How are inputs configured on two AC-1, AC-1A, or AC-1 Plus modules when configured as dual reader doors?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How are inputs configured on two AC-1, AC-1A, or AC-1 Plus modules when configured as dual reader doors?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1342 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How are inputs configured on two AC-1, AC-1A, or AC-1 Plus modules when configured as dual reader doors?

Picard Product_Support
‎2018-09-10 03:29 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:43 AM

Issue

How are inputs configured on two AC-1, AC-1A, or AC-1 Plus modules when configured as dual (entry / exit) reader doors? Are there any restrictions on which input channels can be used and for what purpose?

Environment

Continuum IOU Door Module's

  • AC-1
  • AC-1A
  • AC-1 Plus

Cause

There are differences to how the inputs can be configured on AC-1, AC-1A, and AC-1 Plus modules when being used in a dual (entry / exit) reader door configuration.

Resolution

The below information can also be referenced  in the I/O System Reference Guide.

1. AC-1's in Dual Reader Mode (page 141)

The inputs are fixed for a specific purpose. Channel 1 is an Auxiliary input that can be configured as an InfinityInput outside of a door object, whereas channel 2 is the Door Switch and channel 3 the REX which can only be configured in the Door object.

The Door Switch is only physically connected to channel 2 of the Entry AC-1 module. Although, the Exit AC-1 module must have the same resistor configuration on its channel 2 as what is being used for the Door Switch on the Entry AC-1.

Channel 2 and 3 on both the Entry and Exit AC-1's cannot be created, and used, as InfinityInputs - they are to only be configured and used in a Door object.

2. AC-1A's in Dual Reader Mode (page 159)

Same as the AC-1 except the resistors are not required at the Exit AC-1A's Door Switch channel.

3. AC-1 Plus in Dual Reader Mode (page 186)

Any of the supervised input channels can be configured in the door object.

Whichever channels are used for Door Switch and Bond Sensor on Entry AC-1 Plus must be wired into the same channels on the Exit AC-1 Plus and these must have the same resistor configuration. Both of these channels on both AC-1 Plus modules are now unavailable to be used as InfinityInputs.

Any Supervised input channels not used in the door object can be created and used as InfinityInputs.
 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 6394
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore