When MicroSmart tunneling with Operator Interface, an error appears indicating that there are no MicroSmart controllers under the selected DCM.
  • When MicroSmart tunneling with Operator Interface, an error appears indicating that there are no MicroSmart controllers under...
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 09:43 AM
A site has a UNC-520 with ibsMs Service and approximately 20 MicroSmart controllers.  A serial tunnel is successfully established to the UNC.  From the Operator Interface main page, MicroSmart is accessed.  After a few seconds, an error appears indicating that there are no controllers under the currently selected DCM.
A DCM is a board that works with a DMS350A.  However, the site has no DMS installed, just a UNC and MicroSmart controllers.
Niagara R2
DMS
Polling is not enabled in the UNC's MicroSmart Service.
Re-enable polling and reboot the UNC.
  • TAC IA Series
  • 15519