Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2209 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 56
    • 57
    • 58
    • …
    • 111
  • Next »
Label: "Andover Continuum" Show all articles

Does the CX 9702 support Infinet controllers?

Issue Does the CX 9702 support Infinet controllers? Environment Continuum Cyberstation CX 9702 Infinet I2xxx Cause Verification of Infinet bus support on CX 9702 Resolution CX 9702 has a node limit of 4 and will support Infinet controllers up to the node count limitation.
View full article
Picard Product_Support
‎2018-09-06 02:11 PM

Labels:
  • Andover Continuum
1138 Views

Output does not assume value set by a PE InfinityProgram.

Issue An InfinityProgram is setting an output point but the point does not change value, the program is enabled and running. Environment CyberStation CX9900 CX9680 ACX57xx All infinet and i2 devices Cause This issue may be caused by a number of reasons: The InfinityOutput object is disabled. The InfinityOutput object is manually overridden. A second program that executes later in the firing order is setting the output object. Resolution Enable the InfinityOutput object. Return the output override switch to the 'Auto' position. Solve the contention between programs.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
1140 Views

What privileges are given to a Personnel object by setting its ExecutivePrivilege flag to true

Issue Can the executive privilege override features such as Door Forced Locked schedule and Threat Level Environment CyberStation CX968x ACX57xx Cause Need to override door force locked schedule for users with executive privilege. Resolution The executive privilege attribute of a personnel object can only be used to override area/door locked down. Note that the executive privilege attribute will be grayed out unless the Cyberstation key has the area lockdown option enabled.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
1147 Views

How to add area(s) to multiple personnel objects in one operation

Issue Adding area(s) to multiple personnel objects in one operation Environment CyberStation Cause Need to add area(s) to multiple personnel objects in one shot Resolution In the Continuum Explorer select the folder that contains the personnel object. In the right pane select the personnel objects you want to add the area(s) to, you can select ‘Edit\Select All’ from the pull down menu or use a combination of the Shift/Ctrl key with the left button mouse click to multi select. Right click on one of the selected Personnel objects and select ‘Add Areas…’ from the context menu. In the ‘Area’ window you can select one or more areas to assign.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
952 Views

Personnel fail to distribute to controller, controller offline error displays in Distribution View, and controller's error log displays 0x00007402 (ACC_TCP_FAIL_CONNECTING_SO...

Issue Personnel fail to distribute to controller, controller offline error displays in Distribution View, and controller's error log displays 0x00007402 (ACC_TCP_FAIL_CONNECTING_SOCKET) error. Environment Cyberstation Netcontroller Netcontroller II CX9702 ACX5720, ACX5740 Cause The 0x00007402 error corresponds to an issue with the TCP stack on the controller indicating the controller has had a problem re-establishing a TCP connection. The "Transport  Type" has been changed from the default UDP to TCP. Resolution Change "Transport Type" back to UDP and re-attempt Personnel download. Open Controller Device object and go to "Network" tab. In "Transport Type" field, change TCP to UDP. Re-attempt Personnel download.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
1312 Views

BACnet Schedule goes into Fault and shows a value of "ConfigurationError" in its Reliability field.

Issue After modifying a BACnet Schedule it goes into Fault with its Reliability field showing "ConfigurationError". Environment Continuum, BACnet Schedule Object Cause When a user logs into Continuum with a User that does not have view rights to the InfinityController object, the schedule object used is the Infinity Schedule instead of the expected BACnet Schedule. The Infinity Schedule uses Active/Inactive for its TimeValue entries instead of the default 1/0 that the BACnet Schedule object uses. When a value is set as Active/Inactive, the Schedule is unable to interpret this value and goes into fault.  Resolution Make sure that any User that needs to modify BACnet Schedules has view rights to the InfinityController object enabled. Remove all TimeValue Entries that are Active/Inactive, replace with valid entries, save Schedule.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
1331 Views

Cyberstation Access Event Views do not show live events but work on other Cyberstations

Issue Cyberstation Access Event Views do not show live events when the same Event Views are displayed properly on other Cyberstations. Product Line Andover Continuum Environment Continuum Cyberstation EventView Cause More than one Network Interface Card (NIC) installed on a Cyberstation PC can result in erratic communications between Continuum Devices. Continuum supports only one NIC to be enabled on each Cyberstation.  Resolution 1. Uninstall or disable all Network Interface Card (NIC) but one. 2. Perform a Teach from the Cyberstation.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
1375 Views

Can not select X Driver option on a bCX controller even though it is X Driver Enabled.

Issue When editing a bCX controller Comm port you can not select X Driver option on a bCX controller even though it is X Driver Enabled. The Drop down box for Comm1 only has Autoset and Printer options. Environment bCX1 Controllers, X Drivers, X-Drivers, XDrivers Cause When the bCX1 was first released as supported by V1.70 Cyberstation it did not support X Drivers.   Resolution Cyberstation V1.70 and above support all bCX1 controllers (bCX1 9640, 4040 & 4000). The bCX1-CR (4040) did not initially support X Drivers, this feature was added in Cyberstation V1.82 and required a minimum firmware in the bCX1-CR (4040) of V4.500047 (see Compatibility Matrix). The bCX1-CR-INF (9640) did not initially support X Drivers, this feature was added in Cyberstation V1.73 and  required a minimum firmware in the bCX1-CR-INF (9640) of V1.1 The bCX1-R (4000) do not support X Drivers in any version.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
1312 Views

How can a PE program determine which side of a dual reader door a valid access took place?

Issue How do I determine whether a Valid Access event took place at the entry or exit side of the door from within a PE program? Environment CyberStation CX9702 CX9900 CX968x ACX57xx ACX7xx IOU Modules AC1, AC1A, AC1Plus Cause Need a way to determine which side of a dual reader door a valid access event has taken place. Resolution Compare the door’s TimeEntered attribute to the TimeExited attribute, if TimeEntered > TimeExited then the event took place at the entry side of the door, otherwise it took place at the exit side. The same technique can be used for Invalid Attempt events using the door’s InvalidEntryTime and InvalidExitTime attributes
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
1076 Views

Unable to get BCX or 99xx controller to dial out through modem.

Issue Cannot get BCX or 99xx to successfully dial out through a phone line modem. Environment BCX4040 BCX9640 CX9600 99xx Cause The BCX was not initializing the modem. The modem was not properly set to negotiate the dial out request.. 99xx wasn't hanging up the last call Resolution The Initialize Modem Upon Reset option must be set to YES under controller Modem Settings on the controllers webpage.  Using a 99xx,  it may be necessary to initialize the modem twice to hang up the modem.
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
953 Views

Error when upreving a Controller to a new flash version: "This Uprev file does not match this type of controller" or "Update Failure No b3 controller matches to upd...

Issue Failure when upreving a Controller to a new flash version. Error window pops up with the error message "This Uprev file does not match this type of controller.". SmartStruxure "Update Failure No b3 controller matches to update" Environment Continuum Controllers b3 Cause The Controller Model has been entered incorrectly or you are trying to load the wrong flash file into the controller, e.g., the Controller Model in the Device object has been incorrectly set to i2810 when the controller is actually an i2814. Resolution Confirm that the correct flash file for your controller model and the Controller Model field both conform to the actual model type of your Controller. In offline editing check that the database also contains the correct model type. For b3s (Notice the 4th digit) The 4.501064 firmware is for the –Vs The B3865B4.500076 is for the non –V
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1896 Views

How to sound a buzzer when a Request To Exit (REX) button is pressed?

Issue How to sound a buzzer when a Request To Exit (REX) button is pressed on a Continuum Access system? The inputs to a door are not defined as regular Infinity inputs so how can they be programmed by Plain English programming? Environment ACX57xx (ACX5740, ACX5720) and AC-1 IOU modules (AC-1, AC-1A, AC-1 Plus) Cause When engineering an access control project, there is sometimes the requirement to sound a buzzer or turn on a light when the door is unlocked, or when a Request To Exit button is pressed, as the input points used within the door object configuration are not defined as a regular Infinity Inputs, so how to achieve this functionality? Resolution To use a Request To Exit (REX) switch on any of the ACX controllers or AC1 Modules:  It has to be a supervised input wired with the appropriate resistors in one of the 6 standard configurations defined in the installation guides (All available on the Extranet). You can not use a simple digital input switch without resistors. Incorrect circuitry or missing resistors will result in a Trouble indication on the door. The REX input is not a regular Continuum input point as it is defined within the door configuration, as it is not a Infinity input point directly accessible from Plain English but can be read via the "ExitRequest" attribute of the door. To sound a buzzer from the from the door there are 3 options: Use the existing door output and slave a buzzer circuit from the output that drives the Magnetic lock, so will sound when the door unlocks. If you want the buzzer to sound when the REX button is pressed then use a button with a 2 pole switch (2 separate contacts): Wire one to the REX input with appropriate resistors. Wire the other switch to a spare Input Configure it as either a Digital input or a Supervised input with resistors. This point can be used in your PE programming to drive the buzzer output. The third option is to use a Plain English program to read the "ExitRequest" attribute of the door and turn on an output for a defined time. The ExitRequest attribute may only be on for a short period of time so the program must be constantly looking for this attribute to change as well as keeping the controller Scan time low.  
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Labels:
  • Andover Continuum
2035 Views

Errors when exporting extended log points

Issue "ExtLogDataReport – The object type specified is invalid" and "ExtLogEnable – Attribute value is invalid" when exporting extended log points. Product Line Andover Continuum Environment CyberStation Cause Those errors are basically benign.  We have seen this randomly in the past and what they are usually caused by is a “null” value primed in the DB for those attributes Resolution Ignore those errors
View full article
Picard Product_Support
‎2018-09-06 02:09 PM

Labels:
  • Andover Continuum
1220 Views

Installing multiple Continuum Service packs without updating the database causes an Error in Processing Bytecode Error.

Issue After installing Continuum Service Pack 1 2 and three for Continuum 1.62, received Error in Processing Bytecode when running the import/export fixup utility. Environment Continuum 1.62 WebClient 1.62 Cause Continuum Service Packs SP1, SP2 and SP3 were installed without updating the database using Database Initialization after each installation. Resolution Always read the release notes that are included with Continuum Service Packs.  The release notes provide information on how to properly install the service pack. In order to correct this issue follow this procedure. Backup the Continuum Database. Archive Continuum User profiles. Archive all pin files. Archive all graphic background files. Run Database Initialization and update the database. Install Service Pack 1 per the instructions in the release notes. Run Database Initialization and update the database. Install Service Pack 2 per the instructions in the release notes. Run Database Initialization and update the database. Install Service Pack 3 per the instructions in the release notes. Run Database Initialization and update the database.
View full article
Picard Product_Support
‎2018-09-06 02:09 PM

Labels:
  • Andover Continuum
1215 Views

OPC Server Integration

Issue Is an Xdriver (X-Driver) needed for OPC integration? Product Line Andover Continuum Environment Continuum CX(99xx) Cause OPC server requirements Resolution An Xdriver is not needed to operate the OPC Server. Link to OPC Server Datasheet Link to OPC Server Software
View full article
Picard Product_Support
‎2018-09-07 06:05 AM

Labels:
  • Andover Continuum
1925 Views

I2-866-S enclosure for smoke control

Issue What enclosure is supported for I2-866-S Environment Infinet I2-866-S UL 864 Cause Enclosure support for UL 864 I2-866-S Resolution The VAV-ENCL-S enclosure is supported for the I2-866-S
View full article
Picard Product_Support
‎2018-09-06 02:09 PM

Labels:
  • Andover Continuum
853 Views

Upgrading Firmware and received error "could not communicate with specified controller"

Issue Upgrading Firmware and received error "could not communicate with specified controller" Environment Continuum Cyberstation ACX (5720, 5740) Netcontroller 2 (9680) Cause Received error while upgrading firmware. Firmware for the wrong model controller was attempted. Resolution Upgrade firmware with correct model firmware. Andover Continuum Software Compatibility Matrix Link
View full article
Picard Product_Support
‎2018-09-07 05:48 AM

Labels:
  • Andover Continuum
1098 Views

How to see a list of Personnel and their attached Personnel Templates.

Issue Using the "TemplateName" and "TemplateAlias" attributes in a ListView, does not show the attached Personnel Template. Environment Continuum Cyberstation Cause Not using the attribute "RefTemplate" to view attached Personnel Templates. Resolution  Use the attribute "RefTemplate". This is the Personnel's referenced template and is the field used to link to the template. Open the Personnel ListView where you want to view the attached template. Select View-> ListView Configuration. On the columns tab select "Add Column". Select attribute field and from the drop down list select "RefTemplate" Save Listview and re-run. It now shows the attached templates in the RefTemplate field.
View full article
Picard Product_Support
‎2018-09-06 02:09 PM

Labels:
  • Andover Continuum
1015 Views

Where are the updated Continuum Security Demo Graphics (Security System Bonus Pack) located?

Issue Where can the new-look Continuum Security Demo Graphics be found? Environment Continuum Security Cause Continuum Security Demo Graphics (Security System Bonus Pack) could not be found. Resolution The Security System Bonus Pack which includes the Security Graphics and Menu's can be downloaded from The Exchange.
View full article
Picard Product_Support
‎2018-09-07 08:06 PM

Labels:
  • Andover Continuum
1378 Views

What is the maximum number of Access Events a controller can hold?

Issue The AccessEventSize system variable determines the number of events to retain in a controller when it goes offline, what is the largest value you can enter? Environment Access Control systems using the Netcontroller II (9680) and ACX57xx (5740, 5720) Cause When designing an access control system, it is often required to know how many access events a controller will retain if the network connection to the workstations is lost. Resolution There is no fixed maximum number you can enter in the EventLogSize, it is dependent on the available free memory in the controller (Freemem). Typically you should have enough available memory be able to enter a maximum value between 100,000 and 170,000, but this will use up the majority of the controllers available memory. This may be OK if you are only doing Access control with the controller, but if you are also doing: BMS functions then you may have requirements to store logged data for temperatures etc.  Or you may be using X Drivers with thousands of numeric points           These would all use up the free memory and may only allow you to hold a few thousand events.  You have the flexibility to set the value, but the controller will not allow you to enter values that would exceed its available memory.
View full article
Picard Product_Support
‎2018-09-06 02:09 PM

Labels:
  • Andover Continuum
1039 Views
  • « Previous
    • 1
    • …
    • 56
    • 57
    • 58
    • …
    • 111
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of