Description of error messages on the LCD display of the old style Infinet controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Description of error messages on the LCD display of the old style Infinet controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • ScottLeedberg
    ScottLeedberg
  • sesa119747
    sesa119747
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2984 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Description of error messages on the LCD display of the old style Infinet controllers

Picard Product_Support
‎2018-09-06 02:46 PM

Issue

There is an error message on the LCD display of the old style Infinet controllers. What do these errors mean?

Product Line

Andover Continuum

Environment

Infinet Controller

Cause

Information on the error code received on the LCD display.

Resolution

Infinet controller is displaying error 1 on its LCD display.

This message indicates that the controller received a bad packet of data on the Infinet. If the problem persists follow troubleshooting instructions.

  • Verify Infinet cable connections, approved twisted shielded pair cable, less than 4000 feet of network cable between Infilink repeaters, no more than 31 controllers between Infilink repeaters.
  • Verify proper grounding at the Infinet controller on the AC power terminals, poor grounding can cause erratic operation and communication problems. Easiest method to verify ground is to connect a digital voltmeter between the earth ground terminal on the power strip of the controller and the shield of the Infinet. this method will only work if you have connected your shields all through the network back to the Infilink and CX controller.
  • Check the baud rate switch on the Infilink repeater module, although the Infinet controllers auto baud, the Infilink baud rate must be manually switched.
  • Break down the network in segments to identify the bad controller or network segment. A binary search is recommended. (i.e. break the network in half, if this resolves the problem add half of the deleted back on, if it does not resolve the problem cut the remaining network in half, etc.). Once the offending segment has been identified, troubleshoot to the cable segment or controller level

Infinet controller is displaying error 2 on its LCD display. This message means that it could not pass a token to another controller on the Infinet. If the problem persists follow troubleshooting instructions. (No response to the Infinet token pass)

  • Verify Infinet cable connections, approved twisted shielded pair cable, less than 4000 feet of network cable between Infilink repeaters, no more than 31 controllers between Infilink repeaters.
  • Verify proper grounding at the Infinet controller on the AC power terminals, poor grounding can cause erratic operation and communication problems. Easiest method to verify ground is to connect a digital voltmeter between the earth ground terminal on the power strip of the controller and the shield of the Infinet. this method will only work if you have connected your shields all through the network back to the Infilink and CX controller.
  • Check the baud rate switch on the Infilink repeater module, although the Infinet controllers auto baud, the Infilink baud rate must be manually switched.
  • Break down the network in segments to identify the bad controller or network segment. A binary search is recommended. (i.e. break the network in half, if this resolves the problem add half of the deleted back on, if it does not resolve the problem cut the remaining network in half, etc.). Once the offending segment has been identified, troubleshoot to the cable segment or controller level

Infinet controller is displaying an error 3 on its LCD display. This means that the input reference voltage is out of range on the analog inputs.

  • Verify that inputs coming from external transducers are not exceeding the voltage input range, either 5 or 10 volts depending on model, if so use a voltage divider on the input.
  • Verify that any input wiring is not run in the same conduit as high voltage cable, or is properly shielded and grounded. If there is voltage getting coupled into the input wiring, separate the input wiring from the interference, or shield the cables. If the interference is being caused by the end device such as an auxiliary contact form an high voltage device, a cap between .01 and 1 microfarads across the input terminal to earth ground may alleviate the problem.
  • Remove field I/O wiring from the controller and recheck operation. If the problem goes away determine which I/O wire is the culprit and correct it.
  • Power down the Infinet controller and restart while connected to network. This will eliminate this unit having a duplicate ID on the network and it will also run the power up diags.
  • Verify proper grounding at the Infinet controller on the AC power terminals, poor grounding can cause erratic operation and communication problems. Easiest method to verify ground is to connect a digital voltmeter between the earth ground terminal on the power strip of the controller and the shield of the Infinet. this method will only work if you have connected your shields all through the network back to the Infilink and CX controller.
  • Remove field I/O wiring from the controller and recheck operation. If the problem goes away determine which I/O wire is the culprit and correct it.

Infinet controller is displaying an error 4 on its LCD display. This means that the analog output reference voltage is out of range.

  • Verify that inputs coming from external transducers are not exceeding the voltage input range, either 5 or 10 volts depending on model, if so use a voltage divider on the input.
  • Verify that any input wiring is not run in the same conduit as high voltage cable, or is properly shielded and grounded. If there is voltage getting coupled into the input wiring, separate the input wiring from the interference, or shield the cables. If the interference is being caused by the end device such as an auxiliary contact form an high voltage device, a cap between .01 and 1 microfarads across the input terminal to earth ground may alleviate the problem.
  • Remove field I/O wiring from the controller and recheck operation. If the problem goes away determine which I/O wire is the culprit and correct it.
  • Power down the Infinet controller and restart while connected to network. This will eliminate this unit having a duplicate ID on the network and it will also run the power up diags.
  • Verify proper grounding at the Infinet controller on the AC power terminals, poor grounding can cause erratic operation and communication problems. Easiest method to verify ground is to connect a digital voltmeter between the earth ground terminal on the power strip of the controller and the shield of the Infinet. this method will only work if you have connected your shields all through the network back to the Infilink and CX controller.
  • Remove field I/O wiring from the controller and recheck operation. If the problem goes away determine which I/O wire is the culprit and correct it.

Infinet controller is displaying an error 5 on its LCD display. This indicates the controller underwent a reset of power down and retained memory ( warm start). If there is not reason for this to occur power outages etc., then troubleshoot the problem.

  • Verify proper grounding at the Infinet controller on the AC power terminals, poor grounding can cause erratic operation and communication problems. Easiest method to verify ground is to connect a digital voltmeter between the earth ground terminal on the power strip of the controller and the shield of the Infinet. this method will only work if you have connected your shields all through the network back to the Infilink and CX controller.
  • Measure the AC power at the controller, Verify it is within specification (nominal +/- 20%). Typically 24 VAC power that is daisy chained will drop the voltage along the connections leaving the power below the acceptable level even if the transformer is sized correctly.
  • Verify that any outputs that are driving inductive loads such as relays, actuators, or valves, have a varistor across the coil n the field device.
  • Verify that any input wiring is not run in the same conduit as high voltage cable, or is properly shielded and grounded. If there is voltage getting coupled into the input wiring, separate the input wiring from the interference, or shield the cables. If the interference is being caused by the end device such as an auxiliary contact form an high voltage device, a cap between .01 and 1 microfarads across the input terminal to earth ground may alleviate the problem.
  • Remove field I/O wiring from the controller and recheck operation. If the problem goes away determine which I/O wire is the culprit and correct it.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3100
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of