How can I change the "State" of a "Unconfigured" LON controller using WorkPlace Tech so that it can be downloaded?
  • How can I change the "State" of a "Unconfigured" LON controller using WorkPlace Tech so that it can be downloaded?
  • sesa116868
    sesa116868
‎2018-09-06 11:13 AM
Cannot download LON controller that is in the "Unconfigured" state.
I/A Series MNL series controllers
Controller was placed in the "Unconfigured" state by accidentally holding the service pin button too long.
1a.  If running the WorkPlace Tech Tool software under Microsoft Visio 2007 or earlier, select the "Configure LON Device" function under the Tools menu.  Continue with step 2, below.
1b.  If running the WorkPlace Tech Tool software under Microsoft Visio 2010, select "Configure" under the "Device" selection on the WorkPlace Tech Ribbon Bar.
2.  The "Configure Device" window will be displayed.  Use any of the standard methods; enter Neuron ID, Browse for device or Listen for Service Pin, to select the device.
3.  Click the [OK] button to reconfigure the device.
4.  A WorkPlace Tech status window will be displayed, normally displaying "Successfully configured the device.".  Click [OK] to close the window.
The device is now in the configured mode and can be downloaded.
  • TAC IA Series
  • 10893