. 3.  Click Save  
View full article
Picard Product_Support
‎2018-09-06 09:38 AM

Labels:
  • TAC IA Series
3458 Views

In a Niagara G3 station with a BACnet MSTP integration, the following error appears in the application director output: DCMD_MSTP_TX_FRAME returned 11 (errno 3)

Issue In a Niagara G3 station with a BACnet MSTP integration, the following error appears in the application director output: Transaction Timed out! invokeId 223 TransactionException in poll() for BacnetDevice {Kens_RM106}:pl=PollList [Kens_RM106 device:7219 3000:13] 196608025 {160} 10 PLEs) DCMD_MSTP_TX_FRAME returned 11 (errno 3) DCMD_MSTP_TX_FRAME returned 11 (errno 3) DCMD_MSTP_TX_FRAME returned 11 (errno 3) .... Hundreds & hundreds more Environment Niagara G3 Cause MSTP trunk / traffic issues Resolution See the discussion about an identical issue at Niagara-Central.com.  Here is a link:  https://community.niagara-central.com/ord?portal:/discussion/DiscussionThread/11258
View full article
Picard Product_Support
‎2018-09-11 07:17 AM

Labels:
  • TAC IA Series
4380 Views
  • « Previous
    • 1
    • …
    • 81
    • 82
    • 83
    • 84
    • 85
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore