Issue
Would like the ability to disable "Ping Failed" alarms in G3
Environment
Tridium Niagara G3 (AX) network controllers (ENC, JACE-645, JACE6, JACE7)
Cause
Network communication issues sometimes causes device to timeout on a ping request, but quickly recovers. This failure causes an unnecessary alarm to be generated.
Resolution
1. Go to the Property Sheet of the appropriate network (e.g.. Lonworks Network, Bacnet Network)
2. Expand Monitor, and set the Alarm on Failure field to False.
3. Click Save