Access Expert Controller in Unknown State

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Controller in Unknown State
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • sesa119747
    sesa119747
  • Derrick_Ratliff
    Derrick_Ratliff
  • Alan_Wood
    Alan_Wood
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1630 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Controller in Unknown State

Picard Product_Support
‎2018-09-06 08:35 AM

Issue

Controllers are unable to get online after configuration and being added to the relative instance.

Product Line

Access Expert

Environment

  • Access Expert in Cloud or Premise Installations
  • Win 7, Win 8, Server 2012, Server 2014
  • SSC Controller

Cause

There are two reason why this could happen:

  1. The controller is not communicating with the Feenics Host Service.
  2. Outbound Ports are being blocked.

Resolution

To resolve the issues, please check the following:

  1. The controller is not communicating with the Feenics Host Service.
  • The panel may have lost power or network communication.
  • Dip switches may be set incorrectly (Refer to the Mercury Installation Manuals for operating modes)
  • Network Firewall may be blocking outbound communication over port 3001 (Give our Network Tester tool a try, find it within the downloads)
  • Configured DNS server may be unable to resolve at the correct IP.

      2.    The user is unable to see events through the Feenics Event Publishing Service.

  • Outbound port 4502 may be blocked. (Give our Network Tester tool a try, find it within the download section)
  • The client has lost internet connection.
Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (1)
  • Find more articles tagged with:
  • 18961
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of