Issue
Programmable controller does not get added. Progress window never closes
Can not add programmable controller.
Environment
StruxureWare Building Operation 1.3 SP
Function block editor
TAC Xenta 301, TAC Xenta 302, TAC Xenta 401, TAC Xenta 281, TAC Xenta 282, TAC Xenta 283
Cause
Check if there are any blocks named "version". This is a reserved word that is not allowed as a name
Resolution
Open Function block editor and search your application (F7) for the word version.
Change version to something else