Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

In I/A Series G3, history extensions cannot be enabled to begin collection.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • In I/A Series G3, history extensions cannot be enabled to begin collection.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa116871
    sesa116871

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1396 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

In I/A Series G3, history extensions cannot be enabled to begin collection.

Picard Product_Support
‎2018-09-07 05:24 AM

Issue

History Extensions in History Service show a “Fault” Status.  The Fault cause displays: "Duplicate history id:" followed by the name of the object.

Environment

I/A Series G3, version 3.3.22 and later

Cause

 By default, history extensions inherit the name of the objects they’re attached to (e.g. CFM).  If CFM is to be trended on multiple VAV units (VAV1, VAV2, etc.), this can cause issues when enabling history collection in the History Service; one or more histories will be in a “Fault” state, with the error message: “Duplicate history id:” for the Fault Cause.

Resolution

To resolve the issue, the history names can be configured to include the parent folder names:

 

 

1.  Open the Program Service in the station’s Services container, and click on the “Find Objects” button at the bottom of the Batch Editor view

2.  In the Bql Query Builder window, select (Custom Type) in the “Of type:” drop-down menu.  Two more drop-down menus will appear.  In the middle drop-down, select “history”.  In the last drop-down, select the appropriate history extension (e.g. NumericIntervalHistoryExt).  Then, click OK.  The Batch Editor view will populate with all of the history extensions in the station for the extension type selected

 

 

3.  In the Batch Editor view, highlight all of the history objects, then click the “Edit Slot” button at the bottom of the view

4.  In the Edit Slot window, select “historyName” in the Property drop-down menu.  In the New Value field, type the following:

     %parent.parent.name%_%parent.name%

 

 

NOTE:  Depending on the tree structure, the filter may need to be modified in order to create a unique history name.  For example, if the network is structured in the following format:

 

In this example, the object nviSatSwitch1_value is a child of the Points container, which is a child of the device MnlRs3_10. In order to create a unique name for the history extension, the correct filter would need to be:

        %parent.parent.parent.name%_%parent.name%.

 

5.  Click OK.  After a few seconds, the BatchEditor Results window will appear, displaying the objects that were changed.  The history extensions now have unique names, and can be enabled in the History Service

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 4553
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore