Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 465
    • 466
    • 467
    • …
    • 501
  • Next »

XIF parser fails due to "-sign.

Issue The XIF parser could fail if there is a "-sign in a commented row in the XIF default field. Environment TAC Vista Cause The XIF parser could fail if there is a "-sign in a commented row in the XIF default data field. Example: # ----------------------------------------------------- # ----------------------------------------------------- FILE value 1 1 ##dde1  "1,2,3\x00,1,2;"         // UCPTdownDriveTime                SNVT_time_sec 0x66,0x66 ##dde3 "1,2,23x00,2,2;"         // UCPTupDriveTime                     SNVT_time_sec   Resolution Just removing the "-sign will work: # ----------------------------------------------------- # ----------------------------------------------------- FILE value 1 1 ##dde1 1,2,3\x00,1,2;           // UCPTdownDriveTime             SNVT_time_sec 0x66,0x66 ##dde3 1,2,23x00,2,2;         // UCPTupDriveTime                   SNVT_time_sec
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • TAC Vista
1186 Views

Can multiple TCP/IP XDrivers be installed on a single 2nd Generation Controller?

Issue Will a single 2nd generation Controller  (NC2, bCX) support two IP XDrivers on two different comm ports?    Environment XDriver NC2 (CX9680) bCX4040 Cause Want to enable two IP XDrivers on different comm ports of the same Controller. Resolution You can only enable one IP XDriver per Controller. (Example: You can not enable a BACnet IP XDriver on one comm port and a Modbus IP XDriver on another, you would need two Controllers for this - one IP XDriver on each.)
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • Andover Continuum
1473 Views

Programmable controller does not get added. Progress window never closes

Issue Programmable controller does not get added. Progress window never closes Can not add programmable controller. Environment StruxureWare Building Operation 1.3 SP Function block editor TAC Xenta 301, TAC Xenta 302, TAC Xenta 401, TAC Xenta 281, TAC Xenta 282, TAC Xenta 283 Cause Check if there are any blocks named "version". This is a reserved word that is not allowed as a name Resolution Open Function block editor and search your application (F7) for the word version. Change version to something else
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • EcoStruxure Building Operation
1240 Views

Unable retrieve objects from a third party device that has been added to Continuum.

Issue Continuum found and added both third party chiller controllers, RLE LD5200.  When a send to database is executed however, no objects are added to the Continuum database. Environment BACNet RLE LD5200 Cause Some BAS systems use a 16 bit identifier while Continuum uses 32 bits. Resolution Problem resolved updating the third party controller firmware..
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • Andover Continuum
1117 Views

TAC License server can't be started

Issue TAC License server can't be started. TAC license server crashes Environment TAC Vista 5.1.8 Cause The license server can't start if there is a DEMO license in the same folder as the "real" license. Note that in 5.1.8 the default path to the license files have changed to: C:\Program Files\Schneider Electric\License Server\TacLic\Licenses Any license files that are in the old directory will be moved to the new one when upgrading. If you need to use DEMO licenses for a site you can add them to a separate directory and add that directory in the license setup.   Resolution Delete any DEMO licenses in: C:\Program Files\Schneider Electric\License Server\TacLic\Licenses Go to services and start TACLicenseServer  
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • TAC Vista
1673 Views

What causes "?_1" to be displayed in a Plain English program?

Issue When editing a PE program it displays "?_1" Environment Plain English Cause An object that the program is referencing has been deleted. If multiple objects have been deleted then the integer after the ?_ will increment. Resolution An object that the program is referencing has been deleted.  Recreate the missing object, enter it into the program and save the program.
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • Andover Continuum
1390 Views

What modems are supported for Xenta 901 dial -up to TAC Vista?

Issue What modems are supported for Xenta 901 dial -up to TAC Vista? Environment TAC Vista TAC Xenta 901 Cause Want to use a dial-up to TAC Vista. The support for dial-up in TAC Vista is mainly for upgrading of older systems. We have not added any new modems to the list in many years Resolution These modems are supported Us Robotics,3Com 56k Sportster(V92) D-Link DFM-560E+ Siemens MC-35 (GSM modem) Siemens M-20 (GSM modem) SRT (GSM modem) Wawecom (GSM modem) SRT DIN 35 (Leased line) SRT DIN (Dial up)
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • TAC Vista
1224 Views

Unable to Update ASC

Issue Unable to update an ASC when adding a new MR to an existing system. Product Line TAC INET Environment All versions of I/Net utilizing HVAC applications. Cause On a system that has multiple sublan devices and adding a new or several devices to the controller, when updating the UPD files it appears to get downloaded but when the MCI update is done, only one point is written to the database. If the points are added manually, a Memory Error would come up indicating that there is not enough memory in the controller to do this. However, this is not seen when doing the UPD file update nor MCI Update. Resolution To resolve this issue, the following steps needs to be done: Connect to the controller Go to Edit/Controller/Configuration Verify that the controller does in fact have memory left If not, look at the trends that are on the resident I/O Points If possible, delete unwanted trends that are using up memory to free it up to allow these devices to be added Once done, go back to ASC Parameters and then update the ASC and MCI again.
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • TAC INET
1619 Views

Filtering The AnalogSamples_xi.rpt SevenReport using the cell definition

Issue Filtering The AnalogSamples_xi.rpt SevenReport using the cell definition Environment I/NET Seven Reports Cause In some cases, the cell number can be used on a 7 trend to allow only trends of a certain type to show up in reports. If this rule is applied, you will need to change the stock reports to allow for this function. Resolution Open the AnalogSamples_xi.rpt file in Seven Reports Cancel the Date Time range selector In the Design View, click on the second icon from the left, directly underneath the word "Design" the tool tip labels it as "Select records to be used in report  Select Expert" Click on the " " tab browse to the bottom and expand "RptTrendDefinitions" Click on "CellNumber" Click OK In the left hand drop down select "is equal to" In the Right hand drop down, enter the cell number you wish to filter for. Click OK Preview the Report Save it using a different file name. 
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • TAC INET
1288 Views

Revised Kvs value V292

Issue In older versions of the documentation for V292, the Kvs value is incorrectly listed for some sizes.  Environment V292: 7219254000 7219258000 7219262000 7219266000 7219270000 Cause Incorrect information in older documentation. Resolution To make sure you are using the correct Kvs value, please refer to the latest available documentation that is available on the Extranet.
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • Field Devices
1155 Views

The BDelay object from the LonWorks jar conversion library intermittently shows very large "remaining time" causing logic issues.

Issue The BDelay object from the LonWorks jar conversion library intermittently shows very large "remaining time" causing logic issues. Environment R2, UNC's Cause The BDelay object does not initialize the time remaining properly under some conditions. Resolution In the Lib jar - programObjects - hvac folder there is a program called DelayedOutput.sns.  This program can do the delayed on and off function but will need to be enhanced if the time remaining output is required.
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • TAC IA Series
927 Views

Replacement for damper actuator NM24-SR

Issue NM24-SR is obsolete and needs be replaced. Environment   8760020000 NM24-SR  8751019000 MD10A-24 Cause Obsolete product needs replacement. Resolution   NM24-SR (8760020000) is replaced by the MD10A-24 (8751019000)
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • Field Devices
1327 Views

Kamstrup energy/heat/flow/cool meters pressure class

Issue What is the maximum system pressure for the meters? Environment Kamstrup Heat meter cool meter flow meter Cause It is important to make sure that the system pressure does not exceed the maximum pressure specified for the components included. Resolution Depending on which meter is chosen, it is either 16 Bar (PN16) or 25 Bar (PN25). This is defined in the charts that are available here: Heat/Flow Meter
View full article
Picard Product_Support
‎2018-09-11 04:00 AM

Labels:
  • Field Devices
1628 Views

Actuator for VGS211F

Issue Which actuator is suitable for valve VGS211F? Environment VGS211F: VGS211F-15CS04 VGS211F-15CS05 VGS211F-15CS07 VGS211F-15CS08 VGS211F-20CS VGS211F-25CS VGS211F-32CS VGS211F-40CS VGS211F-50CS VGS211F-65CS VGS211F-80CS VGS211F-100CS Forta: M700 MG900SR M800 M1500/MV15B M3000 Cause Application assistance. Resolution Depending on application,  the Forta range actuators are suitable: M700, MG900SR, M800, M1500/MV15B, M3000.   For more information ad details, please see the VGS211F data sheet.
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • Field Devices
2545 Views

MVB46 actuator for V311T

Issue Will a MVB46 fit straight onto a V311T valve?   Environment Controlli / Satchwell MVB46 TAC Forta Cause Controlli actuator on Schneider Electric / TAC valve Resolution   The Forta series actuators are suitable for use on the V311T valve. The data sheet for V311T has the different size Forta actuators listed, depending on application requirements.
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • Field Devices
1114 Views

Equivalent / replacement for actuator MS61-7203 from the European portfolio

Issue Needs a European replacement for a US product. Environment MS61-7203 AV-822 linkage kit TAC Forta Cause Replacing US portfolio product from EU equivalent. Resolution Use the TAC forta actuator that suits the application best. Together with linkage kit AV-622 this will fit most of the valves where the MS61-7203 fits.
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • Field Devices
1056 Views

Which replacement actuator for MZ88T?

Issue MZ88T is obsolete.  Environment MZ88T: 8455011000 8455013000 8455015000 MZ140-230T MZ140-24T MZ140-24M Cause Obsolete actuator needs replacement.  Resolution MZ88T series is replaced by the MZ140 series: MZ88T (230) is replaced by MZ140-230T MZ88T (24) is replaced by MZ140-24T MZ88TA is replaced by MZ140-24M
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • Field Devices
1350 Views

Unable to remove editlock from Continuum Objects

Issue Objects appear to be edit locked, however no asterisk appears in the editor title bar. Environment Cyberstation Continuum Users Cause Continuum user permissions had been restricted. Resolution Restored full edit permissions to Continuum User.
View full article
Picard Product_Support
‎2018-09-06 10:19 AM

Labels:
  • Andover Continuum
1368 Views

Can an alarm be configured to close the current graphic before launching the alarmed points graphic?

Issue How can an alarmed point be configured to close the currently active graphic before launching the graphic points alarm graphic. Environment Pinpoint Alarm Graphic Cause Using the Display Graphic action on an Event View, it is necessary to have only one alarm graphic open at a time. Resolution Event Notifications provide for the launching of specific graphic panels when a point goes into alarm. No provision exists for closing having this alarm close the currently active graphic panel before it' launches its graphic.
View full article
Picard Product_Support
‎2018-09-06 10:19 AM

Labels:
  • Andover Continuum
1109 Views

Field Devices - What grade of stainless steel is used in the Satchwell DWA range of sensor pockets?

Issue What grade of stainless steel is used in the Satchwell DWA range of sensor pockets Environment Sensor Pockets DWA Satchwell Cause Customer requires assurance that the stainless steel pockets are the correct grade. Resolution The DWA (Satchwell range) pockets that we sell are made from 316Ti steel. We use 316Ti rather than the 316L because of elevated temperature mechanical strength, pitting corrosion resistance, mechanical polishing and weldability.
View full article
Picard Product_Support
‎2018-09-06 10:19 AM

Labels:
  • Field Devices
1127 Views
  • « Previous
    • 1
    • …
    • 465
    • 466
    • 467
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore