Can multiple TCP/IP XDrivers be installed on a single 2nd Generation Controller?
  • Can multiple TCP/IP XDrivers be installed on a single 2nd Generation Controller?
  • AdamSteele
    AdamSteele
‎2018-09-06 10:21 AM
Will a single 2nd generation Controller  (NC2, bCX) support two IP XDrivers on two different comm ports?
XDriver
NC2 (CX9680)
bCX4040
Want to enable two IP XDrivers on different comm ports of the same Controller.
You can only enable one IP XDriver per Controller.
(Example: You can not enable a BACnet IP XDriver on one comm port and a Modbus IP XDriver on another, you would need two Controllers for this - one IP XDriver on each.)
  • 13396