Continuum displays the error "Cannot Create Empty Document."
  • Continuum displays the error "Cannot Create Empty Document."
  • JohnBoehmer
    JohnBoehmer
  • Alan_Wood
    Alan_Wood
  • sesa116832
    sesa116832
‎2018-09-06 02:50 PM
When opening a pinpoint graphic on Cyberstation, Continuum displays the error "Can't Create Empty Document."
CyberStation
This error may be displayed when trying to create or open a graphic file.
May indicate that either the XML parser or the Pinpoint.INI file has been corrupted.
The fix is to reinstall the XML parser.
  1. On the workstation displaying the error, exit Continuum gracefully.
  2. Open  Windows Explorer
  3. Browse to the C:\Windows Folder
  4. Find and delete Pinpoint.ini  (Continuum will rebuild this file on startup).
Try to edit or create a graphic file. If the problem persists, the fix is to reinstall the XML parser.
  3. Browse to the Program Files > Continuum > Install folder
  4. Run msxml3.msi
  5. Run msxml4.msi
  6. If you have an older version of Continuum you may only find msxml3.msi.
  7. You should not have to reboot the workstation after the install has completed successfully.
  8. Start Continuum
  9. You may need to Uninstall Continuun, reboot, Reinstall Continuum
  10. If the above doesn't correct the issue, go to a restore point prior to the problem or reformat the hard drive and reinstall Windows and Cyberstation
  • 2956
50% helpful (1/2)