Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1688 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 73
    • 74
    • 75
    • …
    • 85
  • Next »
Label: "TAC IA Series" Show all articles

Niagara G3 alarm emails are not being received by email recipient.

Issue The EmailRecipient is not receiving alarm emails sent by a Niagara G3 station. Environment Niagara G3, ENS, ENC-520, ENC-520 Cause If spam filter is enabled, the SMTP server will not route email as long as the Reply to parameter of the OutgoingAccount is empty.  It will treat the message as spam. Resolution The OutgoingAccount’s “Reply To” field must contain an email address. - Open the station in the tree - Navigate to Config > Services > EmailServices > OutgoingAccount - Fill in a reply to email address in the “Reply to” field.       Note:  In some cases a factious email address of the format xxxx@xxx.comcan be entered.  However, depending on the SMTP server, the "Reply to: field must contain a valid email address on the local SMTP server.
View full article
Picard Product_Support
‎2018-09-10 11:46 AM

Labels:
  • TAC IA Series
1494 Views

Enterprise Network Server station failed

Issue Enterprise Network Server station failed. Attempts to start the station resulted in the following error messages. ERROR [15:32:36 04-Jul-12 SGT][sys] Cannot load station java.io.EOFException    at javax.baja.xml.XParser.read(XParser.java:753)    at javax.baja.xml.XParser.parseText(XParser.java:621)    at javax.baja.xml.XParser.next(XParser.java:268)    at javax.baja.io.BogDecoder.decodeDocument(BogDecoder.java:164)    at javax.baja.io.BogDecoder.decodeDocument(BogDecoder.java:152)    at com.tridium.sys.station.Station.loadStation(Station.java:128)    at com.tridium.sys.station.Station.bootStation(Station.java:78)    at com.tridium.sys.station.Station.main(Station.java:978)    at sun.reflect.NativeMethodAccessorImpl.invoke0(Native Method)    at sun.reflect.NativeMethodAccessorImpl.invoke(Unknown Source)    at sun.reflect.DelegatingMethodAccessorImpl.invoke(Unknown Source)    at java.lang.reflect.Method.invoke(Unknown Source)    at com.tridium.sys.Nre.runClass(Nre.java:224)    at com.tridium.sys.Nre.main(Nre.java:149) App Failed   Environment I/A Series G3 Cause The station's config.bog appears to be corrupted. The reason for this is unknown at this time. Resolution Restore the station database with the latest copy of a known good backup.
View full article
Picard Product_Support
‎2018-09-06 12:07 PM

Labels:
  • TAC IA Series
1507 Views

When was the GCS bus controller discontinued?

Issue When was the GCS bus controller discontinued? Environment Network 8000 Cause Field request Resolution The GCS controller was discontinued in 2001.  
View full article
Picard Product_Support
‎2018-09-10 12:09 PM

Labels:
  • TAC IA Series
1207 Views

A multiple page application file created with WorkPlace Tech 5.8.0 or 5.8.1 prints with page numbers 0 of 0 on all pages.

Issue When printing a multiple page application, i.e., an application consisting of a device definition and one or more custom object pages, all pages are numbered 0 of 0. Environment WorkPlace Tech Tool release 5.8.0 or release 5.8.1 Cause The title block stencil script created in WorkPlace Tech release 5.8.0 or release 5.8.1 does not execute properly resulting in all pages showing "Page 0 or 0". Resolution Update to WorkPlace Tech Tool release 5.8.2.  Note that upgrading will not automatically correct the issue in application files created with release 5.8.0 or release 5.8.1.  Use the following procedure to correct the issue in application files created with those releases of the WorkPlace Tech Tool software. Open the application using WPT 5.8.2. Select the "Background" page of the drawing. Press Ctrl-A to select everything on the page then press the Delete key to delete everything from the page. Select the "Annotation" style sheet (stencil page). Drag a new copy of the "Schneider Electric Border" stencil onto the page. Drag a new copy of the "Controller Info Block" stencil onto the page.  This block is normally placed in the lower left corner of the drawing. Save the updated application file.
View full article
Picard Product_Support
‎2018-09-06 11:13 AM

Labels:
  • TAC IA Series
1135 Views

How can I change the "State" of a "Unconfigured" LON controller using WorkPlace Tech so that it can be downloaded?

Issue Cannot download LON controller that is in the "Unconfigured" state. Environment I/A Series MNL series controllers Cause Controller was placed in the "Unconfigured" state by accidentally holding the service pin button too long. Resolution 1a.  If running the WorkPlace Tech Tool software under Microsoft Visio 2007 or earlier, select the "Configure LON Device" function under the Tools menu.  Continue with step 2, below. 1b.  If running the WorkPlace Tech Tool software under Microsoft Visio 2010, select "Configure" under the "Device" selection on the WorkPlace Tech Ribbon Bar. 2.  The "Configure Device" window will be displayed.  Use any of the standard methods; enter Neuron ID, Browse for device or Listen for Service Pin, to select the device. 3.  Click the [OK] button to reconfigure the device. 4.  A WorkPlace Tech status window will be displayed, normally displaying "Successfully configured the device.".  Click [OK] to close the window. The device is now in the configured mode and can be downloaded.
View full article
Picard Product_Support
‎2018-09-06 11:13 AM

Labels:
  • TAC IA Series
1537 Views

In OPRIF 11.6, the "database save" command does not work.

Issue In OPRIF 11.6, the "database save" command does not work.  When pressing "S" for save, the first prompt asks for the drive letter where the files will be saved (i.e. C drive).  After pressing enter, the second prompt requests a filename.  An eight-digit filename can be entered.  A file path is optional.  After pressing enter, a new screen should appear as the database save begins.  However, after pressing enter, the screen returns to the main database menu. There are no errors reported. Environment DMS OPRIF 11.x Cause A graphic screen is missing from the installation of OPRIF.  After entering the driver letter and filename for the database save, a new screen should appear.  The graphic file is requested but doesn't exist.  As a result, the database save command aborts and returns to the main database menu screen. Resolution The simplest solution is to re-install OPRIF 11.6 "overtop" the existing installation.  The missing file(s) will install.
View full article
Picard Product_Support
‎2018-09-06 11:13 AM

Labels:
  • TAC IA Series
825 Views

Unable to host a replacement NL220 dongle for a lost dongle

Issue When you get a replacement dongle for a lost NL220 dongle, NL220 will not let you confirm that dongle with the PC. You get an error message that indicates "Only one key can be confirmed and that the key confirmation will be canceled" Product Line Other, TAC IA Series, TAC Vista Environment NL220 Cause There is a NLS credit conflict that prevents the replacement dongle from confirming with the PC. Resolution You can force a confirmation by following these steps. You run NL220 and wait the error message to appear When you have the error message press Ctrl+shift+n This will then let you confirm the new dongle on your computer.
View full article
Picard Product_Support
‎2018-09-06 11:13 AM

Labels:
  • TAC IA Series
  • TAC Vista
1201 Views

WorkPlace Tech 5.x BACnet IP communications is not working

Issue WorkPlace Tech 5.x BACnet IP communications is not working. BACnet Ethernet communications works. Environment I/A Series WorkPlace Tech 5.x Symantec Endpoint Protection version 11.0.4202.75 Cause This has been found to be caused by the Symantec Endpoint Protection version 11.0.4202.75. It appears to be blocking the BACnet IP traffic. BACnet IP communications in WorkPlace Tech is working on another computer which has Symantec Endpoint Protection version 11.0.6200.754 installed and the Symantec Management Client service running. It is not known if the issue is actually an issue with the Symantec version or if it is caused by settings in the Symantec Endpoint Protection application. Resolution Stop the Symantec Management Client service when you need to use BACnet IP communications in WorkPlace Tech. (In Windows, go to 'start' > 'run'. Type in 'services.msc' and click 'OK'. This is the shortcut to the Services). The Symantec Management Client service provides communication with the Symantec Endpoint Protection Manager, controls SMC.exe and SMCgui.exe processes. Explanation for Processes and Services used by Symantec Endpoint Protection can be found here. It is recommended that the Symantec Management Client service be restarted after using WorkPlace Tech to ensure that your computer is protected against threats.
View full article
Picard Product_Support
‎2018-09-06 11:29 AM

Labels:
  • TAC IA Series
1642 Views

What is the warranty on a I/A Series product?

Issue What is the warranty on a I/A Series product? Environment N.A. Cause Field office question Resolution Refer to "Warranty" section of the "Terms and Conditions" document found under the Products menu of the iPortal web site.  Note that these warranty terms only apply to those that buy our products direct from Schneider Electric.  End user warranty terms are usually determined by the installing office.
View full article
Picard Product_Support
‎2018-09-06 11:12 AM

Labels:
  • TAC IA Series
931 Views

Software Support for Design 360 and Studio 360

Issue Technical support contact information for Design 360 and Studio 360 Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Design 360 Studio 360 Cause Design 360 or Studio 360 has issues requiring technical support assistance which is not provided by PSS. Resolution Schneider Electric Employees should contact PSS who will provide you with your Branch Administrator and Technical Expert contact information. Partners may contact Smartware directly for any support of the tool at: Email: techsupport@smartwaretech.com Phone: (716) 213-2222
View full article
Picard Product_Support
‎2018-09-10 10:33 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
3937 Views

Shield grounding details for the B-LINK-AC BACnet MS/TP repeater.

Issue Communication issues caused by improper grounding of the BACnet MS/TP shield connections to the B-LINK-AC repeater.   Environment BACnet MS/TP installation with B-LINK-AC repeaters. Cause The shield connection on port 1, labeled "(Input)", of the B-LINK-AC repeater is internally wired differently than the four other ports. Resolution Due to the differences in how the shield terminals are wired, the following techniques must be followed when wiring the B-LINK-AC BACnet MS/TP repeater. Port 1, marked (Input), must have its MS/TP bus shield connected to the SHLD terminal, which is isolated from Earth Ground. The incoming MS/TP shield must be grounded at only one point, at a location other than the repeater. Typically this is at the opposite end of the bus, or where the MNB-1000, UNC, ENC or other BACnet parent controller resides. All four of the other repeater ports, # 2 - 5, have their SHLD terminals tied together, and tied to Earth Ground internally, through the power supply's Earth Ground connection. For each MS/TP bus cable connected these ports, the single point of ground for the shield is at the repeater and, therefore, the shield must not be grounded at any other point on the bus. None of the five MS/TP ports on the repeater have internal termination resistors.  If a MS/TP trunk ends at the repeater, a 120 ohm terminating resistor must be connected between the MSTP+ and MSTP- terminals on that port of the repeater.  Likewise, the far end of each MS/TP trunk must also be terminated with a 120 ohm resistor between the MSTP+ and MSTP- terminals of that last controller. None of the five MS/TP ports on the repeater have internal bias resistors.  Standard practices, regarding the biasing of the MS/TP trunks, should be applied, as described in the I/A Series MicroNet BACnet Best Practices Guide, F-27360. Additional information on the use of these repeaters can be found in the "Approved MS/TP Repeaters" section of Chapter 5 of the I/A Series MicroNet BACnet Smoke Control Systems manual, F-27419.
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • TAC IA Series
2266 Views

Computer is licensed for the I/A Series G3 software but gets error "Workbench not licensed to run on this machine".

Issue License is installed on computer but software still says that the computer is not licensed. Environment I/A Series G3 software installed on a Windows computer. Cause Tridium software certificate was not installed properly or has been damaged. Resolution Copy the file "Tridium.certificate" from the certificates folder of another version of the I/A Series G3 software into the certificates folder of the current version. The correct file location is C:\niagara\niagara-3.x.xx\certificates where 3.x.xx is the software version number.
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • TAC IA Series
1099 Views

Can the MNB-Vx be mounted upside down?

Issue Can the MNB-Vx be mounted upside down? Environment MNB Cause Unusual site installation - VAV boxes mounted upside down for better access to the damper shaft Resolution There is no mounting orientation specified for the MNB-Vx controller.  Ensure that all other mounting instructions are followed for proper operation.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • TAC IA Series
1097 Views

How can thousands of unacknowledged alarms and exceptions be deleted quickly in SIGNAL?

Issue How can thousands of unacknowledged alarms and exceptions be deleted quickly in SIGNAL? Environment SIGNAL (all versions) Cause Months of unacknowledged alarms and exceptions were allowed to accumulate. Resolution The files containing all the alarms and exceptions are located in the SIGNAL\ALARM and SIGNAL\EXCEPT folders respectively. Shutdown SIGNAL (all programs).  In the ALARM folder, delete the alarm_a.dat, alarm_u.dat, and alarm_l.num files. In the EXCEPT folder, delete the excep_a.dat, except_u.dat, and excep_l.num files. Reboot the computer.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • TAC IA Series
895 Views

Some of the dynamic values on a graphic screen in InVue are not updating.

Issue Each time an InVue graphic screen appears, not all of the dynamic values (tags or remote references) update.  No error messages appear. Environment InVue 1.1 WIBS 1.1 Wonderware Cause The InVue computer hardware was replaced.  It has a dual/multi-core CPU which was never validated with InVue. Resolution Disable the settings in the computer's BIOS such that the CPU behaves like it is a single-core.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • TAC IA Series
1283 Views

Will the Vykon Alarm Service run on a Niagara G3 Soft Jace or ENC?

Issue Will the Vykon Alarm Service run on a Niagara G3 Soft Jace or ENC? Environment Niagara G3 Cause Application specific for a jobsite Resolution No.  The Vykon Alarm Service is only supported on an Enterprise Network Server (ENS).
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • TAC IA Series
1367 Views

Installed I/A Series G3 Workbench on a new computer with Windows 7 Professional 32-bit and the host ID changes each time Workbench is started.

Issue Installed I/A Series G3 Workbench on a new computer with Windows 7 Professional 32-bit and the host ID changes each time Workbench is started.  This has been seen on new Dell laptops and computers that have been provided a replacement hard drive with Dell operating system (Microsoft OS) installation disks. Environment I/A Series G3 build 3.4.xx, Enterprise Server, Workbench Cause Host IDs continuously change as the software does not have rights to write the encrypted host ID key into the registry. Resolution Locate the Niagara service and Workbench executables (niagarad.exe and wb.exe).  These files are located under the niagara's directory (bin folder).          Example: \niagara\niagara-3.x.xx\bin Right click and select properties for each executable. Select the compatibility tab and check the "Run this program as an administrator" privilege level checkbox.  The host ID is now allowed to be written to the registry by the software.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • TAC IA Series
1189 Views

"License Invalid" or "License Registry Error" displayed when opening the WorkPlace Tech Tool program.

Issue Popup window displays "License Invalid", "License Registry Error", "License on wrong machine" or other related error when starting the WPT software. Environment WPT software (any release) Cause License information stored in license file does not agree with the WPT/WPTL license information stored in the Windows registry. Resolution Use the following procedure to locate the proper version of the program and to generate the license diagnostic text file.  NOTE: If the old computer has WorkPlace Tech release 4.0.0 or release 5.x.x prior to release 5.7, skip step 2 in the following procedure. Open the Windows Explorer (My Computer icon) Search for the file "WPTLDiag.exe" in the Program Files folder of the C:\ drive (or drive where the program files have been installed).  If found, skip to step 4, below. Search for the file "WIBSLicenseDiag.exe" in the Program Files folder of the C:\ drive (or the drive where the program files have been installed). Right-Click on the file found in step 2 or 3 and select "Open".  This will cause the license diagnostic program to run. When the program opens its display, select Save from under the File menu and save the "WIB License Diagnostic.txt" file. Locate the license file listed on line 1 of the WIB License Diagnostic display. Email the complete displayed text error message along with a zipped copy of the license file and diagnostic output file to Product Support A product support case will be created for you with the submitted information.  A product support engineer will contact you after reviewing your submitted information to assist you in correcting the issue.
View full article
Picard Product_Support
‎2018-09-06 11:50 AM

Labels:
  • TAC IA Series
2071 Views

'Error waiting service pin' when attempting LonWorks communications in WorkPlace Tech

Issue 'Error waiting service pin' when attempting LonWorks communications in WorkPlace Tech Environment I/A Series WorkPlace Tech Echelon U10 USB Network Interface Cause WorkPlace Tech is not recognizing the Echelon U10 USB Network Interface.  The U10 USB Network Interface is recognized correctly in Windows Control Panel > LonWorks Interfaces.  Resolution Reinstall the U10 USB Network Interface and the Echelon Open LDV driver. To uninstall the U10 Network Interface (with the U10 Network Interface physically connected to an USB port): In Windows, go to 'start' > 'run', type in 'devmgmt.msc' and click 'OK'. This will bring up the Device Manager.  Expand 'Universal Serial Bus controller'. You should be able to see 'Echelon USB Network Interface'. Right-click on the 'Echelon USB Network Interface' and select 'Uninstall'. Remove the U10 Network Interface from the USB port. To reinstall the Open LDV driver: Uninstall Echelon Open LDV driver from Windows Add or Remove Programs. Install Echelon Open LDV driver using the installation file.  After completing the above steps, connect the U10 Network Interface to an USB port on the computer. It should automatically install. Test with WorkPlace Tech. 
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • TAC IA Series
4566 Views

Cannot add the HistoryPointList object to an ENC Niagara G3 station.

Issue  The Platform Software Manager shows that the History module is installed in the ENC, but a HistoryPointList object cannot be added to the ENC.   The error message “drop failed: java.baja error” is displayed in the Program Director window. Environment Niagara G3 all version, ENC-410, ENC-520 Cause The HistoryPointList object requires that the ENC’s Module Content Filter be set to  ui+runtime. Resolution Set the ENC’s Module Content Filter Level to ui+runtime. 1. Open the ENC’s Platform and click on Set Module Filter 2. Select ui+runtime and then click on Finish. The HistoryPointList object can now be added to the ENC.
View full article
Picard Product_Support
‎2018-09-06 11:05 AM

Labels:
  • TAC IA Series
974 Views
  • « Previous
    • 1
    • …
    • 73
    • 74
    • 75
    • …
    • 85
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore