Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 65
    • 66
    • 67
    • …
    • 508
  • Next »

PSI / XPSI Revision 4.0 will not tunnel, nor will it connect via modem.

Issue PSI / XPSI Revision 4.0 will not tunnel, nor will it connect via modem. Product Line TAC IA Series Environment PSI / XPSI Revision 4.0 Cause Not supported in this release. Resolution Upgrade to PSI / XPSI Revision 4.1, which the file PSIv4.10.zip is available for download on The Exchange Download Center. Click here to see the Release Notes included in the zip file.
View full article
Picard Product_Support
‎2018-09-07 02:28 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 11:04 PM

Labels:
  • TAC IA Series
1530 Views

Commissioning an EM4300

Issue Having issues integrating an EM4300 Zigbee power meter with an MPM Product Line EcoStruxure Building Expert Environment Multi Purpose Manager (MPM) EM4300 Cause Procedure only available in Building Expert Guide Resolution In order to establish communication with the EM4300 Zigbee power meter, the following procedure must be followed: 1. Login to Building Expert. 2. In Explorer tab, click Add Devices. A new window opens. 3. Select EM4300. 4. Click the Add Devices button. Building Expert automatically adds an EM4300 Device to your project. 5. In the Explorer tab select the ZigBee Configuration (ZBC1) object. 6. Click on Edit Settings and check the Treat Extended Network ID as a Hexadecimal box. Note: Validation of the Extended Network ID field changes based on this checkbox. For the EM4300, the Extended Network ID is a 16 digit hexadecimal string, where the last 8 characters must be precisely 04015E10 and the first 8 characters are user-defined. Note that the first 8 characters must be unique from one ZigBee network to the other if using multiple MPMs configured as ZigBee Coordinators in the same deployment or building. Note: The “Treat Extended Network ID as Hexadecimal” box must be checked. Note: Ensure the Stack Profile used is ZigBee Pro and the selected Security Profile is Home Automation. 7. In the Devices pane, select the EM4300. 8. Click on the ZigBee EM4300 Configuration (ZEM1) object. 9. Click the Bind button. 10. Once the device appears in the dialog window, select it and click on the Bind Device button 11. The table now displays the binding information of the device. 12. Select the required points and click Save. Note: Selecting a point automatically checks the COV checkbox. The COV boxed are non-editable. Commissining multiple EM4300 devices: When integrating multiple EM4300s and if you notice that the EM4300 device has joined the wrong network, you have the ability to remove it and make it join the correct one. Follow the procedure below. 1. In the Explorer tab Select the ZigBee Discovery (ZBD1) object. 2. Click the Scan button to find devices. 3. The table below will list all the discovered ZigBee devices, specifying whether or not they are bound.
View full article
Picard Product_Support
‎2018-09-10 10:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:51 PM

Labels:
  • EcoStruxure Building Expert
1307 Views

Error: LNS #25 lcaErrDatabase "Database error. (Subsystem: LNS, #25)[DB#-2506]"

Issue "Database error. (Subsystem: LNS, #25)[DB#-2506]" After clicking OK there may be another error: "The global database is not open. (Subsystem: LNS, #64)". When the Echelon LonMaker Design Manager opened, there is nothing in the Database Name field. Product Line TAC Vista Environment LonMaker Vista LNS Cause This error can occur when ports that the LNS Database is trying to use are already being used by other applications. The ports in question are 6001 and 6002. Resolution To check which application is using these ports, use the following DOS command: netstat -bn Once you know which application is using ports 6001 and 6002, shut that application down and relaunch LonMaker or your LNS-based application. For further information refer to Echelon Support article kb481
View full article
Picard Product_Support
‎2018-09-07 03:42 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:47 PM

Labels:
  • TAC Vista
1589 Views

Using Schneider Electric actuators with competitors' globe valves

Issue Using Schneider Electric actuators with competitors' globe valves Product Line Field Devices Environment Schneider Electric actuators (Americas field devices) 3rd party globe valves Cause To replace 3rd party / competitor valve actuators with Schneider Electric valve actuators, a linkage / adapter may be required to install the Schneider Electric actuator onto the 3rd party / competitor valve.  Resolution Refer to the AV-800 Series Competitive Globe Valve Adapters Selection Guide for a list of adapter kits, recommended Schneider Electric actuators and supported 3rd party / competitors' globe valves (Johnson Controls, Siemens, Honeywell).  The Selection Guide can also be downloaded from the Publication Zone with iPortal. If you do not have access to the iPortal, use the guest access credentials. Once you have logged on, go to 'Links' > 'Publication Zone'.  Installation instructions showing assembly drawings can be downloaded here.
View full article
Picard Product_Support
‎2018-09-06 02:49 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:36 PM

Labels:
  • Field Devices
2323 Views

Editing the sample Personnel Import Utility (PIU) XSL files.

Issue Proper way to 'activate' portions of Personnel Import Utility (PIU) XSL files. Product Line Andover Continuum Environment CyberStation with PIU Cause Difficulty in getting transformation file to import records Resolution Transformation files used with the PIU are located in the \Continuum directory. These are XSL files and are built in a way that features are commented out in the file and those features can be 'activated' by uncommenting. XSL is a language for expressing style sheets. An XSL style sheet is a file that describes how to display an XML document of a given type. When the XSL files are opened with Internet Explorer (IE) you see color-coding and bold text. The bold text is activated, the light grey is not. You can only view the code in IE, not edit it. Use an advanced text editor like Notepad ++ (https://notepad-plus-plus.org/) and you can easily see and edit the file to activate portions of it. Note: Make sure when 'activating" the syntax option in the file by removing the leading  - <!--   you also remove the trailing   --> .  The following is what the file CSVToContinuumTransformation.xsl looks like.   <?xml version="1.0"?> <xsl:stylesheet version="1.0" xmlns:xsl="http://www.w3.org/1999/XSL/Transform" xmlns:msxsl="urn:schemas-microsoft-com:xslt" xmlns:TAC="http://www.tac.com/TAC" extension-element-prefixes="msxsl" exclude-result-prefixes="TAC"> <!-- - define the Javascript or C# or VBScript functions that you want to include within a msxsl:script element. - language indicates the scripting language - implements-prefix gives the namespace prefix that you declared for your function (i.e. TAC) - Use the functions where ever you want. For example <alias> <xsl:value-of select="TAC:today()" /> </alias> --> <msxsl:script language="C#" implements-prefix="TAC"> <!-- it's often helpful to use a CDATA section so you don't have to worry about escaping less-than signs or anything --> <![CDATA[ public string today() { return "abcdefs"; } ]]> </msxsl:script> <!-- <xsl:stylesheet version="1.0" xmlns:xsl="http://www.w3.org/1999/XSL/Transform"> <xsl:output method="xml" indent="yes"/>--> <xsl:template match="SourceUsers"> <SourceUsers> <xsl:apply-templates select="SourceUser"/> </SourceUsers> </xsl:template> <!-- Need to include only the mapped personnel attributes or if every thing everything is added remove the ones that are included below in XSLT tags--> <xsl:template match="SourceUser"> <!-- You can declare variables, parameters --> <xsl:param name="allPhoneNumbers" select="HomePhone"/> <xsl:copy> <xsl:copy-of select="ADA|Address|AllowEntEntEgr|Blood|CardNumber|CardType|City|Country|DateOfBirth|DefaultClearanceLevel| Department|DepartmentCode|EmergencyContact|EmergencyPhone|EmpNumber|ExecutivePrivilege|ExpirationDate|EyeColor| FirstName|HairColor|Height|HomePhone|Info1|Info2|Info3|Info4|Info5|Info6|JobTitle|LastName|LicenseNumber| LostCard|MiddleName|NonABACardNumber|OfficeLocation|ParkingSticker|PIN|SecurityLevel|Sex|SiteCode| SocSecNo|StateOfResidence|StartDate|Supervisor|VehicleInfo|Visitor|Weight|WorkPhone|Zip|FipsAgencyCode|FipsOrgId| FipsSystemCode|FipsCredentialNumber|FipsCredentialSeries|FipsOrgId|FipsCredentialIssue|FipsOrgCategory|FipsPersonId| FipsPersonOrgAssociation|FipsPivState|FipsPivControlled|FipsExpirationDate|PhotoFile|Signature|ResponseTransaction|State|FipsHmac"/> <!--<Adding OwnerFolder to personnel object. This is must other wise it won't create or update any objects>--> <OwnerFolder>Root\CardHolders</OwnerFolder> <!--<Adding OwnerFolder to personnel object end>--> <!--<Alias is necessary to create or update object and it should be unique in the system>--> <Alias> <!-- By default, we'll use the employeeNumber + samaccountname as an alias (16 chars max). --> <!-- On newer systems, the logon name is userPrincipalName --> <!-- One Way --> <!-- <xsl:value-of select="concat(samaccountname,EmpNumber)"/> --> <!--<xsl:value-of select="concat(FirstName,LastName)"/>--> <!--In IDMS system Serial Number is a unique number. Use this as Alias added to a Character or a group of characters to generate a valid alias. See the Example --> <xsl:value-of select="concat(FirstName,LastName)"/> <!--<xsl:choose> <xsl:when test="string-length(EmpNumber)=0"> <xsl:value-of select="samaccountname"/> </xsl:when> <xsl:otherwise> <xsl:value-of select="concat(LastName,EmpNumber)"/> </xsl:otherwise> </xsl:choose> --> <!-- Other Ways --> <!-- This option combines the last name and EmpNumber --> <!--<xsl:value-of select="concat(substring(LastName,1,12),substring(EmpNumber,2,5))"/>--> <!-- This option combines the EmpNumber last and first name from CyberStation --> <!--<xsl:value-of select="concat(EmpNumber,FirstName,LastName)"/> --> <!-- This option combines the last name and FirstName --> <!--<xsl:value-of select="concat(LastName, FirstName)"/>--> </Alias> <!-- Example of using User defined functions --> <!-- <alias> <xsl:value-of select="TAC:today()" /> </alias>--> <!--<Adding departmentcode DepartmentCode to personnel object if it contains only numbers>--> <!--<<xsl:value-of select="number(department)"/>--> <!-- <DepartmentCode><xsl:number value="Department" /></DepartmentCode> --> <!--<Adding CardType>--> <!--<CardType>AC4plus432</CardType>--> <!--<Adding SiteCode>--> <!--<SiteCode>15</SiteCode>--> <!--<Adding Signature, PhotoFile, FingerPrint use firstname.jpg or Lastname.jpg or Firstname+LastName.jpg. Use the combination depending upon the jpg files stored on the hard drive. A few examples below >--> <!--<Adding Signature>--> <!--<Signature>D:\picsForSri\signatures\LISASIG.BMP</Signature>--> <!--<Signature> <xsl:value-of select="concat('D:\',FirstName,'.jpg')"/> </Signature>--> <!--<Signature> <xsl:value-of select="concat('c:\',Lastname,'.jpg')"/> </Signature>--> <!--<Adding FingerPrint>--> <!--<FingerPrint>D:\picsForSri\Fingerprints\Finger.jpg</FingerPrint>--> <!--<Adding photofile>--> <!--<PhotoFile>D:\picsForSri\pics\Elmer1.jpg</PhotoFile>--> <!--Assigning default areas to the imported personnel--> <!-- To implement Area Links, uncomment the section below before the <AreaLinks> tag and after the </AreaLinks> tag--> <!-- To add more areas, copy the <AreaLink></AreaLink> tags and everything between them and paste after the first </AreaLink> tag--> <!-- State can be Enabled or Disabled, Preload is Workstation Only and can be True or False, AreaId example - Root\MyPersonnelFolder. --> <!-- This is line 1 of 2 to remove to implement Area Links <AreaLinks> <AreaLink> <AreaId><![CDATA[Full Path To Area Here]]></AreaId> <SchedId>Full Path To Schedule Here</SchedId> <State>Enabled</State> <Preload>False</Preload> <ClearanceLevel>0</ClearanceLevel> </AreaLink> </AreaLinks> This is line 2 of 2 to implement Area Links --> <!--<Adding Templates to personnel object>--> <!--<Adding Templates to personnel object with Department name>--> <!--<RefTemplate> <xsl:value-of select="concat('Root\Templates\Personnel Templates\', Department)"/> </RefTemplate>--> <!--<Adding Templates to personnel object based on department>--> <!--<Can do the same way with departmentCode DepartmentCode>--> <!--<xsl:value-of select=AreaTemplate1000/> same as <xsl:text>AreaTemplate1000</xsl:text>--> <!--<RefTemplate> <xsl:choose> <xsl:when test="StateOfResidence='MA'"> <xsl:text>Root\Templates\Personnel Templates\AllAccess</xsl:text> </xsl:when> <xsl:when test="StateOfResidence='NY'"> <xsl:text>Root\Templates\Personnel Templates\PowerUser</xsl:text> </xsl:when> <xsl:otherwise> <xsl:text>Root\Templates\Personnel Templates\StandardUser</xsl:text> </xsl:otherwise> </xsl:choose> </RefTemplate>--> <!--<Adding one personnel Template to personnel object >--> <!--<RefTemplate> Root\Templates\Personnel Templates\PT1</RefTemplate>--> <!--Template> <xsl:choose> <xsl:when test="StateOfResidence='MA'"> <xsl:text>Root\Templates\Personnel Templates\All Access</xsl:text> </xsl:when> <xsl:when test="StateOfResidence='PA'"> <xsl:text>Root\Templates\Personnel Templates\Power User</xsl:text> </xsl:when> <xsl:when test="StateOfResidence='NY'"> <xsl:text>Root\Templates\Personnel Templates\Standard User</xsl:text> </xsl:when> </xsl:choose> </RefTemplate>--> <!--<Adding one personnel Template to personnel object >--> <RefTemplate>Root\Templates\Personnel Templates\Standard User</RefTemplate>--> <!-- Manipulate states--> <!-- If the attribute is using here don't add it at the <xsl:copy-of select--> <!-- <StateOfResidence> <xsl:choose> <xsl:when test="StateOfResidence='Massachusetts'"> <xsl:text>MA</xsl:text> </xsl:when> <xsl:when test="StateOfResidence='New Hampshire'"> <xsl:text>NH</xsl:text> </xsl:when> <xsl:when test="StateOfResidence='Washington DC'"> <xsl:text>DC</xsl:text> </xsl:when> <xsl:when test="StateOfResidence='Connecticut'"> <xsl:text>CT</xsl:text> </xsl:when> <xsl:otherwise> <xsl:value-of select="StateOfResidence"/> </xsl:otherwise> </xsl:choose> </StateOfResidence>--> <!-- Manipulate phone numbers--> <!--</telephonenumberFormat>--> <!-- <WorkPhone> <xsl:choose> <xsl:when test="contains(WorkPhone,'-')"> <xsl:value-of select="WorkPhone"/> </xsl:when> <xsl:when test="string-length(WorkPhone)=0"> <xsl:value-of select="WorkPhone"/> </xsl:when> <xsl:otherwise> <xsl:value-of select="concat(substring(WorkPhone,1,3),'-',substring(WorkPhone,4,3),'-',substring(WorkPhone,7,4))"/> </xsl:otherwise> </xsl:choose> </WorkPhone> --> <!--Replacing the linefeed in the adress --> <!-- Unicode of linefeed &#xA; (is line break \n), Unicode of tab &#x9;--> <!-- <xsl:value-of select="translate(Address, '\n', ' ')"/> Won't work --> <!-- <Address> <xsl:value-of select="translate(Address, '&#xA;', ' ')"/> </Address> --> <!--************************************************************** --> <!--These are the examples of how to parse Multi valued Active Directory attributes after mapping them to Continuum attributes --> <!-- Use Continuum attributes names instead of these dummy attribute names, variables names can be at as your wish --> <!-- This example takes the first element from the list, it shows the use of a variable --> <!--<HomePhone> <xsl:variable name="phoneNumbers" select='HomePhone'/> <xsl:value-of select="substring-before($phoneNumbers, ',')"/> </HomePhone>--> <!-- This example takes the second element from the list. --> <!-- It uses a param at the top of the file. after the line <xsl:template match="SourceUser">--> <!--Or use a local variable between phone2 tags<xsl:variable name="allPhoneNumbers" select='HomePhone'/>--> <!-- <Phone2> <xsl:variable name="after-first-comma" select='substring-after($allPhoneNumbers,",")'/> <xsl:variable name="second-comma" select='substring-before($after-first-comma,",")'/> <xsl:value-of select="$second-comma"/> </Phone2> --> <!-- This example outputs a xml tag if the element exists in the list --> <!-- <memberOf> <xsl:variable name="memberGroups" select="memberOf"/> <xsl:if test="contains($memberGroups, 'Engineering')"> Engineering Lab1 </xsl:if> </memberOf> --> <!--************************************************************** --> </xsl:copy> </xsl:template> </xsl:stylesheet>
View full article
Picard Product_Support
‎2018-09-06 02:48 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:34 PM

Labels:
  • Andover Continuum
1319 Views

Device Template for trane Uc800

Issue Device Template for trane Uc800 Product Line TAC Vista Environment Xbuilder Xenta Server MODBUS Cause Device Template Required Resolution Here is a MODBUS device Template for a TRANE UC800
View full article
Picard Product_Support
‎2018-09-10 11:45 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:26 PM

Labels:
  • TAC INET
  • TAC Vista
1501 Views

How can a new computer purchased with Microsoft® Windows Server 2008 or Windows Server 2008 R2 be legally downgraded to an earlier Server class operating system?

Issue Microsoft no longer allows OEM computer manufacturers to install Microsoft® Windows Server 2003 or Microsoft® Windows Server 2003 on OEM computers.  Is there a valid legal and legitimate workaround for running software products that are not compatible with Microsoft® Windows Server 2008? Product Line TAC IA Series Environment New server class computer that was purchased pre-loaded with Microsoft® Windows Server 2008 or Microsoft® Windows Server 2008 R2 I/A Series software that runs only on Microsoft® Windows Server 2003 such as: I/A Series (Niagara) R2 - all releases I/A Series (Niagara) G3 - all releases prior to 3.6.x Cause Microsoft® Windows Server 2003 is no longer available on new computers. Resolution Downgrade the Microsoft® Windows Server 2008 to Microsoft® Windows Server 2003 According to the Windows Server License supplied with all versions of Microsoft® Windows Server 2008 (including R2), the license grants the customer the right to run an earlier level or edition of Windows Server.  Microsoft permits this downgrade because many customers need to continue using old versions of Windows Server for compatibility reasons. More information is available in this Microsoft document.
View full article
Picard Product_Support
‎2018-09-10 06:30 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:10 PM

Labels:
  • TAC IA Series
1178 Views

Using a 4-20 mA CO2 sensor with a Xenta 102-AX in StruxureWare

Issue Configuring the Xenta 102-AX to accept a 4-20 mA CO2 sensor input on Universal Input 3.  A negative value is required on the CO2 offset value, but it is not possible to edit the scaling of the input in StruxureWare. Product Line EcoStruxure Building Operation Environment Xenta 102-AX 4-20 mA output CO2 sensor SmartStruxure Cause The Xenta 102-AX universal inputs are designed to work with a 0-5V input.  The best option is to always buy a CO2 sensor that is compatible.  However, if 4-20 mA CO2 sensors have already been purchased and installed, they can be made to work. Resolution In this example, a 4-20 mA CO2 sensor with a 0-2000 ppm range is assumed. In the Xenta 102-AX Plug-In > Hardware Configuration Tab, set Input 3 Selection to None Wire the CO2 sensor and a 250Ω resistor across U3 and M.  This converts the 4-20 mA signal to 1-5V. In SBO WorkStation, create a Function Block program to convert the 0 to 100 % signal to ppm.  (You can import the Function Block program here). Edit Bindings on the CO2 Curve program and bind the nvoUnvInput3/Value.lev_percent from the UnivIn3Sense folder of the 102-AX to the CO2_RAW of the CO2 Curve program. Bind the CO2 from the CO2 Curve program to nviCO2/Value.ppm that is in the UnivIn3Sense folder of the 102-AX. At this point, if you have values entered in for the Airflow Reset or CO2 Low Limit and CO2 High Limit then the Airflow reset will be active and operational. Also, if you have multiple CO2 sensors on multiple 102-AXs then you don't have to have a CO2 Curve Function Block program for each one.  You can just edit the existing CO2 Curve program and copy/paste the exiting Function Block program multiple times in the same Function Block program.  You would just need to rename each public point with a unique name.  Note: An input of 0V (a sensor that has not been wired yet) will result in an nvoCO2sensor value of 65535 (invalid).
View full article
Picard Product_Support
‎2018-09-10 09:50 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:01 PM

Labels:
  • EcoStruxure Building Operation
1565 Views

How do I automatically backup the entire TAC I/NET Seven SQL database.

Issue When only the MSDE version of I/NET Seven is installed there is no way to automatically backup the entire SQL Database at scheduled intervals. Product Line TAC INET Environment TAC I/NET Seven running on Windows XP using Microsoft MSDE SQL Server. Cause When only the MSDE version of I/NET Seven is installed there is no way to automatically backup the entire SQL Database at scheduled intervals. Resolution A batch file BackupInetDb.bat has been developed to allow users to create a Scheduled Task within Windows which launches the batch file with the appropriate command line switches. Click here to download the zip file which contains the BackupInetDb.bat and instructions on how to configure an automated backup.
View full article
Picard Product_Support
‎2018-09-07 03:35 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:50 PM

Labels:
  • TAC INET
1411 Views

Save failed in TAC Graphics Editor

Issue Error message generated when saving a graphic page as a Vista Object. Save Failed. Link contains invalid Vista characters. " ! # % & \ ' ( ) * + , - ; < = > ? and leading/trailing period is not accepted. There is also a limit of 40 chars between each period. Product Line TAC Vista Environment TAC TGML Graphics Editor Vista Workstation Cause A graphic page link or binding has invalid characters or contains more than 40 characters between each period. This error may occur when converting graphic pages from OGC to TGML. Resolution Open graphic page in TAC Graphics Editor. Click on the Links tab at the bottom of the page. In the Links pane there is a list of all links associated with the graphic page. Double click on a link that contains an invalid character (seen above in the error message) or more than 40 characters between periods. (All invalid links must be corrected before the graphic page can be saved) On the right side of the screen in the Properties pane, the name and address of the link can be found here. Remove the invalid characters from both fields. Perform a Save as Vista Object.
View full article
Picard Product_Support
‎2018-09-10 05:07 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:48 PM

Labels:
  • TAC Vista
1339 Views

In an I/A Series G3 station, is there a way to relocate a history from one parent history container to another without losing history data?

Issue In an I/A Series G3 station, is there a way to relocate a history from one parent history container to another without losing history data? In addition, can the associated history ID be modified to allow new data to log and append into the relocated history? Product Line TAC IA Series Environment I/A Series G3 (Niagara) station Cause Sometimes a user will want to move a history to a different folder. Resolution See the procedure illustrated with screen captures.
View full article
Picard Product_Support
‎2018-09-10 06:33 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:41 PM

Labels:
  • TAC IA Series
1439 Views

STR800 Series Wall Module wiring details

Issue Not generally available Product Line Field Devices Environment I/A series Field device Cause Information not provided with the documentation supplied. Resolution The STR800 Series User manual can be downloaded by selecting this link. The STR800 Temperature Sensor RoHS Certificate can be downloaded by selecting this link. The STR800 Wall Module Specification Sheet can be downloaded by selecting this link. Other STR800 documentation is available on the Schneider Download Center.
View full article
Picard Product_Support
‎2018-09-10 12:51 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:39 PM

Labels:
  • Field Devices
  • TAC IA Series
1510 Views

Lua script to convert a thermistor used on a analogue input on a SEC-TE to a temperature reading

Issue Lua script to convert a thermistor input on a SEC-TE to a temperature reading Product Line EcoStruxure Building Expert Environment SEC-TE MPM Cause When a temperature sensor is wired to a SEC-TE Smart Terminal controller, it can only be displayed as ohms. There is no option to use an AIC (Analogue Input Configuration) object to convert the reading. Resolution A Lua script is required to convert the input to a temperature value. 1. Import the Lua script At the top of the script in Section 1: 2. Edit the ME.AV17 input to the input used. 3. Edit the ME.AV48 to the Analogue Variable used to display the value. At the bottom of the script in Section 3: 3. Edit the AIC number to the AIC used to convert the value. Download here the Import File Download here the Txt File
View full article
Picard Product_Support
‎2018-09-07 02:18 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:25 PM

Labels:
  • EcoStruxure Building Expert
1754 Views

[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Powerlogic PM800 Power Meter

Issue Integration to the Powerlogic PM800 power meter with the Xenta 500 \ Xenta 700 \ Xenta 900 and Modbus RTU Product Line TAC Vista Environment Xenta 511, 527, 701, 711, 721 (5.1.5 up) Xenta 731, 913 (all versions) XBuilder Powerlogic PM800 Power Meter Cause Disclaimer: This device template is intended to provide a starting point for an integrator, and is in no way written to be the mandatory points list for your integration effort. Product Support Services-Dallas has written this device template in an effort to give our customers a starting point and solid example of how to develop a device template for the above product. The integrator will be responsible for any additions or modifications to this device template. Please report any problems to PSS Dallas at product.support@buildings.schneider-electric.com Resolution Please us the following .dev file as a starting point and a guide to the integration. This .dev file contains a set list of registers that PSS assumed would be seen as critical and important to the integration process. If any other data is needed please see this supported document to make the necessary changes.     To use these files in Xbuilder please follow these steps: Extract the .dev file from the .zip file in the link above, and place it on your harddrive. In Xbuilder, right click on the Modbus Master device and chose Add Device Browse to the needed .dev file and choose Open. Rename the newly added device to a unique name within the Modbus Master network.
View full article
Picard Product_Support
‎2018-09-07 03:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:22 PM

Labels:
  • TAC Vista
4471 Views

Replacement of Satchwell CZU Mk 2 Zonemaster Controller by S-E Satchwell CZU Mk 4 Zonemaster Controller due to obsolescence.

Issue Satchwell CZU Mk2 Zonemaster Controller requires replacement. Product Line Field Devices Environment Stand alone Fan Coil Unit Temperature Controller. Satchwell CZU Mk 2 Zonemaster Controller. CZU 2201 CZU 2202 CZU 2203 Cause Obsolescence of Satchwell CZU Mk 2 Zonemaster Controller. Resolution Replacement of Satchwell CZU Mk 2 Zonemaster Controller with S-E Satchwell CZU Mk 4 Zonemaster Controller. The CZU 4201 may be used to replace the following CZU Mk 2 Controllers :- CZU 2201, CZU 2202, CZU 2203 N. B. CZU 2201 Controllers provided an additional -9 to +9 V d.c. output enabling connection to peripherals such as the Satchwell NSU 1401 Night Set-back Override Unit, TSU 1402 Two Step Auxiliary Unit and SSU 1403 Signal Selector Unit. CZU 2202 and CZU 2203 Controllers provided an additional -0.5 to +9 or -9 to +0.5 V d.c. output enabling connection to the Satchwell NSU 1401 Night Set-back Override Unit.  Additional outputs are not provided on the CZU 4201 Controller and in those applications where these are required then it will be necessary to consider an alternative Controller to the CZU 4201. Details of the CZU 4201 may be viewed here. A remote Satchwell Adjustable Room Temperature Sensor such as the DRT 3451, or a remote Satchwell Duct Temperature Sensor from the DDU range of Sensors may have been installed and connected to the Controller. Any existing remote Satchwell Temperature Sensors may be retained for connection to the CZU 4201. Should the remote Satchwell Adjustable Room Temperature Sensor require replacement then this may be replaced by an S E STR 612 Adjustable Room Temperature Sensor. Details of the STR 612 may be viewed here. Should the remote Satchwell Duct Temperature Sensor require replacement then this may be replaced by an S E STD 670 Duct Temperature Sensor. Details of the STD 670 may be viewed here
View full article
Picard Product_Support
‎2018-09-10 03:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:19 PM

Labels:
  • Field Devices
2522 Views

Replacement of Satchwell CD2401 Proportional Controller-Actuator by Schneider Electric Satchwell CZT Proportional Controller due to obsolescence.

Issue Satchwell CD2401 Proportional Controller-Actuator requires replacement. Product Line Field Devices Environment Stand alone discreet Satchwell CD2401 Proportional Controller-Actuator Cause Obsolescence of Satchwell CD2401 Proportional Controller-Actuator Resolution Replace Satchwell CD2401 Proportional Controller-Actuator with Schneider Electric Satchwell CZT5305 Proportional Controller, compatible Temperature Sensor and MD Series Actuator and Linkage Kit. Replace Satchwell CD2401 Proportional Controller-Actuator with Schneider Electric Satchwell CZT5305 Proportional Controller. Details of the Schneider Electric Satchwell CZT 5305 Proportional Controller may be viewed here. Replacement of Temperature Sensor It should be noted that although the existing Satchwell Temperature Sensor associated with the CD2401 Proportional Controller–Actuator is obsolete, it is compatible with the CZT Proportional Controller and may be retained. Should it be decide to install a replacement Temperature Sensor however, then the following may be considered. Room Temperature Sensor STR600 series details of which appear here. Duct Temperature Sensor STD660 details of which appear here. Immersion Temperature Sensor STP660 details of which appear here. NB In order to utilize the existing Pocket a Pocket Adaptor DWA0001 will also be required. Pocket Adaptor DWA0001 details of which appear here. OR Surface mounting Temperature Sensor STC600 details of which appearhere. Replacement of Actuator. Whilst the existing Satchwell MB Valve Body may also be retained, a new Schneider Electric Actuator and Linkage Kit will need to be installed on the MB Valve Body in order to permit control from the CZT Proportional Controller. Details of the Schneider Electric MD10A-24 Actuator may be viewed here. Details of the Schneider Electric LMD/AR-MB Linkage Kit may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 12:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:17 PM

Labels:
  • Field Devices
2896 Views

MPM-UN Modbus connection polarity

Issue The modbus RS485 connectors on the MPM-UN are marked MOD A & B, the documentation does not state the polarity. Product Line EcoStruxure Building Expert Environment MPM-UN Modbus Cause Documentation does not state the polarity of the Modbus connectors. Resolution Connect the Modbus device to the A-B connectors on the MPM. Connect the positive lead to connector A and the negative lead to connector B.
View full article
Picard Product_Support
‎2018-09-11 01:41 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:14 PM

Labels:
  • EcoStruxure Building Expert
1607 Views

When trying to open web pinpoint on a remote client the following error occurs 0x8000401A

Issue When trying to open web pinpoint on a remote client session the users receive the error below: Product Line Andover Continuum Environment MS Server 2008 and newer Windows 7 and newer Continuum 1.9x and 2.x webClient Remote Desktop Cause This issue is caused when a remote desktop connection is made on a Windows 7, Windows 2008 server or newer Operating Systems.  The console becomes locked.  It will stay locked until the local session is restored with a logon. Resolution  Resolution: 1)      Create a Bat file. **************************************************************************************** @echo off REM Restores session 0 to the "console".  Thus allows local machine REM to return to the service accounts desktop without being locked. REM ------------------------------------------------------ tscon.exe 0 /dest:console @%windir%\System32\tscon.exe 0 /dest:console @%windir%\System32\tscon.exe 1 /dest:console @%windir%\System32\tscon.exe 2 /dest:console ***********************************************************************************************   2)      Place this file on the desktop of the Web Server system. 3)      When you disconnect from the remote session run this Bat file. Do not just disconnect. This must be ran “As an Administrator” This will disconnect the session and restore the console.
View full article
Picard Product_Support
‎2018-09-10 09:53 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:10 PM

Labels:
  • Andover Continuum
1443 Views

Unable to load SigXmlExport.dll error

Issue When trying to connect to a Sigma system from SmartStruxure an "Unable to load SigXmlExport.dll" error message is displayed. Product Line EcoStruxure Building Operation, Satchwell Sigma Environment SmartStruxure Enterprise Server version 1.5 Sigma 4.08 Cause The Sigma to StruxureWare Support files have not been installed to the Sigma installation. Resolution Download the Sigma To StruxureWare Building Operation Support Program from the Exchange Download Center. This additional software allows a Sigma Release 4.08 installation to respond to data import requests from SBO 1.5 and takes Release 4.08 to Build 3.46.66 On the existing Sigma 4.08 Sigma server PC, run SigmaSBOSupportSetup.exe and install the software to completion. There is no need to stop Sigma clients or the server.
View full article
Picard Product_Support
‎2018-09-11 03:00 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:07 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
1493 Views

Lua Program for measuring EnOcean Signal Strength

Issue Lua Program for measuring EnOcean Signal Strength Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Cause Requirement to measure and alarm from the EnOcean Signal strength. Resolution Download either the txt file or c2g import file. The file is set to monitor 3 EnOcean devices, either copy the relevant sections to add more devices, or remove to reduce the number of devices. An AV is required for each EnOcean Device. In the Lua program, edit the EnOcean Device ID, this can be found in the "EnOcean Device Configuration" properties. In the Lua program, edit the AVs to those that are to be used. Edit the AV and add the ID in the description and any other description required. How the Lua program works: The Lua script is set to assign each AV an abnormal value (10000) after a time period in (3600) seconds. The EnOcean device will overwrite via the program the value in the AV when a value is received from the device. For an alarm, create an Event, set the high limit (9999) and a time period set to a value beyond that a signal is received from the EnOcean device. Set the low limit to -200. Notes: EnOcean devices send packets at varying times, some at change of state. The timer needs to reflect how often a packet is sent. Several Lua programs may need to be used and the EnOcean devices grouped with similar packet broadcast times. e.g. an infrequently used switch would be different to a temperature sensor.
View full article
Picard Product_Support
‎2018-09-11 07:30 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:03 PM

Labels:
  • EcoStruxure Building Expert
1595 Views
  • « Previous
    • 1
    • …
    • 65
    • 66
    • 67
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of