Issue
On a jobsite, an energy meter was converted from a pulse output to a voltage output. Can the analog input be totalized in the associated MNL controller like the pulse input was previously?
Environment
MNL
Cause
Changes on-site
Resolution
Analog values cannot be totalized in the MNL controller. The next best option is to send the real-time analog value to the area controller (i.e. Niagara UNC or ENC) via a nvo and use the features available at that level for totalization.