Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Lua Program for measuring EnOcean Signal Strength

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Lua Program for measuring EnOcean Signal Strength
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1664 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Lua Program for measuring EnOcean Signal Strength

Picard Product_Support
‎2018-09-11 07:30 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:03 PM

Issue

Lua Program for measuring EnOcean Signal Strength

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite

Cause

Requirement to measure and alarm from the EnOcean Signal strength.

Resolution

Download either the txt file or c2g import file.

The file is set to monitor 3 EnOcean devices, either copy the relevant sections to add more devices, or remove to reduce the number of devices.

An AV is required for each EnOcean Device.

In the Lua program, edit the EnOcean Device ID, this can be found in the "EnOcean Device Configuration" properties.

In the Lua program, edit the AVs to those that are to be used.

Edit the AV and add the ID in the description and any other description required.

How the Lua program works:

The Lua script is set to assign each AV an abnormal value (10000) after a time period in (3600) seconds. The EnOcean device will overwrite via the program the value in the AV when a value is received from the device.

For an alarm, create an Event, set the high limit (9999) and a time period set to a value beyond that a signal is received from the EnOcean device. Set the low limit to -200.

Notes:

EnOcean devices send packets at varying times, some at change of state. The timer needs to reflect how often a packet is sent. Several Lua programs may need to be used and the EnOcean devices grouped with similar packet broadcast times. e.g. an infrequently used switch would be different to a temperature sensor.

Labels (1)
Labels:
  • EcoStruxure Building Expert
Attachments
EnOcean Signal (PG2).zip
Tags (1)
  • Find more articles tagged with:
  • 16502
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.