Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 73
    • 74
    • 75
    • …
    • 500
  • Next »

How long is the battery backup on the 7716?

Issue How long is the battery backup on the 7716? Environment I/NET site Cause How long is the battery backup on the 7716? Resolution The battery backup of a 7716 will last 30 Days. Refer to TCON 096.
View full article
Picard Product_Support
‎2018-09-07 12:34 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Labels:
  • TAC INET
1141 Views

How long does PSS support a product after it is released?

Issue How long does PSS support a product after it is released? Product Line Andover Continuum, EcoStruxure Building Operation, TAC IA Series, TAC INET, TAC Vista Environment All Schneider Electric Buildings Business software platforms Cause After a few years, the majority of issues with a release product are documented in the Knowledge Base.  At this point, if the customer is having issues requiring Product Support, we ask that they upgrade to the current version. Resolution Please read the following Product Announcements: PA_00271 Software Support Policy - General Overview.pdf PA_00272 Software Support Policy - Supplementary info for_Andover_Continuum.pdf PA_00274 Software Support Policy - Supplementary info for TAC Vista.pdf PA_00279 Software Support Policy - Supplementary info for TAC INET.pdf PA_00280 Software Support Policy - Supplementary info for TAC IA Series.pdf
View full article
Picard Product_Support
‎2018-09-07 02:30 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC INET
  • TAC Vista
1753 Views

How does the SNMP agent in TAC Xenta Server work and what are the limitations?

Issue Can I send live data over SNMP? How many trap pages can I define? Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731 Cause All Xenta Servers (except Xenta 913 and Xenta 527-NPR) have a built in SNMP agent. However, the SNMP protocol in them cannot handle sending live data over SNMP. It can only send alarms along with specific fields of those alarms.   Resolution The Xenta Server supports SNMP version 1 and SNMP Traps. It can only be used to send SNMP and not to receive. The first step to setting up SNMP is to create alarms in XBuilder and link the points to the alarms that are to be monitored. Then, the filters used by the SNMP traps should be defined. This is done using SNMP trap pages. SNMP Trap Page The SNMP trap page is where you define a set of rules in Xbuilder of when to send a trap to the SNMP manager. This includes severity of the alarm or a wildcard string based on the address of the point.  In XBuilder you can create up to 10 SNMP trap pages, which will give you possibilities to define 10 different alarm filters. An SNMP trap page is created by right-clicking a folder in the System pane of XBuilder and then selecting New > Page > SNMP Trap Page. (It is recommended that a separate folder be created for SNMP trap pages and that this folder be restricted to only system administrators.) Once the SNMP trap page has been created it is then configured by right-clicking on the SNMP trap page object and selecting SetupSNMP Trap Filter.   SNMP Field Configuration The SNMP field configuration is where you define what 8 pieces of data will be sent to the SNMP manager (due to the UDP limit of 8 fields). That data consists of things like date/time, type, address, priority, description, etc. The SNMP field configuration is accessed by clicking on the Tools menu and selecting SNMP Field Configuration.     For more information on SNMP in Xenta Servers please see the TAC Xenta Server - TAC Networks Technical Manual, section 16. Note: SNMP is only supported by Xenta Server devices and is not supported by TAC Vista.  
View full article
Picard Product_Support
‎2018-09-10 01:02 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
1754 Views

How do you integrate MNL version 3 controllers into a SmartStruxure solution Automation Server?

Issue I/A Series MNL version 3 controller profiles are not shown in the list when adding a new LON device to a SmartStruxure Automation Server.  How do I add the template for one of those controllers to the Automation Server? Environment SmartStruxure 1.3 or newer Automation Server I/A Series MNL version 3 or earlier controllers. Cause Templates are not provided in SmartStruxure 1.3 for the older families of I/A Series MNL controllers Resolution Import a device template per StruxureWare Building Operation release 1.3 Technical Reference Guide section 40.14. This procedure is used any time the device template was not pre-defined or has not been imported into the AS. The templates for the older MNL family of controllers can be downloaded from the Download Center. You should also download the associated readme file so that you understand the arrangement of the files in the folders of the zip file. We suggest that you download and unzip the entire file to your computer using the folder structure contained in the zip file. The readme file lists the xif files contained in each of the xif folders. The xif files contained in the xif_40 folder are already contained in the SmartStruxure 1.3 system. When importing these templates into StruxureWare 1.3, you may get some warnings about SelfDoc strings and possibly errors about missing DRF types. Both issues can be ignored. If errors are reported regarding missing DRF types, click the [No] button to continue the import process.   After importing the template, you can then create the device under the LonWorks network as defined in the StruxureWare Building Operation Technical Reference Guide section 40.2. The template that you imported will be listed based on the name and profile of the device. You can assign a name of your choice (or use the default) for the created device. After device NeuronID or using the service pin process to send it from the controller, you then commission the added device. You should select the option "Keep current configuration in the device". Do not check the "Device application file" because the I/A Series MNL controllers do not use loadable executable files.
View full article
Picard Product_Support
‎2018-09-11 08:40 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1728 Views

How do I upgrade a WorkPlace Tech Tool drawing created in version 3.1 to the latest version?

Issue Upgrading computer to a newer version of the WorkPlace Tech Tool and need to tell customer how to upgrade his existing files. Environment Application drawings created in WPT 3.2 or earlier WPT 5.8 is now installed. Cause An internal change was made to the WorkPlace Tech Tool drawing format in WPT 3.2sp1.  Drawings must be in the format created by this version before they can be automatically be upgraded to a newer version. Resolution NOTE: DO NOT INSTALL WORKPLACE TECH 3.2 ON A COMPUTER THAT ALREADY HAS AN NEWER INSTALLATION OF THE WORKPLACE TECH TOOL SOFTWARE INSTALLED.  If this is the case, a different computer must be used for the conversion. Follow the directions in the "WorkPlace Tech Tool Version 3.2 Service Pack 1 Installation Instructions. This document along with the WPT32.exe  and WPT32sp1_Lite.exe software can be downloaded from The Exchange Download Center. Although the installation instructions document states that WPT32 runs only on Windows 2000, it will also run properly on Windows XP.  Visio 2000sp1 is required for WorkPlace Tech 3.2. The procedure for converting the application file is as follows. You may either copy the entire project folder from the existing version of WPT into the 3.2sp1 projects folder or create a new project under WPT32.sp1.  After creating the new project copy the applications to be converted into that project folder and add them to the project. Open the application to be converted using WPT2.3sp1, allow any processing to occur then compile the application. If any errors occur when processing or compiling, the errors must be corrected before continuing.  If the existing version of the application nearly or completely fills the controller there is a slight chance that the upgraded application may not fit in the controller. After correcting any errors and successfully compiling the application, make sure that the application drawing file has been saved.  The converted application file may now be copied to and added to a project in the WorkPlace Tech Tool release 5.x.x.
View full article
Picard Product_Support
‎2018-09-10 05:12 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC IA Series
1118 Views

How do I request a new TIP (Demo) license for the I/A Series G3 software?

Issue How do I request a new TIP license for the I/A Series G3 software? Environment I/A Series G3 software installation Cause I/A Series G3 License request process for field offices on the TIP program has changed. Resolution See Product Announcement PA-00186 for details. Please note that the demo license described in this document is only available to our partner offices that participate in the TIP program.  If your office does not participate in the program, please contact your regional sales manager for more information. As noted in the license forms, the completed request should be emailed directly to our I/A Series R2/G3 license team at IASeries.License@schneider-electric.com.
View full article
Picard Product_Support
‎2018-09-10 07:45 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC IA Series
1367 Views

How do I determine which version of the VAS client is needed to update a site?

Issue The current version of the VAS client cannot query for records for years beyond 2010. There are two versions of the VAS Client upgrade on The Exchange Download Center. How do I determine which version of the VAS client is needed to update a site? Environment I/A Series R2 Enterprise Server Vykon Alarm Service Client 2.4x Vykon Alarm Service Client  3.xx Cause The Query Wizard in the VAS 2.4 system could not query record dates beyond 2010. Resolution VAS Client 2.50 -- The VAS_2.50_Client.zip file contains the VAS 2.50 Client Installer and associated Enterprise Server vas service module (vas-2.301.532.v2.jar). VAS 2.50 is for use with Enterprise Servers that utilize database management systems including Cloudscape, MSDE, Microsoft SQL, or Oracle. If currently using VAS 2.4x, upgrade to vas-2.301.532.v2 jar and VAS 2.50 client. If currently using VAS 3.xx, do not install this version. Download and upgrade to vas-2.301.532.v3.jar and VAS 3.92 client. VAS Client 3.92 -- The VAS_3.92_Client.zip file contains the VAS 3.92 Client Installer and associated Enterprise Server vas service module (vas-2.301.532.v3.jar). VAS 3.92 is for use with Enterprise Servers that utilize MSDE, Microsoft SQL, or Oracle database management systems only. VAS 3.92 Is not compatible with Cloudscape. If currently using VAS 3.xx, upgrade to vas-2.301.532.v3 jar and VAS 3.92 client. If currently using VAS 2.4x, do not install this version. Download and upgrade to vas-2.301.532.v2.jar and VAS 2.50 client.
View full article
Picard Product_Support
‎2018-09-10 11:08 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC IA Series
1792 Views

How do Controller LANs connect to Host LANs?

Issue How do Controller LANs connect to Host LANs? Product Line TAC INET Environment I/NET Site Cause Understanding network architecture can help design and servicing of networks. Resolution Controller LANs connect to Host LANs through Link Taps. (TCON209, 1-5). Refer to Explain and define I/NET Ethernet, C-LAN, and Sub-LAN communication for further explanation.
View full article
Picard Product_Support
‎2018-09-07 12:25 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1346 Views

How can you determine what standard drivers are included with the basic I/A Series G3 hardware product license?

Issue How can you determine what standard drivers are included with the basic I/A Series G3 hardware product license? Environment I/A Series G3 (Niagara) hardware License (ENS, ENC, NXT, etc.) Cause Product data sheet is not clear in regards to what license options are included with the standard basic license for an I/A Series G3 hardware products. Resolution Refer to the TAC I/A Series G3 Hardware License Request form. In the "I/A Series G3 Drivers" section of the form there is a box that contains text beginning with "Standard drivers for the xxx include".  This box lists the complete set of standard drivers included with the license for associated hardware product. For example, at the time this is written, the ENC-520 Series TAC I/A Series G3 Hardware License Request form shows the following: This box indicates that the following drivers are included with the standard license for an ENC-520. LON BACnet-IP / BACnet-Ethernet (Client only) BACnet MS/TP oBix Client / Server The ENS-1, ENC-410 and JACE-NXT have similar lists of included drivers.  Refer to the license request form for the hardware product for the list of included drivers.
View full article
Picard Product_Support
‎2018-09-10 08:19 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC IA Series
1250 Views

How can an existing Enterprise Server station be configured to run the Vykon Alarm Service (VAS)?

Issue How can an existing Enterprise Server station be configured to run the Vykon Alarm Service (VAS)? Environment Enterprise Server Vykon Alarm Service Cause For Enterprise Server to support VAS, check the Enterprise Server shipped date to determine if part number IA-ENT-AS is required. Resolution An Enterprise Server station is already licensed to support VAS. It also includes support for two VAS clients. If additional clients are required, order part number IA-ENT-AS-C for each additional client. If the Enterprise Server was shipped before November 1, 2002, it did not include support for VAS. It must be ordered separately using part number IA-ENT-AS (which will also include support for two VAS clients). The Enterprise Server must also be upgraded to, at minimum, build r2.301.330. For more information, review R2 Worksheet (xlt) tab "ENT SVR Estimator" for additional notes on various part numbers. VAS software can be downloaded from The Exchange. Download VAS v2.4 CD Image.zip and VasPatch.zip. Unzip the CD Image for the Installation Instruction Manual. The VasPatch is installed last.
View full article
Picard Product_Support
‎2018-09-07 04:16 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC IA Series
1313 Views

How can a new Source website account be obtained?

Issue How can a new Source website account be obtained? Product Line TAC IA Series Environment Repository for all I/A files from legacy programming tools to new released versions or updates of Niagara and WorkPlace Tech Cause New employee of a Schneider Electric branch or partner Resolution The Source has been deactivated and all files have been migrated to The Exchange. Navigate to The Exchange Extranet and register for a new account. For more information on registration, see Register for The Exchange.
View full article
Picard Product_Support
‎2018-09-11 04:32 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC IA Series
1260 Views

How can a backup of an MNB controller, including app and links, be made so that if the controller fails, it can be completely reloaded.

Issue Need to save the application, configuration and COV link data for an MNB-controller so that in the event the controller fails, all the information can be easily reloaded into a new controller. Environment MNB family controllers WorkPlace Commissioning Tool, version 5.7.2 or newer Cause Need to save the application, configuration and COV link data for an MNB-controller so that in the event the controller fails, all the information can be easily reloaded into a new controller. Resolution The Backup and Restore facility of WorkPlace Commissioning Tool allows the user to backup the complete controller application, configuration, flow balance and COV link data for a single or multiple controllers or restore of a single controller on a given network in a simple operation.  The procedures for using the Backup and Restore functions of the WPCT are included in the WorkPlace Tech Tool version 5.7.2 release notes.  The Backup and Restore documentation is available via this WorkPlace Tech Tool release 5.7.3 Release Notes from The Exchange Download Center.
View full article
Picard Product_Support
‎2018-09-10 07:13 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC IA Series
1081 Views

How can I know when new products are released?

Issue How can I know when new products are released? Environment I/NET Site Cause How can I know when new products are released? Resolution Visit the Building Business Extranet. Email a request to the Buildings Business ExchangeMail marketingadmin@buildings.schneider-electric.com
View full article
Picard Product_Support
‎2018-09-06 11:33 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1429 Views

How are inputs configured on two AC-1, AC-1A, or AC-1 Plus modules when configured as dual reader doors?

Issue How are inputs configured on two AC-1, AC-1A, or AC-1 Plus modules when configured as dual (entry / exit) reader doors? Are there any restrictions on which input channels can be used and for what purpose? Environment Continuum IOU Door Module's AC-1 AC-1A AC-1 Plus Cause There are differences to how the inputs can be configured on AC-1, AC-1A, and AC-1 Plus modules when being used in a dual (entry / exit) reader door configuration. Resolution The below information can also be referenced  in the I/O System Reference Guide. 1. AC-1's in Dual Reader Mode (page 141) The inputs are fixed for a specific purpose. Channel 1 is an Auxiliary input that can be configured as an InfinityInput outside of a door object, whereas channel 2 is the Door Switch and channel 3 the REX which can only be configured in the Door object. The Door Switch is only physically connected to channel 2 of the Entry AC-1 module. Although, the Exit AC-1 module must have the same resistor configuration on its channel 2 as what is being used for the Door Switch on the Entry AC-1. Channel 2 and 3 on both the Entry and Exit AC-1's cannot be created, and used, as InfinityInputs - they are to only be configured and used in a Door object. 2. AC-1A's in Dual Reader Mode (page 159) Same as the AC-1 except the resistors are not required at the Exit AC-1A's Door Switch channel. 3. AC-1 Plus in Dual Reader Mode (page 186) Any of the supervised input channels can be configured in the door object. Whichever channels are used for Door Switch and Bond Sensor on Entry AC-1 Plus must be wired into the same channels on the Exit AC-1 Plus and these must have the same resistor configuration. Both of these channels on both AC-1 Plus modules are now unavailable to be used as InfinityInputs. Any Supervised input channels not used in the door object can be created and used as InfinityInputs.  
View full article
Picard Product_Support
‎2018-09-10 03:29 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • Andover Continuum
1347 Views

Health status shows "too many remote controllers assigned" message

Issue Controller Health Status shows, "Controller (ID **) has too many Remote Controllers assigned." What does this message mean, and is it a cause for concern? Product Line Security Expert Environment Security Expert Client SP-C Controller Cause This error message is related to cross controller communication. When using cross controller communications, the maximum number of controllers that can be linked together is 64. For additional details on cross controller communications, see page 4 of AN 180 Security Expert - Cross Controller Operations - Integration Guide. Resolution The controllers that are not taking part in cross controller linking are the ones that are showing the "Controller (ID **) has too many Remote Controllers assigned." message. Evaluate what values/controllers are being shared to ensure your programming is performing as expected. See AN 180 Security Expert - Cross Controller Operations - Integration Guide for further details on cross controller communications and which values use this. Limit the number of sharing controllers to 64 or split the controllers up into two systems.
View full article
Guinan AdamSteele Guinan
‎2020-06-22 04:22 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • EcoStruxure Security Expert
1307 Views

Having a mix of Cyberstation versions on the same system

Issue Is it possible to have different software versions on the Cyberstation workstations? Product Line Andover Continuum Environment Continuum Cyberstation Cause When adding an extra workstation to a system does it have to match the version of existing workstations? Resolution All workstations on the same system must be exactly the same version including any service packs. This also includes Web Client servers. You will either need to install the same version as the rest of the system or upgrade all other workstations to the latest version, although this may need an upgrade of the security keys. Cyberstation software can be downloaded from The Exchange Download Center.  
View full article
Picard Product_Support
‎2018-09-09 09:46 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • Andover Continuum
1499 Views

Have the VZ22, VZ32, VZ42 valves been replaced by the VZ219, VZ319, VZ419 series?

Issue Have the VZ22, VZ32, VZ42 valves been replaced by the VZ219, VZ319, VZ419 series? Product Line Field Devices Environment Vista Satchwell Continuum Micronet Sigma Cause VZ*19* zone valves now available with equal or better specification than the older VZ*2 valves Resolution As per PA-00911 the VZ22, VZ32, VZ42 series valves are no longer available for sale.  The alternative is the standard catalogue zone offer, either the VZ*08* with MZ140 for thermal (low cost, silent) solutions, or the VZ*19* with MZ20 for a Motoric actuator solution. The alternative range VZ*08E or VZ*19*, is lower in cost and would be a suitable replacement in most applications. For high pressure applications, the VP228E PIBCV would be a suitable alternative. There should be no technical concern with changing over a PIBCV from a zone valve if the system pressure is above 25 kPa. There will be slight dimensional differences in the zone valve body length but for most installations the existing pipework should be able to accommodate the difference. A cross reference from the discontinued offer to the new offer is detailed PA-00911.   Datasheets for all valves and actuators can be found here or here for MZ18A, MZ18B, MZ20A, MZ20B, VZ*19*
View full article
Picard Product_Support
‎2018-09-06 12:02 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • Field Devices
2310 Views

HHC cable to connect to LTS80U Space Sensor Assemblies (maintenance) port

Issue What HHC cable do I need to connect to a LTS80U Space Sensor Assemblies (maintenance) port? Environment LTS80U Space Sensor Assembly Hand Held Console Cause Connecting the HHC allows for configuration. Resolution The part number is 602135-0002. It is a two foot (or 60 cm) straight, silver modular cable; Console-3. Refer to TCON 073 for more details.
View full article
Picard Product_Support
‎2018-09-06 09:27 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1179 Views

Guidelines for using large numbers in Access Control

Issue Are there any documented guidelines for using large number in Access Control? Product Line TAC INET Environment I/NET Site Cause Are there any documented guidelines for using large number in Access Control? Resolution Begin by referencing TCON 300. All SLIs and DPUs must use I/NET Seven revision 1.x (or later) compatible binary software. All DPUs must have DIP switch 7 set to ON. Within a single tenant, you can assign a large key/card number directly to an individual, or translate the number using the Key/Card Translation table, but not both (i.e., you cannot have duplicate key/card numbers or individual numbers within a single tenant). Use compatible EPROMs in the DPUs Note: If you directly assign a key/card to an individual, and later translate the same key/card for another individual, only the translated key/card will be operational within I/NET. Other useful articles: SCU dip switch 6 for dual station addressing How to convert existing Idisc to large numbers (Hex) DPU memory allotment in a 7910A and a Non-mipped 7920
View full article
Picard Product_Support
‎2018-09-06 11:03 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Labels:
  • TAC INET
1381 Views

Getting distribution file installation (no core software) error when attempting to commission the JACE-6E.

Issue Getting distribution file installation (no core software) error when attempting to commission the JACE-6E.  The error states "No core software was found that can be installed to the remote host." Environment I/A Series G3, JACE-6E, TRD-J-600E Cause Attempting to install an I/A Series G3 version that is not compatible with the JACE-6E platform (e.g. versions below 3.6.47). Workbench not set up to be an installation tool (required distribution files are not available within the Workbench environment). Resolution Attempting to install an I/A Series G3 version that is not compatible with the JACE-6E platform (e.g. versions below 3.6.47). The TRD-J-600E is compatible with I/A Series G3 version 3.6.47.1 or later. The I/A Series ENS with Workbench files are available for download from The Exchange Download Center. Workbench not set up to be an installation tool (required distribution files are not available within the Workbench environment). Re-install the I/A Series G3 software and enable the checkbox that configures Workbench to be an installation tool. The checkbox indicates "This instance of TAC I/A Series Enterprise Network Server will be used as an installation tool." The distribution files related to each of the platforms will be installed on the computer.
View full article
Picard Product_Support
‎2018-09-11 08:41 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM

Labels:
  • TAC IA Series
2585 Views
  • « Previous
    • 1
    • …
    • 73
    • 74
    • 75
    • …
    • 500
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore