Changing the NetController Model Type between 9900 and 9940
  • Changing the NetController Model Type between 9900 and 9940
  • sesa119747
    sesa119747
  • Carl_Slack
    Carl_Slack
‎2018-09-06 02:50 PM
  • NetController CX9900
  • NetController CX9940
Update NetController model number in Continuum database
  1. Backup the database.
  2. Shut down Continuum as precautionary measure
  3. Open the SQL Enterprise Manager
  4. Open the SQL Query Analyzer
  5. Select the ContinuumDB
  6. To change from 9900 to 9940, type in update infinitycontroller set CntrlType = 44 where UiName = ‘Infinity1’ and execute
  7. To change from 9940 to 9900, type in update infinitycontroller set CntrlType = 42 where UiName = ‘Infinity1’ and execute
  8. Please note that you must change ‘Infinity1’ to match the Uiname of your controller
  9. Start Continuum up again and verify that the change was effective