Getting distribution file installation (no core software) error when attempting to commission the JACE-6E.
  • Getting distribution file installation (no core software) error when attempting to commission the JACE-6E.
‎2018-09-11 08:41 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM
Getting distribution file installation (no core software) error when attempting to commission the JACE-6E.  The error states "No core software was found that can be installed to the remote host."
I/A Series G3, JACE-6E, TRD-J-600E
  1. Attempting to install an I/A Series G3 version that is not compatible with the JACE-6E platform (e.g. versions below 3.6.47).
  2. Workbench not set up to be an installation tool (required distribution files are not available within the Workbench environment).
  • The TRD-J-600E is compatible with I/A Series G3 version 3.6.47.1 or later. The I/A Series ENS with Workbench files are available for download from The Exchange Download Center.
  • Re-install the I/A Series G3 software and enable the checkbox that configures Workbench to be an installation tool. The checkbox indicates "This instance of TAC I/A Series Enterprise Network Server will be used as an installation tool." The distribution files related to each of the platforms will be installed on the computer.