Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,825
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 501
    • 502
    • 503
    • …
    • 509
  • Next »

Configuring a minimum off time for a TAC Xenta 121-HP

Issue It is desired to configure a minimum off time, so when the compressor stops in e.g. heating mode, it will not start again before a minimum time has elapsed in the same mode. This setting is not available in the device. Environment TAC Xenta 121-HP Cause There is no setting for minimum stop time when in the same mode, there is only a minimum stop time between modes. Resolution As a workaround, set the "Activate at" value to something other than zero (say 10%), so that you can use the "Hysteresis" at 10%, and this way get a delay. This way you will get a delay in the most cases, a little time before the controller reacts.
View full article
Picard Product_Support
‎2018-09-06 08:38 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
998 Views

Continuum crashing when alarms are being sent out as emails.

Issue Email alarming is configured correctly but Continuum keeps crashing when alarms are sent as emails. ACCDataServices is the crashing module.   Windows Application log shows two email errors that point to an issue with Outlook. Email, Failed to send email - SendNote in Send function failed. Result is 80070057. Email, Failed to send email -  SubmitMessage failed in CSession::SendNote, Result is 80070057 Environment Continuum Alarming Outlook Cause Outlook account folder is too large and does not have available space for new entries. In this case the folder was 7GB in size with emails going back eight years. Resolution Archive Outlook account folder and truncate to free up space for new emails.  
View full article
Picard Product_Support
‎2018-09-06 08:38 AM

Labels:
  • Andover Continuum
1100 Views

It is not possible to query multiple OU containers with the Personnel Import Utility

Issue With the Personnel Import Utility, is it possible to query multiple OU containers? Product Line Andover Continuum Environment Personnel Import Utility (PIU) Cause Need to be able to query multiple OU containers. Similar to below query. Server Name: LDAP://test/DC=test, DC=com (test and com are separate domains) Resolution Unfortunately the query cannot be changed to accommodate this. Different Domains can be specified but it is not possible to go down to the OU level.
View full article
Picard Product_Support
‎2018-09-06 08:38 AM

Labels:
  • Andover Continuum
972 Views

Can the Personnel Import Utility update existing Personnel only and not create new Personnel objects if they do not already exist?

Issue Can the Personnel Import Utility update existing Personnel only and not create new Personnel objects if they do not already exist? Environment Personnel Import Utility PIU Cause Need to be able to only modify existing Personnel and not create new ones when performing Personnel import with the PIU. Resolution The way the PIU handles this, to modify existing Personnel or if none exists to create a new one, is "functions as designed". There is no way to stop a new Personnel object from being created when it is unique.
View full article
Picard Product_Support
‎2018-09-06 08:37 AM

Labels:
  • Andover Continuum
1087 Views

Version compatibility between StruxureWare Building Operation Technician Tool and servers

Issue Is a certain version of Technician Tool Mobile Application compatible with all versions of StruxureWare Building Operation? Product Line EcoStruxure Building Operation Environment Building Operation Technician Tool Automation Server Enterprise Server Cause The Technician Tool will always be backwards compatible, meaning that the latest version of the tool will work with any version of SBO. Older versions of the Technician Tool may not work with a newer version of SBO. Resolution Please note: Mobile experience to be replaced with EcoStruxure™ Building Operation v2.0 WebStation. For further information, please refer to Notice of Withdrawal of the Building Operation Technician Tool Always use the latest version of Technician Tool Mobile Application when possible, as that will work with all SBO versions.
View full article
Picard Product_Support
‎2018-09-06 08:37 AM

Labels:
  • EcoStruxure Building Operation
2014 Views

"Validation failed for property 'PrimaryPassword'" when renaming an Automation Server

Issue When attempting to rename an Automation Server, the following error is shown: Validation Error Validation failed for property 'PrimaryPassword'. Path: '[server path]'. Type 'Password' Cannot set property value to null because the property is not nullable. Environment Automation Server Cause The Automation Server has been cloned using a backup of another Automation Server, and in that process the SMTP server passwords have been set to null. Resolution Configure a password for the primary and secondary SMTP server. It does not matter what the password is set to.
View full article
Picard Product_Support
‎2018-09-06 08:36 AM

Labels:
  • EcoStruxure Building Operation
1228 Views

Forcing a value from the BACnet front-end will be overridden by the Lua script

Issue When Forcing a value from SBO, it is just overwritten by the Lua script all the time. Product Line EcoStruxure Building Expert Environment MPM SE8000 Cause By default, the MPM executes the program once every second, so if written simply like: Output_1 = Off the output will be turned Off every second. Resolution Declare a few variables in the Lua script that will help you implement the logic you need, here is an example: var("Override_Status","ME.BV1") var("Override_Value","ME.BV2") if changed.Override_Status and Override_Status == 1 then ME.BO1 = Override_Value elseif changed.Override_Status and Override_Status == 0 then ME.BO1 = ME.BI1 end Basically, an override status points will act as a "Override button", and when it is active, The output will be equal to override value specified in SBO. Else, if it is disabled, the output will be set to what ever you currently have in your script. In the example above, the output will be equal to the input.
View full article
Picard Product_Support
‎2018-09-06 08:36 AM

Labels:
  • EcoStruxure Building Expert
2044 Views

Digital Sentry Control point 7.9 or greater breaks Cyberstation Video Integration

Issue Upgrading Digital Sentry breaks the Video Server connection or cameras won't learn or video streams do not work Product Line Andover Continuum, Pelco Environment Pelco Digital Sentry 7.9 or greater Continuum Video Integration 1.94 SP1 up to 2.01 Windows 7 Windows Server 2008 Windows Server 2012 Cause Pelco released a newer version of Control Point that is used in Digital Sentries Video Recorders 7.9 and above. This newer API is not currently supported in any version Continuum, up to version 2.01. Resolution Available as of July 2017, install version 2.02 of Continuum, it is a full install. R&D has worked on revising the Continuum Video Integration to work with the newer versions of Control Point 7.15 and above. The only work around prior to this to get the video Integration to function was to downgrade the Digital Sentry to Control point 7.8 Uninstall the DS ControlPoint software using Add/Remove programs (MS Windows XP) or Programs and Features (MS Windows 7). Install: How to install the DS ControlPoint client software Note: Upgrading the Continuum Security Key to an Endura Key will not allow the newer API to be used with a Digital Sentry with Continuum. A copy of the latest Video Compatibility Matrix can be downloaded from the Download Center in PA-00568.
View full article
Picard Product_Support
‎2018-09-10 12:59 PM

Labels:
  • Andover Continuum
  • CCTV
2490 Views

Error importing a StruxureWare Building Operation export file

Issue Error importing a StruxureWare Building Operation export file. Below is an example of the error.  ERROR: Import failed to commit changeset transaction with an exception. RecoverableException: /home/ci/ci-build/rb-rb-1.8.1-system/source/server/nsp_servers/csc/changesetmanager/source/ChangeSetTransaction.cpp(1442) Invalid Data Error: File_Extension_Not_Permitted (0x10048) in module Security_Manager(74). "Not permitted to store the file "htgseqintro.wmv" with the current Document Policy." - Stack Environment StruxureWare Building Operation 1.8 Cause The export file contains a document file extension that is not permitted in the Document Policy Permitted File Extensions Resolution The file extension has to be added to the Permitted File Extensions list. See Adding a File Extension to the Permitted File Extensions List on Web Help. For the error example shown in the issue of this article, the extension wmv has to be added to the Document Policy Permitted File Extensions. list. 
View full article
Picard Product_Support
‎2018-09-10 10:33 AM

Labels:
  • EcoStruxure Building Operation
2060 Views

Access Expert Controller in Unknown State

Issue Controllers are unable to get online after configuration and being added to the relative instance. Product Line Access Expert Environment Access Expert in Cloud or Premise Installations Win 7, Win 8, Server 2012, Server 2014 SSC Controller Cause There are two reason why this could happen: The controller is not communicating with the Feenics Host Service. Outbound Ports are being blocked. Resolution To resolve the issues, please check the following: The controller is not communicating with the Feenics Host Service. The panel may have lost power or network communication. Dip switches may be set incorrectly (Refer to the Mercury Installation Manuals for operating modes) Network Firewall may be blocking outbound communication over port 3001 (Give our Network Tester tool a try, find it within the downloads) Configured DNS server may be unable to resolve at the correct IP.       2.    The user is unable to see events through the Feenics Event Publishing Service. Outbound port 4502 may be blocked. (Give our Network Tester tool a try, find it within the download section) The client has lost internet connection.
View full article
Picard Product_Support
‎2018-09-06 08:35 AM

Labels:
  • EcoStruxure Access Expert
1629 Views

Access Expert credentials not working

Issue After a card is created and added to a user, card is read and the credentials are invalid and not working. Product Line Access Expert Environment Access Expert, Server 2012 R2 and above. Version 2 Version 3 Cause There are several reasons that  could cause Access Denied to occur as listed below. Resolution To resolve the issue please follow the steps below: Access Denied – Invalid Card Format The intelligent controller has no configured card format which matches the number of bits sent from the credential reader. Opening this event inside the live monitor or event history view will display the card bit length of the credential along with its hexadecimal encoding. Access Denied – Invalid Facility Code The intelligent controller has a card format which matches the bit length of the card, however there are no card formats which match the facility code. Opening this event inside the live monitor or event history view will display the interpreted card numbers & facility code based off of the card format with matching bit length. Access Denied – Card/PIN Not Found The intelligent controller has matched the card format & facility code, but has no matching card number value. Opening this event inside the live monitor or event history view will display the interpreted card number & facility code based off of the format with matching bit length. When receiving this event with a card believed to have been programmed correctly, Users may issue a clear/reload cards on the controller to update the database. Access Denied – No Door Access The intelligent controller has acknowledged that this card has access on this intelligent controller, but not to this particular reader.     Access Denied – Door Schedule The intelligent controller has acknowledged that this card has access to this reader, but it is outside the allowed schedule. This event may also trigger if the interface dip switches are not configured correctly. **Don't forget to take advantage of Mercury’s Simulated Card Read functionality to ensure that the controller is making the correct access decision. In V3 the Card Formats needs to be added to the Controller in Order for this to work. **If a reader produces no audible response or LED change when a credential is presented it means that either the reader is powered incorrectly, or that it cannot read the credential technology.
View full article
Picard Product_Support
‎2018-09-06 08:35 AM

Labels:
  • EcoStruxure Access Expert
2452 Views

Access Expert "Access Denied - no door access"

Issue Access Denied NO access at the door Product Line Access Expert Environment Win Server 2012 R2 and above Cause 1) The cardholder does not have sufficient Access Levels assigned. 2) The Max access levels has been reached by the intelligent controller. 3) The access levels were not successfully downloaded to the controller. Resolution To resolve this, the following steps need to be followed: 1. Ensure that the access levels contains a door group which consists of the trouble reader. 2. Check that the person has the correct access level assignment, 3. Try saving the access level again so that it is pushed to the controller. 4. If possible, issue a reboot command to the intelligent device to ensure database synchronization. OR if the system database limit on access levels has been reached, take the following steps. Verify the user has permissions on the Role Go to the General Configuration Select System Settings Select the Hardware Tab on the bottom Change the Max Access Level to a higher level than the default (100). Save and Reboot the controller for the changes to take effect
View full article
Picard Product_Support
‎2018-09-06 08:35 AM

Labels:
  • EcoStruxure Access Expert
2045 Views

Communication issue with Xenta devices

Issue The communication with TAC Xenta controllers is slow or inconsistent Product Line EcoStruxure Building Operation Environment TAC Xenta LonWorks communication Cause The Non group receiver timer is not properly set. Every device has a timer called Non group receive timer. The Non group receive timer is used to make sure that a re-sent Lon package will not be treated as a new message and to determine when a receiver buffer can be released. It is used in Acknowledged, Repeated and Request/Response transactions, but not in Unacknowledged ones. If this timer is set too low, a re-sent package, like Unacknowledged repeated message, may be treated as new messages, that will be sent on to the application. The communication buffers will not be released until the timer has expired. If the timer is set too long, that may result in the device running out of buffers, and new messages will not be received during this time. If a device has many SNVTs or TACNV’s being transferred there may be a need to increase the value of the Non group receiver timer. The default value for a programmable Xenta device is 768 ms. Resolution Change the Non group receive timer of the Xenta devices. The default value for a programmable TAC Xenta device is 768 ms. The recommended timer values are:   Number of network variables Non group receive timer value < 50 768 ms (default) 50 – 100 1024 ms > 100 1536 ms     The default value for the AS and AS-P  is 8,092 ms. There is no need to change that value.
View full article
Picard Product_Support
‎2018-09-10 01:01 PM

Labels:
  • EcoStruxure Building Operation
2271 Views

Creating New User Roles in Access Expert

Issue Creating new user roles and knowing the access that is needed for it to become active. Product Line Access Expert Environment Cloud or Premise Installations V2 Win 7 Win 8 Server 2012 Server 2014 Cause Knowing what the role the user is playing would determine what selections need to be activated for them. Resolution To achieve this the following steps need to be followed: Open up General Configuration Select the Roles icon Click on the tab for New Role (everything is blank by default) Name and configure accordingly Check all tabs to make sure everything is Viewable and Editable Save and close Now this role can be selected for any user once created
View full article
Picard Product_Support
‎2018-09-06 07:40 AM

Labels:
  • EcoStruxure Access Expert
1437 Views

Actuator control signal impedance

Issue Some actuator datasheets do not specify the impedance of the 0-10V control signal, this is required to determine fan out from a controller. Product Line Field Devices Environment MB3 Range - MB3-24M, MB3-SO-24M, MB3-SC-24M MZ20 Range - MZ20A, MZ20A-R MVT56 Range Cause Information not defined on the specification sheet. Resolution MB3 Range 0-10V control signal input impedance = 200K Ohms. MZ20 and MVT56 Ranges 0-10V control signal input impedance = 32K Ohms.
View full article
Picard Product_Support
‎2018-09-06 07:40 AM

Labels:
  • Field Devices
997 Views

Variable Status Alarms do not operate on a BACnet point.

Issue If a Variable status alarm is setup on a BACnet point it never triggers. Environment Workstation V1.8.1  and earlier Cause The reason is that the 3 available triggers (Forced, Overridden and Offline) do not apply to the BACnet protocol. If you open up the bindings page for a BACnet point you will see that none of the BACnet point attributes are the same as these 3 trigger statuses. Resolution Although from the SBO side you can force a point, what actually happens is that the value becomes commanded at "Command priority 8" (by default). The BACnet protocol does not have a Forced attribute. There is also no attribute listed for Overridden and Offline point in the BACnet standard. Because of this the Variable Status Alarm does not apply to a BACnet point.  
View full article
Picard Product_Support
‎2018-09-06 07:39 AM

Labels:
  • EcoStruxure Building Operation
1604 Views

Renewing OpenLNS CT Annual Maintenance

Issue Why isn't the OpenLNS a full, un-limited license? Environment OpenLNS OpenLNS CT Cause Renewing OpenLNS CT Annual Maintenance You can renew your annual maintenance for OpenLNS Server and OpenLNS CT before they expire. Renewing your OpenLNS and OpenLNS CT annual maintenance enables you to continue installing software updates and upgrades. If you do not renew the products’ maintenance, you can still use the products; however, you will not be able to upgrade it with updates or upgrades released after your annual maintenance expired. You cannot renew your annual maintenance after it has expired. Once it has expired, you must purchase a new activation key to be able to install any updates or upgrades released after your maintenance expired. To renew your annual maintenance, purchase an OpenLNS Commissioning Tool Professional One-Year Maintenance Renewal (Echelon model number 93800) or an OpenLNS Commissioning Tool Standard One-Year Maintenance Renewal (Echelon model number 93810). Echelon will process your order, and your maintenance coverage will be extended so that you can continue updating and upgrading OpenLNS and OpenLNS CT for an additional year. Resolution If paying the annual maintenance fee, you have access to updates and upgrades. Not paying still means that the program could be used, however it could not be updated with the latest patches.
View full article
Picard Product_Support
‎2018-09-06 07:39 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1355 Views

MPM rebooting with message in the log like "Message:Task ID 38:Lua_User_PGs expired"

Issue MPM rebooting with message in the log like: MASTER_MAN (id= 9) 361893.721> FAULT: core_watch.c:333; code:0; time:2017-02-13 15:34:25; Message:Task ID 38:Lua_User_PGs expired at 361886.5; Top Of Stack:0x000000F3 0x20D4BE7C 0x71B73B76 0x0000007A 0x00000000 0x60000013 0x60000013 0x00000000 0x2084D224 0x08080808 0x09090909 0x10101010 0x11111111 0x00000015 0x2006FD91 0x2006FD91 0x20D48D3C 0x20062159 0x00000000 0x00000000 0x20EE8248 0x20D48D3C 0x00000000 0x00000000 0x22D50000 0x00000000 0x20D1E8E4 0x000007D0 0x00000000 0x2084D238 0x00000000 0x00000000 ; Product Line EcoStruxure Building Expert Environment MPM Cause This is an error in one of the PG object (user written Lua script) possibly an infinite loop. Resolution Disable or delete 1 by 1 your Lua PG's to identify the PG with the issue.
View full article
Picard Product_Support
‎2018-09-06 07:39 AM

Labels:
  • EcoStruxure Building Expert
2552 Views

BACnet Input shows "Out of Service". When attempting to set a value or remove the out of service flag an error is seen.

Issue BACnet Input shows "Out of Service". When attempting to set a value or remove the out of service flag an error is seen. "An attempt has been made to write to a BACnet property with a value that is outside the range of values defined for the property." Environment bCX4040 b3 Controllers Cause An xP Module attached to the Controller was malfunctioning and the inputs on this board were not functioning. Resolution Powering everything down, re-seating the xP Module board and powering the Controller back up resolved the problem.
View full article
Picard Product_Support
‎2018-09-06 07:38 AM

Labels:
  • Andover Continuum
1960 Views

Automatically backup a b3 controller to flash

Issue How to automatically have b3 controller backup to flash. Product Line EcoStruxure Building Operation Environment b3 Script Program Cause Script program syntax is a bit different to how it was done in Continuum, specific details needed on how to set this up.  Resolution This is a sample script program to enable automatic backup to flash when the controller database is different to what is currently stored in Flash. Create the below Script Program in the b3 controller. Make sure to bind both the input and output variables to statusbackup/value. 'bind statusbackupin and statusbackupout to the systemvariable statusbackup/value. numeric input statusbackupin numeric output statusbackupout init: if ts >= 5 then goto checking checking: if statusbackupin = backupneeded Then   statusbackupout = backupnow Endif goto wait1day wait1day: if td >= 1 then goto init
View full article
Picard Product_Support
‎2018-09-06 07:38 AM

Labels:
  • EcoStruxure Building Operation
1524 Views
  • « Previous
    • 1
    • …
    • 501
    • 502
    • 503
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of