Cannot add the HistoryPointList object to an ENC Niagara G3 station.
  • Cannot add the HistoryPointList object to an ENC Niagara G3 station.
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 11:05 AM
 The Platform Software Manager shows that the History module is installed in the ENC, but a HistoryPointList object cannot be added to the ENC.
 The error message “drop failed: java.baja error” is displayed in the Program Director window.
Niagara G3 all version, ENC-410, ENC-520
The HistoryPointList object requires that the ENC’s Module Content Filter be set to  ui+runtime.
Set the ENC’s Module Content Filter Level to ui+runtime.
1. Open the ENC’s Platform and click on Set Module Filter
2. Select ui+runtime and then click on Finish.
The HistoryPointList object can now be added to the ENC.