Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Access Expert credentials not working

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert credentials not working
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa119747
    sesa119747
  • Derrick_Ratliff
    Derrick_Ratliff
  • Cody_Failinger
    Cody_Failinger
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2493 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert credentials not working

Picard Product_Support
‎2018-09-06 08:35 AM

Issue

After a card is created and added to a user, card is read and the credentials are invalid and not working.

Product Line

Access Expert

Environment

  • Access Expert, Server 2012 R2 and above.
  • Version 2
  • Version 3

Cause

There are several reasons that  could cause Access Denied to occur as listed below.

Resolution

To resolve the issue please follow the steps below:

  1. Access Denied – Invalid Card Format
    • The intelligent controller has no configured card format which matches the number of bits sent from the credential reader.
    • Opening this event inside the live monitor or event history view will display the card bit length of the credential along with its hexadecimal encoding.
  2. Access Denied – Invalid Facility Code
    • The intelligent controller has a card format which matches the bit length of the card, however there are no card formats which match the facility code.
    • Opening this event inside the live monitor or event history view will display the interpreted card numbers & facility code based off of the card format with matching bit length.
  3. Access Denied – Card/PIN Not Found
    • The intelligent controller has matched the card format & facility code, but has no matching card number value.
    • Opening this event inside the live monitor or event history view will display the interpreted card number & facility code based off of the format with matching bit length.
    • When receiving this event with a card believed to have been programmed correctly, Users may issue a clear/reload cards on the controller to update the database.
  4. Access Denied – No Door Access
    • The intelligent controller has acknowledged that this card has access on this intelligent controller, but not to this particular reader.
  5.     Access Denied – Door Schedule
    • The intelligent controller has acknowledged that this card has access to this reader, but it is outside the allowed schedule.
    • This event may also trigger if the interface dip switches are not configured correctly.

**Don't forget to take advantage of Mercury’s Simulated Card Read functionality to ensure that the controller is making the correct access decision.

In V3 the Card Formats needs to be added to the Controller in Order for this to work.

**If a reader produces no audible response or LED change when a credential is presented it means that either the reader is powered incorrectly, or that it cannot read the credential technology.

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (1)
  • Find more articles tagged with:
  • 18964
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore