Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Shield grounding details for the B-LINK-AC BACnet MS/TP repeater.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Shield grounding details for the B-LINK-AC BACnet MS/TP repeater.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2265 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Shield grounding details for the B-LINK-AC BACnet MS/TP repeater.

Picard Product_Support
‎2018-09-06 11:11 AM

Issue

Communication issues caused by improper grounding of the BACnet MS/TP shield connections to the B-LINK-AC repeater.

 

Environment

BACnet MS/TP installation with B-LINK-AC repeaters.

Cause

The shield connection on port 1, labeled "(Input)", of the B-LINK-AC repeater is internally wired differently than the four other ports.

Resolution

Due to the differences in how the shield terminals are wired, the following techniques must be followed when wiring the B-LINK-AC BACnet MS/TP repeater.

  1. Port 1, marked (Input), must have its MS/TP bus shield connected to the SHLD terminal, which is isolated from Earth Ground. The incoming MS/TP shield must be grounded at only one point, at a location other than the repeater. Typically this is at the opposite end of the bus, or where the MNB-1000, UNC, ENC or other BACnet parent controller resides.
  2. All four of the other repeater ports, # 2 - 5, have their SHLD terminals tied together, and tied to Earth Ground internally, through the power supply's Earth Ground connection. For each MS/TP bus cable connected these ports, the single point of ground for the shield is at the repeater and, therefore, the shield must not be grounded at any other point on the bus.

None of the five MS/TP ports on the repeater have internal termination resistors.  If a MS/TP trunk ends at the repeater, a 120 ohm terminating resistor must be connected between the MSTP+ and MSTP- terminals on that port of the repeater.  Likewise, the far end of each MS/TP trunk must also be terminated with a 120 ohm resistor between the MSTP+ and MSTP- terminals of that last controller.

None of the five MS/TP ports on the repeater have internal bias resistors.  Standard practices, regarding the biasing of the MS/TP trunks, should be applied, as described in the I/A Series MicroNet BACnet Best Practices Guide, F-27360.

Additional information on the use of these repeaters can be found in the "Approved MS/TP Repeaters" section of Chapter 5 of the I/A Series MicroNet BACnet Smoke Control Systems manual, F-27419.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 10992
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore