Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Commissioning an EM4300

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Commissioning an EM4300
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • SaidSawan
    SaidSawan
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1363 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Commissioning an EM4300

Picard Product_Support
‎2018-09-10 10:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 10:51 PM

Issue

Having issues integrating an EM4300 Zigbee power meter with an MPM

Product Line

EcoStruxure Building Expert

Environment

Multi Purpose Manager (MPM)

EM4300

Cause

Procedure only available in Building Expert Guide

Resolution

In order to establish communication with the EM4300 Zigbee power meter, the following procedure must be followed:

1. Login to Building Expert.
2. In Explorer tab, click Add Devices. A new window opens.
3. Select EM4300.
4. Click the Add Devices button. Building Expert automatically adds an EM4300 Device to your project.
5. In the Explorer tab select the ZigBee Configuration (ZBC1) object.
6. Click on Edit Settings and check the Treat Extended Network ID as a Hexadecimal box.

Note: Validation of the Extended Network ID field changes based on this checkbox.

For the EM4300, the Extended Network ID is a 16 digit hexadecimal string, where the last 8 characters must be precisely 04015E10 and the first 8 characters are user-defined. Note that the first 8 characters must be unique from one ZigBee network to the other if using multiple MPMs configured as ZigBee Coordinators in the same deployment or building.

Note: The “Treat Extended Network ID as Hexadecimal” box must be checked.

1.png

Note: Ensure the Stack Profile used is ZigBee Pro and the selected Security Profile is Home Automation.

7. In the Devices pane, select the EM4300.
8. Click on the ZigBee EM4300 Configuration (ZEM1) object.
9. Click the Bind button.
10. Once the device appears in the dialog window, select it and click on the Bind Device button

2.png

11. The table now displays the binding information of the device.
12. Select the required points and click Save.

3.png

Note: Selecting a point automatically checks the COV checkbox. The COV boxed are non-editable.

Commissining multiple EM4300 devices:

When integrating multiple EM4300s and if you notice that the EM4300 device has joined the wrong network, you have the ability to remove it and make it join the correct one.
Follow the procedure below.


1. In the Explorer tab Select the ZigBee Discovery (ZBD1) object.
2. Click the Scan button to find devices.
3. The table below will list all the discovered ZigBee devices, specifying whether or not they are bound.

4.png

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (1)
  • Find more articles tagged with:
  • 18815
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore