Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,840
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 329
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1823 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 44
    • 45
    • 46
    • …
    • 92
  • Next »
Label: "TAC IA Series" Show all articles

When using a Niagara R2 Master Enterprise Server, do the projects require the same Project ID?

Issue When using a Niagara R2 Master Enterprise Server, do the projects require the same Project ID? Environment Niagara R2 Master Enterprise Server Cause Project ID is required for license information. Resolution Example: Two projects will eventually have a Master Enterprise Server (MES) over both of them.  One of the projects is in progress and the second phase will follow.   In order to use a MES and allow both projects to communicate with it, do both projects need to have the same Project ID? Or can each separate Enterprise Server maintain its own Project ID?   Requirement: The MES is licensed to support multiple Enterprise Servers (with different project IDs). Purchase the IA-MES-1 which supports an Enterprise Server for one site.  Additionally, each IA-MES-N would add another Enterprise Server (additional site). The project IDs for each Enterprise Server site would have to be provided in the license request form. The license will then list multiple project IDs and add the multisite feature.
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
1269 Views

How can Modbus address xxxx, function 16 be written?

Issue How can Modbus address xxxx, function 16 be written? Environment Modbus driver Cause To use function code 16 instead of 06, configure the properties usePresetMultipleRegister and usePresetMultipleCoil Resolution By default, the Modbus driver uses function codes 05 (Force Single Coil) and 06 (Force Single Register) and can be set up to support the Force Multiple function codes. Navigate to the Modbus Service properties -> General – Config tab. Set the properties usePresetMultipleRegister and usePresetMultipleCoil both to true. The driver will now write using function code 16 instead of 06 for both the ModbusGenericAO and ModbusPresetRegister objects.
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
1269 Views

What is the Analog to Digital Output resolution of the MNL controllers?

Issue What is the Analog to Digital Output resolution of the MNL controllers? Environment MNL Controllers Cause Analog/Digital conversion resolution Resolution The MNL controllers (with the exception of the MNL-800) have a 10-bit equivalent UI resolution and an 8-bit output resolution. The MNL-800 has a 12-bit equivalent UI resolution and an 8 bit output resolution.
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
881 Views

What is the Analog to Digital Output resolution of the MNB controllers?

Issue What is the Analog to Digital Output resolution of the MNB controllers? Environment MNB Controllers Cause Analog to Digital conversion resolution. Resolution The MNB BACnet controllers have 12-bit resolution on the inputs and 8-bit resolution on the analog outputs.
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
798 Views

Can the MNL controllers be powered by DC voltage?

Issue Can the MNL controllers be powered by DC voltage? Environment MNL controllers DC voltage input Cause Using DC voltage is not recommended or supported. Resolution The MNL controllers are not specified for DC operation and all agency approvals were submitted using a power source of 24 VAC 50/60 Hz.
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
792 Views

Can the MNB controllers be powered by DC voltage?

Issue Can the MNB controllers be powered by DC voltage? Environment MNB controllers DC voltage input Cause Using DC voltage is not recommended or supported. Resolution The MNB controllers are not specified for DC operation and all agency approvals were submitted using a power source of 24 VAC 50/60 Hz.
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
947 Views

How can a Network 8000 GCM-84000 or GCM-86000 be connected to the Niagara R2 UNC-520 RS-232 port?

Issue How can a Network 8000 GCM-84000 or GCM-86000 be connected to the Niagara R2 UNC-520 RS-232 port? Environment Network 8000 GCM-84000 GCM-86000 Niagara R2 Cause To use Network 8000 GCM-84000 or GCM-86000 with Niagara R2, connect using a pre-built adapters and silver satin cables. Resolution Pre-built adapters and silver satin cables for this type of connection are available for order.   The RJ-45 to DB-9 adaptor (UNCC-405) will interface to the GCM-86000. The RJ-45 to DB-25 adaptor (UNCC-430) will interface to a GCM-84000. A series of pre-terminated silver satin cables are available in three standard lengths: CBL-RJ45-4 Silver satin patch cable, 4 feet in length CBL-RJ45-10 Silver satin patch cable, 10 feet in length CBL-RJ45-25 Silver satin patch cable, 25 feet in length
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
853 Views

How can a DMS-35, DMS-350A or DMS-3500 be connected to a Niagara R2 UNC-520 RS-232 port?

Issue How can a DMS-35, DMS-350A or DMS-3500 be connected to a Niagara R2 UNC-520 RS-232 port? Environment Niagara R2 UNC-520 DMS-35 DMS-350A DMS-3500 Cause To use a DMS with Niagara R2, connect using a pre-built adapters and silver satin cables. Resolution Pre-built adapters and silver satin cables for this type of connection are available for order.   The RJ-45 to DB-9 adaptor (UNCC-405) will interface to the DMS-350A and DMS-3500 panels. The RJ-45 to DB-25 adaptor (UNCC-430) will interface to the DMS-35 panel. A series of pre-terminated silver satin cables are available in three standard lengths: CBL-RJ45-4 Silver satin patch cable, 4 feet in length CBL-RJ45-10 Silver satin patch cable, 10 feet in length CBL-RJ45-25 Silver satin patch cable, 25 feet in length
View full article
Picard Product_Support
‎2018-09-06 02:40 PM

Labels:
  • TAC IA Series
1190 Views

How to remove data for all logs prior to a specific date in a Niagara R2 Enterprise Server

Issue How to remove, from a Niagara R2 Enterprise Server station, data for all logs prior to a specific date with one command. Product Line TAC IA Series Environment I/A Series R2 Enterprise Server Cause Cloudscape database management Resolution There is a utility that will allow deleting of records before a certain date of all or specific tables in the cloudscape database. The space from deleted records can also be recovered after deleted. This utility is called CloudscapeAdmin and is downloadable from The Exchange Download Center. Download cloudscapeAdmin.jar and place in the x:\niagara\[NiagaraRevision]\nre\lib directory (for Builds 431 and higher). To run this utility the station will need to be stopped. Once the station is stopped, open the console from either the created short cut or x:\niagara\[NiagaraRevision]\nre\bin\console.exe. From here type ‘nre CloudscapeAdmin’ and hit enter to view the commands to use it.  There are two functions that cloudscapeAdmin can do: Delete; The delete command deletes records before a certain date but does not reduce the size used on the disk. The empty area of the database will be filled with new archived data. Compact; The compact command deletes records before a certain date and recovers the space from the disk. This process is slower. Command: nre CloudscapeAdmin x:\niagara\[Niagara Revision]\stations\[Station Name] [User Name] [Password] [delete or compact] [tablename or all] [date] Sample Delete commands: nre CloudscapeAdmin c:\niagara\r2.301.522a\stations\StationName admin admin delete all 2007-07-01 Sample Compact commands: nre CloudscapeAdmin c:\niagara\r2.301.522a\stations\StationName admin admin compact all 2007-07-01
View full article
Picard Product_Support
‎2018-09-07 03:11 AM

Labels:
  • TAC IA Series
2181 Views

How to configure serial tunneling for MicroSmart networks in Niagara G3

Issue How to configure serial tunneling for MicroSmart networks in Niagara G3. Product Line TAC IA Series Environment Niagara G3 OPRIF 11.x Cause Documented procedure with figures don't identify all steps clearly Resolution This video will help you set up and use serial tunneling with MicroSmart networks in Niagara G3.
View full article
Picard Product_Support
‎2018-09-07 03:14 AM

Labels:
  • TAC IA Series
1149 Views

How to program a limit block for use in Niagara G3.

Issue How to program a limit block for use in Niagara G3. Environment Niagara G3 Cause Limit are configure using the Reset object in the kitControl palette in the Math folder. Resolution Use the Reset object found in the kitControl palette in the Math folder.  To use it set the "Input Low Limit" and the "Output Low Limit" to the lowest desired output.  Set the "Input High Limit" and "Output High Limit" to the highest desire value. kitControl-Reset This component performs a linear “reset” on the inA value. Reset is available in the Math folder of the kitControl palette. Reset operation is defined by the following four slots: Input Low Limit — must be less than the Input High Limit Input High Limit — must be greater than the Input Low Limit Output Low Limit — may (or may not) be greater than the Output High Limit Output High Limit — may (or may not) be greater than the Output Low Limit For example, a Reset object is used to establish a hot water control setpoint, based on the outside air temperature at inA. When the outside air temperature is 0°F, the hot water setpoint is 200°F. When the outside air temperature is 75°F, the hot water setpoint is 100°F. The Reset object is configured as: Input Low Limit = 0.0 Input High Limit = 75.0 Output Low Limit = 200.0 Output High Limit = 100.0 Whenever the inA value is beyond the input limits, the output is limited by the corresponding output limit (in this case, 200 at 0°F or below, 100 at 75°F or above). When the input is at an intermediate value, the output scales linearly. For example, when the outside air temperature is at 38.2°F, the Reset output is 149.1°F.
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
3187 Views

Warning - Platform running low on RAM disk space (Niagara G3 Release 3.2.5 and higher)

Issue Warning - Platform running low on RAM disk space (Niagara G3 Release 3.2.5 and higher) Environment I/A Series G3 (typically embedded ENC/JACE platforms) Cause Low disk warning for history RAM disk A station fault will be generated if the free disk space on the history / alarm RAM disk falls below the minimum percentage specified on the PlatformServices property sheet. Resolution During station startup,  /niagara/bin/ramdisk.sh is invoked to create the RAM disk partition.   The RAM disk is named /aram0 and symbolic links are created from /alarm -> /aram0/alarm /history -> /aram0/history.  After the RAM disk is created it is populated with the contents of the alarm.zip and history.zip files.  During a station save or shutdown, the alarm and history files on the RAM disk are zipped and stored under the station directory in alarm/alarm.zip and history/history.zip.  If this fault occurs, users should take one or more of the following actions to prevent history/alarm data from being lost: Reduce number of histories that you are collecting Reduce number of records in each history Increase history RAM disk system (requires reboot). Action 3, above, will reduce the available system memory and should only be taken if there is sufficient free system memory.  Rather than writing history and alarm records directly to persistent storage, a Niagara G3 station stores history and alarm records in a RAM disk. This approach reduces the number and frequency of writes to flash.  Be careful not to increase too much otherwise you risk consuming all the available JACE free RAM causing the niagarad to crash.  Review the free system memory and make sure to leave a buffer of at least 1 MB of free RAM.  The RAM disk size is stored in /niagara/lib/platform.bog and can be adjusted using Services -> Platform Services. After reducing the number of histories, etc. the RAM disk will still indicate a low warning message until the unused histories are removed from the history storage.  Delete the unused histories using the Database Maintenance view on the history component view within the station.
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
3283 Views

Configuring the LON Router (LPR-10) within a Niagara R2 System

Issue Configuring the LON Router (LPR-10) within a Niagara R2 System Environment Niagara R2 system LPR-10 Cause Procedure to configure LON Router (LPR-10) in Niagara R2. Resolution Since most LonWorks networks are unmanaged (that is, managed only by the Niagara station's Lon Device Manager), use the procedure beginning on page A-9, of the Niagara LonWorks Integration Guide, to define the LonWorks network.  Before beginning this process, cut the existing LonRouter and Channel1 from the station. Set the status of all of the Lon devices to "Unknown". The most important part of this process is defining the router and associated channels before beginning any of the automated processes using the LonDeviceManager. Ensure four LON-TERM-2 devices (LON BUS Topology Terminators) are installed. One at each end of the trunk and one at the near end of the router and one at the far end of the router.
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
1308 Views

Is Niagara R2 compatible with Windows Server 2003?

Issue Is Niagara R2 compatible with Windows Server 2003? Environment Niagara R2 Windows Server 2003 Cause Compatibility Resolution Niagara version 514 and higher was officially certified to operate with Windows NT, Windows XP, and Windows Server 2003. As a side note, if using Windows Server 2003, there are two issues to be aware: Windows Server will use IIS services causing a conflict with TCP port 80. This will have to be addressed when engineering the station database. There is an issue with Niagara and Windows Server 2003. Tridium released a Tech Tip as follows: R2 Web Supervisor on Windows 2003 Service Pack JDE will not start. If fui.exe is run from within the Windows command prompt, the following error is displayed: Error occurred during initialization of VM Could not reserve enough space for object heap. The problem is limited to instances where the user is accessing the computer with a Remote Desktop connection. On 8/8/2006, Microsoft issued an update KB921883 which unintentionally causes problems with applications that use large amounts of contiguous memory on a Windows Server 2003 Service Pack 1-based computer. There is a Hotfix now available to resolve the issues generated by this update. Hotfix KB924054.
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
843 Views

Getting an error when adding the ASD service to a Niagara R2 station

Issue Getting an error when adding the ASD service to a Niagara R2 station Environment Niagara R2 ibsAsd driver Cause The error indicates that the serialDriver jar file has not been installed. Resolution The ibsAsd driver will not function without the serialDriver jar file. The serialDriver includes communications class files needed to support ibsAsd. To correct the issue, use the Installation Wizard in the admin tool to install the serialDriver jar. Caution: The station must have the Serial Driver installed. It is recommended that the 516b version released in July 2006 be used. The jar files as well as the ASD driver documentation (F-27429) are available for download from The Exchange Download Center
View full article
Picard Product_Support
‎2018-09-07 02:28 AM

Labels:
  • TAC IA Series
1111 Views

Two stations running concurrently on a Niagara R2 computer

Issue How can two stations run concurrently on a Niagara R2 computer? Product Line TAC IA Series Environment Niagara R2 Cause Operate two stations by running each station on different port. Resolution In order to run two stations simultaneously, set up one of the stations to run on a different port. By default, the station database is set up to run on port 80. Attempting to start a second station will fail if it finds the port unavailable. Open the second station offline; right click on the station root, and select properties. On the configuration tab, set the httpPort to another value (e.g. 8080). Save and close the station database. The station should now start without conflict. Remember to open the station with the IP address followed by the port (e.g. 10.1.146.25:8080). Also, for live external links to work, the address books would have to match (adding the port number).
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
1305 Views

Lifecycle margin versus actual station database resource count in Niagara R2.

Issue Lifecycle margin versus actual station database resource count in Niagara R2. Environment Niagara R2 Cause When pasting objects that are over the maximum allowance size, it will not paste the object because the copy or cut maximum size is depend on the Lifecycle margin. Resolution The UNC-410, UNC-510, and UNC-520 platforms all have a resource count limitation of 600,000.  The TRD-NXT has a resource count limit of 2,500,000. The total number of available resources is the same regardless of support for Web services. The (Search > Resource Count) function under the WorkPlace Pro Search menu item will count the number of resources used. The count is performed from the object currently selected on the JDE tree and includes all child objects. By selecting the station's root name, the resource value for the entire station database will be provided. The dialog box with the information provides the calculated actual Resource count and also will indicate the Lifecycle margin: 20,000. The Lifecycle margin is a JDE term that specifies the maximum size (in resource count) of any “cut” or “copy” permitted in a running station. A cut or copy effectively creates a temporary new tree of objects within the memory of the host. This mechanism is used to support the JDE's “undo” operation (Edit > Undo). As an example, try to cut & paste something and it won't be allowed because of resources.  After checking, for instance, that there is a 43,000 resource count with a lifecycle margin of 20,000, what is happening is that the cut and paste has a total resource count higher than 20,000 which is the max. Perform the cut and paste in smaller portions.
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
1679 Views

Communications issues with a Niagara R2 UNC-520 and Viconics VT-76xx BACnet thermostats

Issue Communications issues with a Niagara R2 UNC-520 and Viconics VT-76xx BACnet thermostats Environment Niagara R2 UNC-520 Viconics VT-76xx BACnet Cause Viconics VT-76xx BACnet thermostats do not support COV. Resolution Use the admin tool servlet to set useCOV to false.
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
1145 Views

What do the network mismatch errors in WorkPlace Commissioning Tool mean?

Issue What do the network mismatch errors in WorkPlace Commissioning Tool mean? Environment  WorkPlace Commissioning Tool Cause Information to troubleshoot network mismatch errors in WorkPlace Commissioning Tool. Resolution These errors are described in the WorkPlace Commissioning Tool and Flow Balance Tool Users Guide (F-27358) page 175.
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
1002 Views

Connection to a DMS MicroPlex MSC-NC is successful. However, when accessing a networked MicroSmart controller, the connection attempt fails.

Issue Connection to a DMS MicroPlex MSC-NC is successful. However, when accessing a networked MicroSmart controller, the connection attempt fails. Environment DMS MicroPlex MSC-NC MicroSmart Controller Cause Flash ROM in the MSC-NC Resolution Reload of the flash in the MSC-NC: Power down Jump J1 (near processor) Power up. Connect with DCT Remove J1 jumper f. Do “Alt-L” as this will start installation of Flash ROM. The above will also take care of these problem issues: Back door password (lack of) "Ghost" controllers that are not there None standard service alarm code (sample: 44+service alarm44144144/144)
View full article
Picard Product_Support
‎2018-09-06 02:39 PM

Labels:
  • TAC IA Series
1007 Views
  • « Previous
    • 1
    • …
    • 44
    • 45
    • 46
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of