Issue
The Platform Software Manager shows that the History module is installed in the ENC, but a HistoryPointList object cannot be added to the ENC.
The error message “drop failed: java.baja error” is displayed in the Program Director window.
Environment
Niagara G3 all version, ENC-410, ENC-520
Cause
The HistoryPointList object requires that the ENC’s Module Content Filter be set to ui+runtime.
Resolution
Set the ENC’s Module Content Filter Level to ui+runtime.
1. Open the ENC’s Platform and click on Set Module Filter
2. Select ui+runtime and then click on Finish.
The HistoryPointList object can now be added to the ENC.