An upload of a GCM with TreeTech failed with this error: DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP1;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object nam...
  • An upload of a GCM with TreeTech failed with this error: DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP1;err...
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 09:42 AM
After initiating an upload of the GCM-86xxx database, the upload aborts and the following errors are displayed in the Notepad pop-up window:
Finished Load of E:001.GCM_01 - ASDGCM5
Request=Upload, Status = ABORTED.
Load Time: 3 Min 53 Sec
PANEL LOAD STATUS REPORT FOR: E:001.GCM_01.LCM_00: LOCAL
Panel UpLoad Started at 03/04/2014 11:46:27 AM
GETLIST:context=E:001.GCM_01.LCM_00
Build block list
Create database records for blocks.
DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP1;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object names must be all alpha-numeric or '_'.
DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP2;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object names must be all alpha-numeric or '_'.
DBCRBLK: error in fi_addrec of E:001.GCM_01.LCM_00.LABEL.^SSEP3;errnum1=-1,xffffffff;errnum2=167,xa7;[xe012005e]Object names must be all alpha-numeric or '_'.
Upload blocks from device.
UPLDBLKS[9672]: error in locate of E:001.GCM_01.LCM_00.LABEL.^SSEP1;errnum1=-1,xffffffff;[xe012000d]Object not found
UPLDBLKS[9672]: error in locate of E:001.GCM_01.LCM_00.LABEL.^SSEP2;errnum1=-1,xffffffff;[xe012000d]Object not found
UPLDBLKS[9672]: error in locate of E:001.GCM_01.LCM_00.LABEL.^SSEP3;errnum1=-1,xffffffff;[xe012000d]Object not found
Panel UpLoad FAILED
Time of Completion: 03/04/2014 11:50:17 AM
UpLoad Time: 3 Min 50 Sec
TreeTech (all versions)
Network 8000
TreeTech only recognizes alpha-numeric characters and the underscore '_'.
Rename the blocks listed.
In the example above, rename the three LABEL blocks from ^SSEP1, ^SSEP2, and ^SSEP3 to legal names.
  • TAC IA Series
  • 15578